    <big>i have a simulation (leed) i am responding to comments on &
      just noticed in my ps-h report for my pv system that:<br>
      <br>
      a) despite not changing anything in the pv setup from my last
      submittal, and<br>
      b) the horizontal columns to the right (last graphic) that sum the
      operating hours not changing,<br>
      c) there is a rearrangement in operating hours allocation between
      the 30/40 run hours and 70/80 run hours columns where the vertical
      column (hours within each part load) are slightly different but
      the differences cancel each other out so the horizontal (total run
      hours) total remains the same,<br>
      d) and there is a slight change in the ac output kwh generated
      while the dc input kwh remains the same.  see screen capture below
      (new run on left, old run on right).  new inverter ac output kwh
      is slightly higher.<br>
      <br>
      this is a little bit of a puzzler as i did not change any of the
      inputs for the pv i'm not sure where to begin to look to see what
      may be the cause behind the changes.  (i have checked the pv
      inputs from the original submittal & they're the same for the
      inverter & panels).<br>
      <br>
      there was no review comment regarding the inputs, or the reports
      specifically, just that the reviewer didn't understand the way
      equest subtracts the pv from each end-use on the electric meter it
      is assigned to, so if i resubmit with a different pv ac output kwh
      this may raise a flag as i'm sure the reviewer (and myself) would
      expect the amount of pv generated to remain the same if it wasn't
      changed.  heck, it's confusing me & i'm the one who set it up.<br>
      <br>
      any ideas what would cause a change in the pv ac output kwh where
      the dc input kwh stays the same?  it doesn't sound like a pv
      module or shading concern.</big>  i have had some adjustments made
    to the hvac & lighting (some slight increases, some slight
    decreases) but neither system would affect the output of the
    inverter, right?<br>
    <br>
    <br>
    <img src="cid:part1.00040101.09040808@gmail.com" alt=""><br>
    <br>
    <br>
    <big>summary columns for load hours when operating, note the
      horizontal totals (right column) are the same but the verticals
      differ starting at column 4 to column 9).</big><br>
    <img src="cid:part2.02060203.00070606@gmail.com" alt=""><br>
    <br>
  </body>
</html>