    <font size="+1">I would not include the large unit.  It is a
      specific purpose/intermittent unit.  I would however investigate
      how it is going to be used.  Normally you try to segregate the
      truck loading areas from the rest of the plant to limit the area
      exposed to the exhaust fumes and to make it easier to remove
      them.  Sometimes though, making large items, this is not
      possible.  Typically these units are connected to CO/CO2 sensors
      and also have an exhaust fan.  If you use the MUA unit to blow the
      exhaust fumes out it won't work when the doors are closed.  This
      is why an exhaust fan works better with the MUA unit.  The way the
      loading normally happens is the trailer is backed in first and the
      tractor comes in last, the door is closed and the truck is shut
      off for the loading period.  That puts all the truck exhaust on
      the ceiling by the loading doors.  That is where you put the
      exhaust fans.  The MUA unit is placed across from the exhaust to
      push the truck exhaust to the exhaust fans.  The unit only runs
      until the sensor is satisfied.  As Bill mentioned you don't have
      to bring that MUA up to plant temperature either, that would
      depend on where you are dumping it and how much air there is.  You
      may not have to heat it at all.  I have used systems which bring
      in air unheated and use fabric tubes to spread it at ceiling level
      in the hot stratified air next to the ceiling.<br>
      I don't consider these events in the general system for heating
      the building but you do have to consider the event and how to
      mitigate it's impact on the plant and meet all the safety rules. 
      You generally have unit heaters near large roll up doors as they
      are leaky and not as well insulated as the rest of the building. 
      This comes in handy when you open the doors or when you have 10
      tons of cold steel sitting in the loading bay.  Don't forget floor
      drains.<br>
      Bruce Easterbrook P.Eng.<br>
      Abode Engineering<br>
      <br>
    </font>
    <div class="moz-cite-prefix">On 08/10/2012 08:52 AM, Bishop, Bill
      wrote:<br>
    </div>
    <blockquote
cite="mid:90D829482BDEDB4CB264DE5060592B1905C25219@lightning.pathfinderengineers.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Wingdings;
        panose-1:5 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
        {mso-style-priority:34;
        margin-top:0in;
        margin-right:0in;
        margin-bottom:0in;
        margin-left:.5in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
span.EmailStyle17
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
/* List Definitions */
@list l0
        {mso-list-id:1001663379;
        mso-list-type:hybrid;
        mso-list-template-ids:-1337134958 67698689 67698691 67698693 67698689 67698691 67698693 67698689 67698691 67698693;}
@list l0:level1
        {mso-level-number-format:bullet;
        mso-level-text:\F0B7;
        mso-level-tab-stop:none;
        mso-level-number-position:left;
        text-indent:-.25in;
        font-family:Symbol;}
ol
        {margin-bottom:0in;}
ul
        {margin-bottom:0in;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Pete,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Before
            increasing the proposed design heating capacity, I would
            consider other changes you can make to the model:<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l0 level1 lfo1"><!--[if !supportLists]--><span
            style="font-size:11.0pt;font-family:Symbol;color:#1F497D"><span
              style="mso-list:Ignore">·<span style="font:7.0pt
                "Times New Roman"">        
              </span></span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Increase
            the process/plug loads (after all, it is a manufacturing
            facility)<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l0 level1 lfo1"><!--[if !supportLists]--><span
            style="font-size:11.0pt;font-family:Symbol;color:#1F497D"><span
              style="mso-list:Ignore">·<span style="font:7.0pt
                "Times New Roman"">        
              </span></span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Decrease
            the heating thermostat setpoint (70F or less)<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l0 level1 lfo1"><!--[if !supportLists]--><span
            style="font-size:11.0pt;font-family:Symbol;color:#1F497D"><span
              style="mso-list:Ignore">·<span style="font:7.0pt
                "Times New Roman"">        
              </span></span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">If
            you have nighttime setback, create a morning warm-up period<o:p></o:p></span></p>
        <p class="MsoListParagraph"
          style="text-indent:-.25in;mso-list:l0 level1 lfo1"><!--[if !supportLists]--><span
            style="font-size:11.0pt;font-family:Symbol;color:#1F497D"><span
              style="mso-list:Ignore">·<span style="font:7.0pt
                "Times New Roman"">        
              </span></span></span><!--[endif]--><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Increase
            the thermostat throttling range a few degrees (reflecting
            less “comfort” but resulting in fewer unmet hours; IMO a
            last resort before adding heating capacity)<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Note
            that you would make the same changes in the baseline for
            any/all of these suggestions.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Regards,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">Bill<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <p class="MsoNormal"><a moz-do-not-send="true"
              href="mailto:wbishop@pathfinder-ea.com"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:blue;text-decoration:none"><img
                  id="Picture_x0020_1"
                  src="cid:part1.02060900.06000208@bellnet.ca"
                  alt="Senior Energy Engineer 28Jun2012" border="0"
                  height="114" width="480"></span></a><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0in 0in 0in">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
                <a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
                [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Peter Baumstark<br>
                <b>Sent:</b> Friday, October 05, 2012 10:54 PM<br>
                <b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> [Equest-users] ASHRAE 90.1 Appendix G
                Proposed Model<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div>
            <p class="MsoNormal"><span
                style="font-family:"Arial","sans-serif"">I
                have a high bay manufacturing facility with two100% OSA,
                CV, low cfm but high air velocity heating only units. 
                These are intended for comfort heating.<br>
                <br>
                The building also has one 100% OSA, CV make-up air (MUA)
                unit, with a gas furnace.  The MUA is only used when one
                or more roll-up doors are open with trucks inside and
                unloading.  This blows the diesel fumes out of the
                building.  The MUA has almost 3x the air volume capacity
                as the two comfort heating units combined.<br>
                <br>
                When I model the proposed design, with just the two
                units intended for comfort heating, I end up with almost
                700 unmet heating hours.  I add the capacity for the MUA
                unit and schedule it for the purpose of comfort heating,
                and my unmet hours go down to less than 10.<br>
                <br>
                Also in 90.1, App G, if unmet load hours exceed 300,
                heating capacity can be added incrementally until unmet
                load hours are reduced to below 300.<br>
                <br>
                So would it be fair to not include the MUA unit for
                heating, but simply add one or two more of the comfort
                heating units to get the unmet hours down?  It seems
                like it may be over-kill to include the MUA unit for the
                purpose of comfort heating.<br>
                <br>
                Any guidance would be appreciated.<br>
                <br>
                Thank you,<br>
                Pete<o:p></o:p></span></p>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>