<html><body><div style="color:#000; background-color:#fff; font-family:times new roman, new york, times, serif;font-size:12pt"><div>All, I am modeling a large research tower, 470,000 SF. On past projects, all of the HVAC systems were 100% outdoor air with heat pipe energy recovery. On this project, we will be returning part of the building, yielding 81% outdoor air. I am trying to model the energy savings. Equest is actually showing an increase in utility costs for going from 100% to 81%, both with and without energy recovery, which is the opposite of what I expected. Both versions of the baseline have economizer. If I compare the utility consumption, it looks as if the fan energy has increased significantly by decreasing the amount of outdoor air (entered as a fraction on the system outdoor air tab) and the cooling energy has increased a little.</div><div> </div><div>Does anyone have any idea what combination of
inputs that I have that would lead to this problem? It seems to me that these results couln't be valid.</div><div> </div><div>Thanks,</div><div>Maria Ramos, PE</div></div></body></html>