    Nimesh,<br>
    <br>
    Are you trying to apply ASHRAE 90.1 for a building in Singapore?  I
    think you should check first the commercial building energy standard
    in Singapore, instead.  However, if  you do want to do a simulation
    in accordance to the ECB method in ASHRAE 90.1, the Reference
    Building should be architecturally the same as your Proposed
    Building, but with shell conditions as prescribed in the standard
    for the appropriate Climate Zone, which for Singapore must be
    Climate Zone 1.  For more information on ASHRAE 90.1 modeling rules,
    please look at the ECB chapter (Chapter 11 in the 2004 version, my
    latest) of the standard.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 9/20/2012 7:40 PM, Nimesh Prajapati Nimesh wrote:
    <blockquote
      cite="mid:1348195249.10464.YahooMailNeo@web193905.mail.sg3.yahoo.com"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html;
        charset=iso-8859-1">
      <div>
        <div><span>Dear Friends,</span></div>
        <div><br>
          <span></span></div>
        <div><span>I am confused here: What is Baseline Standard for
            Singapore Buildings using which I can create Baseline model?</span></div>
        <div><br>
          <span></span></div>
        <div><span>Shall I use ASHRAE 90.1 Appendix - G? Can anybody
            guide me?</span></div>
        <div> </div>
        <div><span>Thanks,</span><br>
          <br>
          <span>Nimesh Prajapati</span><br>
          <br>
          <span></span><span>HVAC Design Engineer  </span></div>
        <div><span>(+91 9687133492)</span><br>
          <span>email: <a class="moz-txt-link-abbreviated" href="mailto:nimonomics@yahoo.in">nimonomics@yahoo.in</a></span><br>
          <span>Skype: nimonicideas</span><br>
          <span>Please consider the environment before printing this
            e-mail.</span></div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>