    <font size="+1">A single system can be a lot of problem.  There is
      just so much variation between the zones most times and there are
      not enough T-stats.  I don't know the number of zones and the
      space size but if you are down to the 100 hour unmet range I think
      you are as close as you are going to get it.  One other thing to
      look at is the timing of the unmet hours.  Many times I have
      found, more so with higher mass buildings is a one hour warm up is
      not enough and you will get a lot of unmet hours right at the
      start of the day.  Sometimes bringing the AHU off night set back 2
      hours before is enough to get rid of these shoulder hours.  There
      can be a big difference in the heat and cooling capacity required
      from maintaining a set point verses trying to recover the space
      from a 4 degree set back.  Equipment these days is sized closer to
      the line and it takes a little more time for the system to get the
      space under control.<br>
      Bruce Easterbrook P.Eng.<br>
      Abode Engineering<br>
      <br>
    </font>
    <div class="moz-cite-prefix">On 11/09/2012 12:40 PM, John Shen
      wrote:<br>
    </div>
    <blockquote cite="mid:COL113-W28C0705A06646FA1AF5D4DED930@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style>
      <div dir="ltr">
        Thank you very much for the response, they were extremely
        helpful. I was able to reduce my unmet hours to ~100 hours but
        not without a whole lot of effort. It appears that my zones had
        a large load discrepancies between one another, the central
        zones had minimal load while certain outer zones had large heat
        loss due to window frames, zone area etc. This seemed to result
        in a system being very sensitive to air flow and I was
        previously making too large of an increment with my min air
        flow. Increasing the reheat-delta-T did make the system much
        easier to deal with as eQUEST seemed to distribute air flow when
        auto-sizing. In the end there were still zones where ~100 unmet
        hours was as low as I could get it no matter how I changed the
        air flows, as the system did appear to be fighting itself to a
        degree. The only fix was to auto-size baseboards in these
        trouble zones. I suppose these issues aren't uncommon when you
        have a single system serving large a number of zones.<br>
        <br>
        <div>
          <hr id="stopSpelling">Date: Mon, 10 Sep 2012 12:42:45 -0400<br>
          From: <a class="moz-txt-link-abbreviated" href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a><br>
          To: <a class="moz-txt-link-abbreviated" href="mailto:johnshen1@hotmail.com">johnshen1@hotmail.com</a><br>
          CC: <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
          Subject: Re: [Equest-users] Power induction unit/ reheat delta
          T<br>
          <br>
          <font size="+1">It seems to me you have gone overboard on your
            zone air flows which will generate unmet hours and also
            waste energy.  This is all a balancing act between several
            conflicting items, air flow just being one.  I don't think
            your delta T is the problem.  Terminal units can heat and
            cool and it sounds like yours are not cooling.  I would also
            suspect your system is fighting itself.  You are going to
            have to troubleshoot what is going on and figure out a
            solution.  Your sim reports will tell you how much heating
            and cooling each zone requires.  From there you can figure
            out how much air you need to to accomplish this.  Compare
            that to how much air you are putting in.  I don't do a lot
            of these types of systems to give you a quick answer with
            the information I have.  Most of the time there is no quick
            answer anyway.  All HVAC systems follow a logical pattern. 
            You need to find where and why you have deviated.  As you
            can see eQuest will take you way out into left field if you
            let it.<br>
            Bruce Easterbrook P.Eng.<br>
            Abode Engineering<br>
            <br>
          </font>
          <div class="ecxmoz-cite-prefix">On 07/09/2012 06:05 PM, John
            Shen wrote:<br>
          </div>
          <blockquote
            cite="mid:COL113-W166539F21017ABFBC9435EDAF0@phx.gbl">
            <style><!--
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}

--></style>
            <div dir="ltr"> <br>
              I am working on a building with air handling units on each
              floor. Interior zones are served by the AHU while exterior
              zones are served by the AHU as well as FC unit which
              provides furthur heating and cooling. I modeled the system
              as a Power Induction Unit with series PIU to represent the
              FC units. I used a reheat delta T determined from AHU and
              FC's spec'd heating capacity and air flow rates and
              allowed eQUEST to autosize and distribute airflow. Thanks
              to the advice given from members on this list I was able
              to reduce my unmet hours to a reasonable range.
              <div><br>
              </div>
              <div>I am working on the baseline model and am again
                having issues with unmet hours. As mentioned the heat
                capacity of VAV systems are determined by the design
                flow rate and the reheat delta T. In order to reduce
                unmet hours I would increase flow rates to particular
                zones by manually increasing Min design flow rates with
                my reheat delta T set at 20F which is what is required
                by ASHRAE. I've been at this for a while and my building
                is basically a wind tunnel, I have floors with supply
                cfm upwards of 100,000 CFM and I still have thousands of
                unmet hours. (my throttling range are at 6)</div>
              <div><br>
              </div>
              <div>Am I allowed to change reheat_delta_T to a larger
                value? </div>
              <div><br>
              </div>
              <div>For a power induction unit with series PIU boxes, is
                there any way for the boxes to provide zone cooling?
                Looking at hourly reports for "zone coil cooling" I have
                0's.</div>
              <div><br>
              </div>
              <div>Much of this might be brought about by the fact that
                my building heating and cooling load has doubled in the
                baseline model.</div>
              <div><br>
              </div>
              <div>Any advice would be much appreciated.<br>
                <div>
                  <hr id="ecxstopSpelling">Date: Mon, 27 Aug 2012
                  09:40:41 -0400<br>
                  From: <a moz-do-not-send="true"
                    class="ecxmoz-txt-link-abbreviated"
                    href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a><br>
                  To: <a moz-do-not-send="true"
                    class="ecxmoz-txt-link-abbreviated"
                    href="mailto:johnshen1@hotmail.com">johnshen1@hotmail.com</a><br>
                  CC: <a moz-do-not-send="true"
                    class="ecxmoz-txt-link-abbreviated"
                    href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                  Subject: Re: [Equest-users] Power induction unit/
                  reheat delta T<br>
                  <br>
                  <font face="Times New Roman, Times, serif" size="+1">For

                    reference on the sim reports go to help/Tutorials
                    and Reference/Detailed Simulation Reports Summary. 
                    It will explain all the reports.  I don't use the
                    SS-G report much.  I also don't do much chilled
                    water cooling.  I looked at a DX design I had done
                    and the SS-G shows no cooling.<br>
                    Cooling is the most difficult to get right because
                    the delta-T is almost always lower than the heating
                    side and on the heating side you can always cheat a
                    little with baseboards to do a final trim even if
                    you don't have them in your system.  You can get a
                    quick idea of the magnitude you are short.  Cooling
                    has no final trim and the eQuest focus is on
                    cooling.  You have also bumped into another limit on
                    cooling capacity.  You are correct that the cooling
                    capacity is dependent on the delta-T and the air
                    flow.  There are 2 delta-T's, the one on your water
                    and the one on your air.  You can play with the
                    water one all day but if you don't have enough air
                    you won't get anywhere.  Equest has a default on the
                    airflow to a zone that is 0.6 cfm/SF.  Your main AHU
                    maximum flow will be based on this value for the sum
                    of all the zones it is supplying.  Most of the time
                    this value is too small for a sun side perimeter
                    zone.<br>
                    I would start with the zone with the worst unmet
                    hours.  You want to use zone reports, start with
                    LS-A which will give you your peak heating and
                    cooling loads for all your zones.  LS-B will give
                    you the components of that load except OA.  SS-R is
                    handy.  Keep an eye on SV-A, it will list the zones
                    and their airflow's as sub-components of the main
                    AHU.<br>
                    You want to go to the air-side HVAC tab and select
                    the zone you want to work on.  Right click and
                    select "Properties".  In the "Basic Specifications"
                    tab you will see on the right side half way down
                    "Zone Design Flow Rates", the first value is "Min
                    Design Flow" and is probably set at 0.6 cfm/SF,
                    start increasing this value.  You may need to be in
                    the 1.2 cfm/SF range, it depends on the zone and the
                    cooling load.    You can calculate what you need
                    too.  As you bring the number up you will see the
                    AHU airflow increase and also the cooling/heating
                    capacity of the AHU increase in SV-A.  Remember that
                    you just want enough air.  Excess air moving wastes
                    energy.  Your unmet hours should be decreasing for
                    that zone.  Some of the other zones will begin to
                    decrease as well but your main problem zones should
                    still have unmet hours.  Deal with each one the same
                    way.<br>
                    Remember this, it is probably THE most important
                    setting in eQuest on the air side.<br>
                    Bruce Easterbrook P.Eng.<br>
                    Abode Engineering<br>
                    <br>
                  </font>
                  <div class="ecxmoz-cite-prefix">On 24/08/2012 05:16
                    PM, John Shen wrote:<br>
                  </div>
                  <blockquote
                    cite="mid:COL113-W411E3BE1CB2180FA45F796EDBD0@phx.gbl">
                    <style><!--
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}

--></style>
                    <div dir="ltr"> Thank you for the response, couldn't
                      have asked for a better explanation.
                      <div><br>
                      </div>
                      <div> I was able to get the heat unmet hours down
                        to a reasonable range. However, I am having
                        difficulties with the Cool unmet hours. It
                        appears I am unable to acquire any cooling
                        capacity which is resulting in a few unmet hours
                        (~150). As mentioned the heating capacity is
                        dependent on the reheat delta t and airflow. I
                        can't seem to find a place to enter delta T for
                        cooling, I have coil delta T set along with an
                        appropriate CHW loop. Yet I don't get any
                        cooling in any of my zones in the SS-G section
                        of the report. Any further help would be
                        appreciated.</div>
                      <div><br>
                      </div>
                      <div>John<br>
                        <br>
                        <div>
                          <hr id="ecxstopSpelling">Date: Fri, 24 Aug
                          2012 09:57:49 -0400<br>
                          From: <a moz-do-not-send="true"
                            class="ecxmoz-txt-link-abbreviated"
                            href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a><br>
                          To: <a moz-do-not-send="true"
                            class="ecxmoz-txt-link-abbreviated"
                            href="mailto:johnshen1@hotmail.com">johnshen1@hotmail.com</a><br>
                          CC: <a moz-do-not-send="true"
                            class="ecxmoz-txt-link-abbreviated"
                            href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                          Subject: Re: [Equest-users] Power induction
                          unit/ reheat delta T<br>
                          <br>
                          <font size="+1"><font face="Times New Roman,
                              Times, serif">You can try changing your
                              interior control zone as this will effect
                              the base capacity that the AHU will supply
                              to the floor.  As for the exterior zones
                              your heat/cool capacity is based on the
                              delta-T and the airflow.  You said you
                              specified the air flow.  Let eQuest
                              auto-size the flow.  By specifying the air
                              flow you have removed most of eQuest's
                              ability to adjust capacity.  One other
                              thing to remember is eQuest is working on
                              the maximum flow as well as all the
                              intermediate conditions as well.  It is
                              these intermediate loads which will
                              trigger most of your unmet hours.  As the
                              sun moves across your exterior zones
                              through the day the peak load will be
                              shifting through the exterior zones as
                              well.  So a zone which was the peak at 10
                              am won't be the peak at 3 pm.  eQuest will
                              count an unmet hour if you are high or low
                              on a zones temperature.  By specifying the
                              cfm to the zone I would guess you may be
                              over cooling some of the zones and
                              triggering unmet hours.  eQuest, if
                              allowed, would reduce the airflow to the
                              10 am zone later in the day and shift the
                              CFM to the 3 pm zone.  This is mostly
                              under the hood stuff and you have to drill
                              pretty deep into your reports to have an
                              idea of what is going on and you won't
                              find the direct answer as to the lower cfm
                              to the zone.  You can get an idea of the
                              heat/cool capacity eQuest is dealing with
                              in each and follow it across the building.<br>
                              Bruce Easterbrook P.Eng.<br>
                              Abode Engineering.<br>
                              <br>
                            </font></font>
                          <div class="ecxmoz-cite-prefix">On 23/08/2012
                            01:56 PM, John Shen wrote:<br>
                          </div>
                          <blockquote
                            cite="mid:COL113-W42CBA256ABB1E18AE29E3BEDBE0@phx.gbl">
                            <style><!--
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}

--></style>
                            <div dir="ltr">
                              <p class="ecxMsoNormal">Working on a
                                building with an air handling unit which
                                serves the entire floor. In the exterior
                                rooms there are Fan coils to supply
                                further heating and cooling to the
                                floor. I have split the floor up into
                                interior zones and exterior zones (each
                                containing a fan coil unit). The AHU I
                                have modeled as a power induction unit
                                which serves all the zones on the floor,
                                the interior zones have terminal type
                                std VAV and the exterior zones have
                                series PIU. With in the exterior zones I
                                have specified flow rates, heat/cool
                                capacity reflecting the FC. However I am
                                getting lots of unmet hours from these
                                exterior zones (~500 hrs each). I
                                inputted a REHEAT-DELTA-T in of 57F
                                (based on fan flow rates and heat
                                capacity) into each of the exterior
                                zones. This greatly reduced the unmet
                                hours; however I find it strange because
                                the unmet hours are completely dependent
                                on REHEAT-DELTA-T and completely
                                independent of the zone heat capacity. I
                                appear to have a poor understanding of
                                how the PIU system works, if anyone
                                could provide further insight it would
                                be much appreciated.</p>
                              <p class="ecxMsoNormal"><br>
                              </p>
                              <p class="ecxMsoNormal">John</p>
                            </div>
                            <br>
                            <fieldset class="ecxmimeAttachmentHeader"></fieldset>
                            <br>
                            <pre>_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
                          </blockquote>
                          <br>
                        </div>
                      </div>
                    </div>
                    <br>
                    <fieldset class="ecxmimeAttachmentHeader"></fieldset>
                    <br>
                    <pre>_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
                  </blockquote>
                  <br>
                </div>
              </div>
            </div>
            <br>
            <fieldset class="ecxmimeAttachmentHeader"></fieldset>
            <br>
            <pre>_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
          </blockquote>
          <br>
        </div>
      </div>
    </blockquote>
    <br>
  </body>
</html>