    <font size="+1">It seems to me you have gone overboard on your zone
      air flows which will generate unmet hours and also waste energy. 
      This is all a balancing act between several conflicting items, air
      flow just being one.  I don't think your delta T is the problem. 
      Terminal units can heat and cool and it sounds like yours are not
      cooling.  I would also suspect your system is fighting itself. 
      You are going to have to troubleshoot what is going on and figure
      out a solution.  Your sim reports will tell you how much heating
      and cooling each zone requires.  From there you can figure out how
      much air you need to to accomplish this.  Compare that to how much
      air you are putting in.  I don't do a lot of these types of
      systems to give you a quick answer with the information I have. 
      Most of the time there is no quick answer anyway.  All HVAC
      systems follow a logical pattern.  You need to find where and why
      you have deviated.  As you can see eQuest will take you way out
      into left field if you let it.<br>
      Bruce Easterbrook P.Eng.<br>
      Abode Engineering<br>
      <br>
    </font>
    <div class="moz-cite-prefix">On 07/09/2012 06:05 PM, John Shen
      wrote:<br>
    </div>
    <blockquote cite="mid:COL113-W166539F21017ABFBC9435EDAF0@phx.gbl"
      type="cite">
      <style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style>
      <div dir="ltr">
        <br>
        I am working on a building with air handling units on each
        floor. Interior zones are served by the AHU while exterior zones
        are served by the AHU as well as FC unit which provides furthur
        heating and cooling. I modeled the system as a Power Induction
        Unit with series PIU to represent the FC units. I used a reheat
        delta T determined from AHU and FC's spec'd heating capacity and
        air flow rates and allowed eQUEST to autosize and distribute
        airflow. Thanks to the advice given from members on this list I
        was able to reduce my unmet hours to a reasonable range.
        <div><br>
        </div>
        <div>I am working on the baseline model and am again having
          issues with unmet hours. As mentioned the heat capacity of VAV
          systems are determined by the design flow rate and the reheat
          delta T. In order to reduce unmet hours I would increase flow
          rates to particular zones by manually increasing Min design
          flow rates with my reheat delta T set at 20F which is what is
          required by ASHRAE. I've been at this for a while and my
          building is basically a wind tunnel, I have floors with supply
          cfm upwards of 100,000 CFM and I still have thousands of unmet
          hours. (my throttling range are at 6)</div>
        <div><br>
        </div>
        <div>Am I allowed to change reheat_delta_T to a larger value? </div>
        <div><br>
        </div>
        <div>For a power induction unit with series PIU boxes, is there
          any way for the boxes to provide zone cooling? Looking at
          hourly reports for "zone coil cooling" I have 0's.</div>
        <div><br>
        </div>
        <div>Much of this might be brought about by the fact that my
          building heating and cooling load has doubled in the baseline
          model.</div>
        <div><br>
        </div>
        <div>Any advice would be much appreciated.<br>
          <div>
            <hr id="stopSpelling">Date: Mon, 27 Aug 2012 09:40:41 -0400<br>
            From: <a class="moz-txt-link-abbreviated" href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a><br>
            To: <a class="moz-txt-link-abbreviated" href="mailto:johnshen1@hotmail.com">johnshen1@hotmail.com</a><br>
            CC: <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
            Subject: Re: [Equest-users] Power induction unit/ reheat
            delta T<br>
            <br>
            <font face="Times New Roman, Times, serif" size="+1">For
              reference on the sim reports go to help/Tutorials and
              Reference/Detailed Simulation Reports Summary.  It will
              explain all the reports.  I don't use the SS-G report
              much.  I also don't do much chilled water cooling.  I
              looked at a DX design I had done and the SS-G shows no
              cooling.<br>
              Cooling is the most difficult to get right because the
              delta-T is almost always lower than the heating side and
              on the heating side you can always cheat a little with
              baseboards to do a final trim even if you don't have them
              in your system.  You can get a quick idea of the magnitude
              you are short.  Cooling has no final trim and the eQuest
              focus is on cooling.  You have also bumped into another
              limit on cooling capacity.  You are correct that the
              cooling capacity is dependent on the delta-T and the air
              flow.  There are 2 delta-T's, the one on your water and
              the one on your air.  You can play with the water one all
              day but if you don't have enough air you won't get
              anywhere.  Equest has a default on the airflow to a zone
              that is 0.6 cfm/SF.  Your main AHU maximum flow will be
              based on this value for the sum of all the zones it is
              supplying.  Most of the time this value is too small for a
              sun side perimeter zone.<br>
              I would start with the zone with the worst unmet hours. 
              You want to use zone reports, start with LS-A which will
              give you your peak heating and cooling loads for all your
              zones.  LS-B will give you the components of that load
              except OA.  SS-R is handy.  Keep an eye on SV-A, it will
              list the zones and their airflow's as sub-components of
              the main AHU.<br>
              You want to go to the air-side HVAC tab and select the
              zone you want to work on.  Right click and select
              "Properties".  In the "Basic Specifications" tab you will
              see on the right side half way down "Zone Design Flow
              Rates", the first value is "Min Design Flow" and is
              probably set at 0.6 cfm/SF, start increasing this value. 
              You may need to be in the 1.2 cfm/SF range, it depends on
              the zone and the cooling load.    You can calculate what
              you need too.  As you bring the number up you will see the
              AHU airflow increase and also the cooling/heating capacity
              of the AHU increase in SV-A.  Remember that you just want
              enough air.  Excess air moving wastes energy.  Your unmet
              hours should be decreasing for that zone.  Some of the
              other zones will begin to decrease as well but your main
              problem zones should still have unmet hours.  Deal with
              each one the same way.<br>
              Remember this, it is probably THE most important setting
              in eQuest on the air side.<br>
              Bruce Easterbrook P.Eng.<br>
              Abode Engineering<br>
              <br>
            </font>
            <div class="ecxmoz-cite-prefix">On 24/08/2012 05:16 PM, John
              Shen wrote:<br>
            </div>
            <blockquote
              cite="mid:COL113-W411E3BE1CB2180FA45F796EDBD0@phx.gbl">
              <style><!--
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}

--></style>
              <div dir="ltr"> Thank you for the response, couldn't have
                asked for a better explanation.
                <div><br>
                </div>
                <div> I was able to get the heat unmet hours down to a
                  reasonable range. However, I am having difficulties
                  with the Cool unmet hours. It appears I am unable to
                  acquire any cooling capacity which is resulting in a
                  few unmet hours (~150). As mentioned the heating
                  capacity is dependent on the reheat delta t and
                  airflow. I can't seem to find a place to enter delta T
                  for cooling, I have coil delta T set along with an
                  appropriate CHW loop. Yet I don't get any cooling in
                  any of my zones in the SS-G section of the report.
                  Any further help would be appreciated.</div>
                <div><br>
                </div>
                <div>John<br>
                  <br>
                  <div>
                    <hr id="ecxstopSpelling">Date: Fri, 24 Aug 2012
                    09:57:49 -0400<br>
                    From: <a moz-do-not-send="true"
                      class="ecxmoz-txt-link-abbreviated"
                      href="mailto:bruce5@bellnet.ca">bruce5@bellnet.ca</a><br>
                    To: <a moz-do-not-send="true"
                      class="ecxmoz-txt-link-abbreviated"
                      href="mailto:johnshen1@hotmail.com">johnshen1@hotmail.com</a><br>
                    CC: <a moz-do-not-send="true"
                      class="ecxmoz-txt-link-abbreviated"
                      href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                    Subject: Re: [Equest-users] Power induction unit/
                    reheat delta T<br>
                    <br>
                    <font size="+1"><font face="Times New Roman, Times,
                        serif">You can try changing your interior
                        control zone as this will effect the base
                        capacity that the AHU will supply to the floor. 
                        As for the exterior zones your heat/cool
                        capacity is based on the delta-T and the
                        airflow.  You said you specified the air flow. 
                        Let eQuest auto-size the flow.  By specifying
                        the air flow you have removed most of eQuest's
                        ability to adjust capacity.  One other thing to
                        remember is eQuest is working on the maximum
                        flow as well as all the intermediate conditions
                        as well.  It is these intermediate loads which
                        will trigger most of your unmet hours.  As the
                        sun moves across your exterior zones through the
                        day the peak load will be shifting through the
                        exterior zones as well.  So a zone which was the
                        peak at 10 am won't be the peak at 3 pm.  eQuest
                        will count an unmet hour if you are high or low
                        on a zones temperature.  By specifying the cfm
                        to the zone I would guess you may be over
                        cooling some of the zones and triggering unmet
                        hours.  eQuest, if allowed, would reduce the
                        airflow to the 10 am zone later in the day and
                        shift the CFM to the 3 pm zone.  This is mostly
                        under the hood stuff and you have to drill
                        pretty deep into your reports to have an idea of
                        what is going on and you won't find the direct
                        answer as to the lower cfm to the zone.  You can
                        get an idea of the heat/cool capacity eQuest is
                        dealing with in each and follow it across the
                        building.<br>
                        Bruce Easterbrook P.Eng.<br>
                        Abode Engineering.<br>
                        <br>
                      </font></font>
                    <div class="ecxmoz-cite-prefix">On 23/08/2012 01:56
                      PM, John Shen wrote:<br>
                    </div>
                    <blockquote
                      cite="mid:COL113-W42CBA256ABB1E18AE29E3BEDBE0@phx.gbl">
                      <style><!--
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}

--></style>
                      <div dir="ltr">
                        <p class="ecxMsoNormal">Working on a building
                          with an air handling unit which serves the
                          entire floor. In the exterior rooms there are
                          Fan coils to supply further heating and
                          cooling to the floor. I have split the floor
                          up into interior zones and exterior zones
                          (each containing a fan coil unit). The AHU I
                          have modeled as a power induction unit which
                          serves all the zones on the floor, the
                          interior zones have terminal type std VAV and
                          the exterior zones have series PIU. With in
                          the exterior zones I have specified flow
                          rates, heat/cool capacity reflecting the FC.
                          However I am getting lots of unmet hours from
                          these exterior zones (~500 hrs each). I
                          inputted a REHEAT-DELTA-T in of 57F (based on
                          fan flow rates and heat capacity) into each of
                          the exterior zones. This greatly reduced the
                          unmet hours; however I find it strange because
                          the unmet hours are completely dependent on
                          REHEAT-DELTA-T and completely independent of
                          the zone heat capacity. I appear to have a
                          poor understanding of how the PIU system
                          works, if anyone could provide further insight
                          it would be much appreciated.</p>
                        <p class="ecxMsoNormal"><br>
                        </p>
                        <p class="ecxMsoNormal">John</p>
                      </div>
                      <br>
                      <fieldset class="ecxmimeAttachmentHeader"></fieldset>
                      <br>
                      <pre>_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
                    </blockquote>
                    <br>
                  </div>
                </div>
              </div>
              <br>
              <fieldset class="ecxmimeAttachmentHeader"></fieldset>
              <br>
              <pre>_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="ecxmoz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="ecxmoz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
            </blockquote>
            <br>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>