The U-factor reported in the .sim file includes the frame effects - if
frames have been modelled. If frames are modelled, each
window may have a different U-factor <br>
depending on the size of the window vs the amount of framing. A
smaller window will have a poorer U-factor. <br><br>
The other issue is that the Simplified method asks for the Glass
Conductance - not the U-factor. <br>
From the DOE22Vol2-Dictionary_47f.pdf manual:<br><br>
GLASS-CONDUCTANCE<br>
The conductance of the glazing, excluding the outside air film
coefficient. The conductance given in glass manufacturers' data sheets
usually includes the outside air film resistance for a wind speed of 7.5
mph (summer) or 15 mph (winter). Table 10 can be used to obtain the
corresponding value of GLASS-CONDUCTANCE. For example, if U(7.5 mph) =
0.64 Btu/ft2-hr-F, then GLASS-CONDUCTANCE = 0.79 (by interpolation). For
Uvalues of different glazing types, see manufacturers' data sheets or the
ASHRAE 1989 Handbook of Fundamentals, <br>
p. 27.16-17.<br><br>
<img src="cid:.0" width=483 height=269 alt="Emacs!"><br><br>
<br>
At 05:01 PM 03/09/2012, Andres Franco wrote:<br>
<blockquote type=cite class=cite cite="">Content-Type:
multipart/related;<br>
<x-tab> </x-tab>
boundary="----=_NextPart_000_0010_01CD89ED.58B2F4F0"<br>
Content-Language: es-co<br><br>
Hi there, I´m working in a medium size project of a warehouse, apparently
all in eQuest is working fine but when I saw the results for
the glass in all my windows the U-Factor values are wrong, I want to know
if somebody has already had this problem or if exists any formula or
something for make an input accurately for the glass factor values in a
correct way, thanks in advance, best regards.<br>
<br><br>
<br><br>
<br>
__________ Información de ESET NOD32 Antivirus, versión de la base de
firmas de virus 7442 (20120903) __________<br><br>
ESET NOD32 Antivirus ha comprobado este mensaje.<br><br>
<a href="http://www.eset.com">http://www.eset.com</a><br><br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
<br>
To unsubscribe from this mailing list send a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
>><br>
Christopher Jones, P.Eng.<br>
Suite 1801, 1 Yonge Street<br>
Toronto, ON M5E1W7<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br>
email cj@enersave.ca<br>
</body>
</html>