Interesting.  When this first popped up I thought it only applied to warehouses, but with the addition of exception (e) to G3.1.1 it would appear this can be used for stairwells, vestibules, mechanical rooms.<div><br></div>
<div>Thanks for the info.</div><div><br></div><div><div>Robby Oylear, PE, LEED AP</div><div>Mechanical Engineer</div><div>Senior Energy Analyst</div><div><br></div><div>D 206-788-4571</div><div><a href="http://www.rushingco.com">www.rushingco.com</a></div>
<div><br></div><br><div class="gmail_quote">On Thu, Aug 30, 2012 at 1:13 PM, Stormy L. Shanks <span dir="ltr"><<a href="mailto:shankssl@kjww.com" target="_blank">shankssl@kjww.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">






<div lang="EN-US" link="blue" vlink="purple">
<div>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Hi, Karen – You can follow addendum dn to ASHRAE 90.1 2007. You can find a PDF of it by googling “addendum dn”. It addresses this situation with the addition
 of HVAC baseline system types 10 and 11, which are for “heated only storage.” I’m still working on fully understanding the addendum myself for a similar building – a hangar with attached office/support. Prior to this addendum, you would have had to model the
 warehouse with cooling even though there isn’t any. The typical loophole was to set thermostat schedules with really high setpoints in cooling mode in the hopes of the cooling never turning on, which sort of worked, but the addendum should make it much more
 realistic. <u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Good luck!<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">Stormy Shanks, PE</span></b><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><u></u><u></u></span></p>

<p class="MsoNormal" style="margin-bottom:12.0pt"><span style="font-size:10.0pt;font-family:"Arial","sans-serif"">Mechanical Engineer
<u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:10.0pt;font-family:"Arial","sans-serif""><a href="http://www.kjww.com/" target="_blank"><span style>www.kjww.com</span></a><u></u><u></u></span></p>
<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p>
<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Karen Smith<br>
<b>Sent:</b> Thursday, August 30, 2012 2:51 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Warehouse configuration on Ashrae<u></u><u></u></span></p><div><div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Hi all,<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Im a bit confused with the classification of Ashrae 90.1 2007, Im currently modeling a facility of a total of 47,600 SF including a 28,000 SF Warehouse. The facility includes 2
 levels of offices, breakrooms, etc and a double height warehouse adjacent to them. The proposed design is composed of   2 AHUs, one for the first floor, one for the second and a only heating and ventilation system based on 2 boilers for the warehouse. According
 to this, the baseline should be a System 5 Packaged VAV with Reheat, Packaged rooftop VAV with reheat, Direct expansion cooling type and  Hot-water fossil fuel boiler for heating. One system per floor, but my confusion is on the part of the warehouse. Should
 I model an additional Cool and Heat System for the warehouse even though in the proposed we have it as only heating and ventilation system? If so, does it have to be the same type of system specified (System 5) or can it be System 3 or 4 instead?<u></u><u></u></p>

<p class="MsoNormal"> <u></u><u></u></p>
<p class="MsoNormal">Thanks.<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<p class="MsoNormal">Karen Smith<u></u><u></u></p>
<p class="MsoNormal">Sustainable Solutions, Inc<u></u><u></u></p>
<p class="MsoNormal"><a href="tel:%28404%29%20784.7061" value="+14047847061" target="_blank">(404) 784.7061</a><u></u><u></u></p>
</div></div></div>
<br><br>
<hr>
<i>This message and any attachments contain information intended for a specific party and may include sensitive or confidential material. If you are not the intended recipient, please do not read, copy, use, or disclose to others.  Please notify the sender of the delivery error by reply and then permanently delete this message and all attachments.</i>
<br>
  ­­  </div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>