<html>
<head>
<style><!--
.hmmessage P
{
margin:0px;
padding:0px
}
body.hmmessage
{
font-size: 10pt;
font-family:Tahoma
}
--></style></head>
<body class='hmmessage'><div dir='ltr'>
Thank you for the response, couldn't have asked for a better explanation.<div><br></div><div> I was able to get the heat unmet hours down to a reasonable range. However, I am having difficulties with the Cool unmet hours. It appears I am unable to acquire any cooling capacity which is resulting in a few unmet hours (~150). As mentioned the heating capacity is dependent on the reheat delta t and airflow. I can't seem to find a place to enter delta T for cooling, I have coil delta T set along with an appropriate CHW loop. Yet I don't get any cooling in any of my zones in the SS-G section of the report. Any further help would be appreciated.</div><div><br></div><div>John<br><br><div><div id="SkyDrivePlaceholder"></div><hr id="stopSpelling">Date: Fri, 24 Aug 2012 09:57:49 -0400<br>From: bruce5@bellnet.ca<br>To: johnshen1@hotmail.com<br>CC: equest-users@lists.onebuilding.org<br>Subject: Re: [Equest-users] Power induction unit/ reheat delta T<br><br>
<font size="+1"><font face="Times New Roman, Times, serif">You can
try changing your interior control zone as this will effect the
base capacity that the AHU will supply to the floor. As for the
exterior zones your heat/cool capacity is based on the delta-T
and the airflow. You said you specified the air flow. Let
eQuest auto-size the flow. By specifying the air flow you have
removed most of eQuest's ability to adjust capacity. One other
thing to remember is eQuest is working on the maximum flow as
well as all the intermediate conditions as well. It is these
intermediate loads which will trigger most of your unmet hours.
As the sun moves across your exterior zones through the day the
peak load will be shifting through the exterior zones as well.
So a zone which was the peak at 10 am won't be the peak at 3
pm. eQuest will count an unmet hour if you are high or low on a
zones temperature. By specifying the cfm to the zone I would
guess you may be over cooling some of the zones and triggering
unmet hours. eQuest, if allowed, would reduce the airflow to
the 10 am zone later in the day and shift the CFM to the 3 pm
zone. This is mostly under the hood stuff and you have to drill
pretty deep into your reports to have an idea of what is going
on and you won't find the direct answer as to the lower cfm to
the zone. You can get an idea of the heat/cool capacity eQuest
is dealing with in each and follow it across the building.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering.<br>
<br>
</font></font>
<div class="ecxmoz-cite-prefix">On 23/08/2012 01:56 PM, John Shen
wrote:<br>
</div>
<blockquote cite="mid:COL113-W42CBA256ABB1E18AE29E3BEDBE0@phx.gbl">
<style><!--
.ExternalClass .ecxhmmessage P
{padding:0px;}
.ExternalClass body.ecxhmmessage
{font-size:10pt;font-family:Tahoma;}
--></style>
<div dir="ltr">
<p class="ecxMsoNormal">Working on a building with an air handling
unit which serves
the entire floor. In the exterior rooms there are Fan coils to
supply further heating
and cooling to the floor. I have split the floor up into
interior zones and
exterior zones (each containing a fan coil unit). The AHU I
have modeled as a
power induction unit which serves all the zones on the floor,
the interior
zones have terminal type std VAV and the exterior zones have
series PIU. With
in the exterior zones I have specified flow rates, heat/cool
capacity
reflecting the FC. However I am getting lots of unmet hours
from these exterior
zones (~500 hrs each). I inputted a REHEAT-DELTA-T in of 57F
(based on fan flow
rates and heat capacity) into each of the exterior zones. This
greatly reduced
the unmet hours; however I find it strange because the unmet
hours are
completely dependent on REHEAT-DELTA-T and completely
independent of the zone
heat capacity. I appear to have a poor understanding of how
the PIU system
works, if anyone could provide further insight it would be
much appreciated.</p>
<p class="ecxMsoNormal"><br>
</p>
<p class="ecxMsoNormal">John</p>
</div>
<br>
<fieldset class="ecxmimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
Equest-users mailing list
<a class="ecxmoz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="ecxmoz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br></div></div> </div></body>
</html>