    Lee-<br>
    The EIR modefier curve acts as a multiplier on the COOLING-EIR
    value, which is the the reciprocal of the COP.  Therefore, if you
    multiply the your curve values times the COOLING-EIR and take the
    inverse, you will see that the efficiency is actually decreasing,
    approaching COP=1.0 at low temperatures.  Keep in mind that this
    curve is not the only EIR modifier curve, there is also the PLR
    curve...<br>
    <br>
    -David<br>
    <br>
    <div class="moz-cite-prefix">On 8/22/2012 9:18 AM, Lee Chorney
      wrote:<br>
    </div>
    <blockquote
cite="mid:CAGHHzOCK69+w9JYbzkEGn7Bfhfo=rov_LrDQiH0xyo5_OqTZrQ@mail.gmail.com"
      type="cite">Hi Everybody,<br>
      <br>
      Does anyone understand the heating EIR curves used for PTACS in
      Equest? It is the "DX-Heat-EIR-fEDB&OAT" curve. I calculated
      the curve using excel (see attached spreadsheet) and found as the
      outside air gets colder the efficiency of the heating curve
      increases. Does that make sense to anyone?<br>
      <br>
      Thanks in advance,<br>
      <br>
      Lee <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>