>From what I see from these input files, the zone AC/Hr went from 0.2 to 0.8.  I did not note a change in any R-value from 4 to 20.  The increased ventilation load is the likely culprit.<br><br><div class="gmail_quote">On Wed, Aug 22, 2012 at 1:42 PM, Lee Chorney <span dir="ltr"><<a href="mailto:leec@alliedconsulting.net" target="_blank">leec@alliedconsulting.net</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi Guys,<br><br>Here all the .inp files. 1.inp is the base and 2.inp is the proposed.<br><br>Thank you,<br><br>Lee<div class="HOEnZb">
<div class="h5"><br><br><div class="gmail_quote">On Wed, Aug 22, 2012 at 12:48 PM, Lee Chorney <span dir="ltr"><<a href="mailto:leec@alliedconsulting.net" target="_blank">leec@alliedconsulting.net</a>></span> wrote:<br>

<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi All,<br><br><br>I recently did a model where I had the same system in both base and proposed but I changed the R-Value from 4 (base) to 20 (proposed). I also changed the window U-value from .80 (base) to .35 (proposed). After I did the run, I saw only a 5% savings between the heating and cooling use in the model. When I looked at the loads I saw the base had twice as much cooling and heating load than the proposed. Does any know why the energy savings would only be 5% when you have a huge difference between the cooling and heating loads?<br>


<br>Thanks,<br><br>Lee<br>
</blockquote></div><br>
</div></div><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><br>-- <br>Ron Pecarina, PE, CEM, LEED-AP BD&C<br>Energy and Sustainable Design Consultants, Inc.<br>1128 Noblewood Drive<br>Billings, MT   59101<br>406-208-0227<br>