    i think a little clarification would help.  as far as i can tell:<br>
    <br>
    is the water heating system in place because 1) the building has
    been built & is being claimed for 179d as part of a new
    construction partially or fully qualifying building or 2) is it in
    place because the building is being renovated?<br>
    <br>
    if it is in place due to 1) above then you should be using part B,
    if it is in place due to 2) above then you should be using part A if
    it is not being touched.<br>
    <br>
    don't forget the minimum requirements in 179d & the nrel
    guidelines 40467.pdf (just google it if you don't have it) are for
    90.1-2001 and unless documented separately the loads and schedules
    are per the nrel appendix c (c<span style="font-size: 9.000000pt;
      font-family: 'ArialMT'">alifornia Nonresidential ACM Approval
      Manual Tables N2-2 and N2-3)</span><br>
    <br>
    <br>
    <br>
    On 8/20/12 3:50 PM, Daniel Sze wrote:
    <blockquote
cite="mid:CABsmQGot8OFYwDi_njEVhFqcQu0_s=DCmWfj68R7J6HZJGuXDA@mail.gmail.com"
      type="cite">Hello people,
      <div><br>
      </div>
      <div>I am working on a 179D project for a client and I need help
        in interpreting a requirement of Appendix G in the ASHRAE
        Standard 90.1.2004.</div>
      <div><br>
      </div>
      <div>For domestic how water systems, App G says that you should
        follow part A for the baseline if a HW system is already in
        place or part B if a new HW systems is to be installed in the
        future.</div>
      <div><br>
      </div>
      <div>Since the client's factory's HW system is in place, shall I
        follow part A even though the system might be significantly
        different from the one specified in the Standard that meets the
        minimum requirements?</div>
      <div><br>
      </div>
      <div>Thank you in advance.</div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>