The PSZ system requires a CONTROL-ZONE if there is more than one zone on
the system. If one conditioned zone is not named as the
CONTROL-ZONE then the first zone after the system definition is assumed
to be the control zone. A control zone cannot be
unconditioned. <br><br>
The fix is to enter Detailed Edit mode, change to Air Side HVAC, select
the System and name the Control Zone - from the list, I selected EL1 SSW
as it is the only conditioned zone on the system. <br><br>
The file opens correctly but I don't believe you can switch back to the
Wizard Mode.<br><br>
At 07:35 AM 06/08/2012, ramesh buddhi wrote:<br>
<blockquote type=cite class=cite cite="">Dear Folks<br><br>
<font size=2>I had modeled an nine storey office Building Iam getting an
BDL error that zone is inconsistent with definition: The reference
expected a definition as TYPE= Conditioned. I designed this as an
unconditioned. How to get rid of this error? Please kindly help me on
this. I had attached the files for your reference along with the weather
file.Thanks a lot in advance.<br><br>
Thanks<br>
Ramesh BR</font> <br>
<font face="verdana" color="#00BF60"><br>
</font><font face="verdana"> New No.110 / Survey No. 151/1, Mahatma
Gandhi Road <br>
Thiruvanmiyur, Chennai 600041 INDIA<br>
Web:
<a href="http://www.greenevolution.in/" eudora="autourl">
www.greenevolution.in</a><br>
Land: +91-44-4201-8369<br>
Cell : +91-99406-19915<br>
</font></blockquote>
<x-sigsep><p></x-sigsep>
>><br>
Christopher Jones, P.Eng.<br>
Suite 1801, 1 Yonge Street<br>
Toronto, ON M5E1W7<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br>
email cj@enersave.ca<br>
</body>
</html>