<font color="#336666"><font face="verdana,sans-serif">Paul,</font></font><div><font color="#336666"><font face="verdana,sans-serif">Great points- I do not think that there will be any systems serving both sides but I will now double check, also will look into the previous space use and HVAC type to be sure about the baseline envelope</font></font></div>

<div><font color="#336666"><font face="verdana,sans-serif"><br></font></font></div><div><font color="#336666"><font face="verdana,sans-serif"> -Thank you for your input.</font></font></div><div><font color="#336666"><font face="verdana,sans-serif"><br>

</font></font></div><div><font color="#336666"><font face="verdana,sans-serif"><br clear="all"></font></font><div style="text-align:left"><font face="verdana, sans-serif" color="#999999"><i>Jeremiah D. Crossett</i></font></div>

<div style="text-align:left"><font face="verdana, sans-serif" color="#999999"><i>CleanTech Analytics</i></font></div><div style="text-align:left"><font face="verdana, sans-serif" color="#999999"><i>503-688-8951</i></font></div>

<div><div style="text-align:left"><a href="http://www.cleantechanalytics.com" target="_blank"><font face="verdana, sans-serif" color="#999999"><i>www.cleantechanalytics.com</i></font></a></div><div><div style="text-align:center">

<br></div><div style="text-align:center"><img src="http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG"><br></div></div></div><div><div><b><p dir="ltr" style="text-align:center;margin-top:0pt;margin-bottom:0pt">

<span style="font-size:11px;font-family:'Droid Serif';color:rgb(204,204,204);background-color:rgb(255,255,255);font-weight:normal;font-style:italic;text-decoration:none;vertical-align:baseline;white-space:pre-wrap">This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics</span></p>

</b></div></div><br>
<br><br><div class="gmail_quote">On Thu, Aug 2, 2012 at 1:39 PM, Paul Riemer <span dir="ltr"><<a href="mailto:Paul.Riemer@dunhameng.com" target="_blank">Paul.Riemer@dunhameng.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

<div lang="EN-US" link="blue" vlink="purple"><div><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">I agree and suggest you model the common wall (#1) as adiabatic, assuming no services will cross the wall and all the spaces are currently conditioned spaces.  If you have an air, water, or refrigerant system serving both sides of the wall, you will have to take the whole system.  And if you are converting a semiheated or unconditioned space, use some judgment on the baseline envelope.  <u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">As a tangent, we may need to improve the definitions of conditioned space in ASHRAE 90.1.  Classifying conditioned/semiheated/unconditioned based on the output capacity of the heating equipment seems problematic, especially for the hyper-insulating & Passive House devotees.<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d">Happy modeling.<u></u><u></u></span></p>

<p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><div><p class="MsoNormal" style="text-autospace:none"><b><span style="font-size:9.0pt;font-family:"Verdana","sans-serif";color:#5f574f">Paul Riemer, PE, LEED AP BD+C</span></b><span style="font-size:9.0pt;font-family:"Calibri","sans-serif";color:#1f497d"> <u></u><u></u></span></p>

<p class="MsoNormal" style="text-autospace:none"><span style="font-size:7.5pt;font-family:"Verdana","sans-serif";color:#5f574f">Associate / Mechanical</span><span style="font-size:7.5pt;font-family:"Verdana","sans-serif";color:#1f497d"><u></u><u></u></span></p>

<p class="MsoNormal"><b><span style="font-family:"Verdana","sans-serif";color:#c00000">DUNHAM</span></b><span style="font-size:11.0pt;font-family:"Verdana","sans-serif";color:#c00000"><u></u><u></u></span></p>

</div><p class="MsoNormal"><span style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1f497d"><u></u> <u></u></span></p><div><div style="border:none;border-top:solid #b5c4df 1.0pt;padding:3.0pt 0in 0in 0in">

<p class="MsoNormal"><b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span style="font-size:10.0pt;font-family:"Tahoma","sans-serif""> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>Ritwik Kakati<br>

<b>Sent:</b> Thursday, August 02, 2012 3:01 PM<br><b>To:</b> CleanTech Analytics; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br><b>Subject:</b> Re: [Equest-users] Existing Building, LEED NC<u></u><u></u></span></p>

</div></div><div><div class="h5"><p class="MsoNormal"><u></u> <u></u></p><div><p class="MsoNormal">Jeremiah,<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">We recently submitted an energy model for the renovation of an existing building to USGBC (for NC 2009), and although the first round of comments came back and my model is still not perfect yet, I can answer what I did to your questions 2, 3 & 4:<u></u><u></u></p>

<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">2. Did not rotate the baseline and take averages. Only submitted the baseline for actual orientation.<u></u><u></u></p><p class="MsoNormal">3. Baseline constructions were existing conditions before the building was renovated.<u></u><u></u></p>

<p class="MsoNormal">4. HVAC system was based on Appendix G of 90.1, not the current/existing system in the building. <u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">For all the above, USGBC so far has not raised any comments/objections for my model, so I am hoping I am correct.<u></u><u></u></p>

<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Hope this helps.<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Thanks,<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p>

<p class="MsoNormal">Ritwik Kakati, LEED Green Associate<u></u><u></u></p><p class="MsoNormal">Design Engineer<u></u><u></u></p><p class="MsoNormal">DAGHER ENGINEERING, PLLC<u></u><u></u></p><p class="MsoNormal">29 Broadway, New York, NY 10006<u></u><u></u></p>

<p class="MsoNormal">T. <a href="tel:212.480.2591%20x140" value="+12124802591" target="_blank">212.480.2591 x140</a><u></u><u></u></p><p class="MsoNormal">F. <a href="tel:212.480.2654" value="+12124802654" target="_blank">212.480.2654</a><u></u><u></u></p>

<p class="MsoNormal"><a href="mailto:rkakati@dagherengineering.com" target="_blank">rkakati@dagherengineering.com</a><u></u><u></u></p><p class="MsoNormal"><a href="http://www.dagherengineering.com" target="_blank">www.dagherengineering.com</a><u></u><u></u></p>

<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">Save Trees, Consider the Environment. Please print only when necessary.<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal">This email and any attachments may contain confidential or proprietary information and use or distribution is strictly prohibited. If you are not the intended recipient, please notify us and delete.  Dagher Engineering, PLLC has no responsibility for errors or discrepancies that may occur in the electronic transmission of data.<u></u><u></u></p>

<p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><u></u> <u></u></p><p class="MsoNormal"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] <b>On Behalf Of </b>CleanTech Analytics<br>

<b>Sent:</b> Thursday, August 02, 2012 3:16 PM<br><b>To:</b> <a href="mailto:bldg-sim@lists.onebuilding.org" target="_blank">bldg-sim@lists.onebuilding.org</a>; <a href="mailto:EnergyPlus_Support@yahoogroups.com" target="_blank">EnergyPlus_Support@yahoogroups.com</a>; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>

<b>Subject:</b> [Equest-users] Existing Building, LEED NC<u></u><u></u></p><p class="MsoNormal"><u></u> <u></u></p><div><p class="MsoNormal">Good day to all..<u></u><u></u></p></div><div><p class="MsoNormal"><u></u> <u></u></p>

</div><div><p class="MsoNormal">Working on modeling an existing building per 90.1 for LEED certification and can not find clear answers in the standard or users guide- and seeking of the advise of the Bidg-Sim community- <u></u><u></u></p>

</div><div><p class="MsoNormal">The building is basically a shell- the 6 inch tilt up concrete walls and concrete floor are the only things remaining un-changed. The building is installing new HVAC systems, a new roof, a new lighting systems, new skylights, new doors, new windows and insulating the existing walls. The space is 35,000 square feet, and beside another building. The building owners bought out their former neighbor and are expanding into their space, the space shares a wall with their current space. <u></u><u></u></p>

</div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><ol start="1" type="1"><li class="MsoNormal">Adiabatic wall- Should it be Modeled with an adiabatic wall separating the "two" buildings (that are actually one building with a separating wall and separate address), or should the "other building" not seeking LEED certification be included in the model?<u></u><u></u></li>

<li class="MsoNormal">Rotated average baseline- This is an existing building and orientation is set, so is this procedure still necessary or required by 90.1/LEED<u></u><u></u></li><li class="MsoNormal">Baseline Constructions- Should the baseline reflect the walls as they where before renovation (Un insulated tilt up concrete walls/R-5 roof deck?) or should it use the ASHRAE light weight constructions with 2007 insulation for the climate, or should it use the actual constructions but add ASHRAE 2007 insulation?<u></u><u></u></li>

<li class="MsoNormal">The HVAC system is a CAV, with convective natural gas heating and and DX cooling- roof top units, the baseline system for this should be system # 5 PVAV- or should the baseline HVAC system be what ever system was in the building before the renovation?<u></u><u></u></li>

</ol></div><div><p class="MsoNormal"><u></u> <u></u></p></div><div><div><p class="MsoNormal">An advanced thank you goes out to all that respond- <u></u><u></u></p></div><p class="MsoNormal"><u></u> <u></u></p></div><div>
<p class="MsoNormal">
<u></u> <u></u></p></div><p class="MsoNormal"><br clear="all"><u></u><u></u></p><p class="MsoNormal"><i>Jeremiah D. Crossett</i><u></u><u></u></p><p class="MsoNormal"><i>CleanTech Analytics</i><u></u><u></u></p><p class="MsoNormal">

<i><a href="tel:503-688-8951" target="_blank">503-688-8951</a></i><u></u><u></u></p><div><p class="MsoNormal"><a href="http://www.cleantechanalytics.com" target="_blank"><i>www.cleantechanalytics.com</i></a><u></u><u></u></p>

<div><p class="MsoNormal" align="center" style="text-align:center"><u></u> <u></u></p><p class="MsoNormal" align="center" style="text-align:center"><img border="0"><u></u><u></u></p></div></div><div><div><p align="center" style="text-align:center">

<i>This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics</i><b><u></u><u></u></b></p>

</div></div><p class="MsoNormal"><u></u> <u></u></p></div></div></div></div></div></blockquote></div><br></div>