Christina,<br>
<br>
The eQUEST web site provides a utility program that converts from
the EnergyPlus *.EPW format to the DOE-2 *.BIN format used in
eQUEST. It's a very simple one-shot process, and you don't need any
other procedures. I think the PDF to which you referred is talking
about customizing an existing weather file, not converting a weather
file from another format, e.g., EPW, to what eQUEST uses.<br>
<br>
Joe<br>
<br>
On 7/25/2012 9:46 AM, Christina Gerometta wrote:
<blockquote
cite="mid:CC358D1E.618%25christina.gerometta@btu-engineering.com"
type="cite">
<meta http-equiv="Context-Type" content="text/html;
charset=US-ASCII">
<div>Hello, </div>
<div><br>
</div>
<div>I am trying to convert real time hourly weather files (taken
from the energyplus request site) into a .bin file to use in
eQuest. I have been referencing the instructions:</div>
<div><br>
</div>
<div><span><a moz-do-not-send="true"
href="http://bepan.info/yahoo_site_admin/assets/docs/7_-_Customizing_eQUEST_Weather_Data_by_Jeff_Hirsch.138125735.pdf">http://bepan.info/yahoo_site_admin/assets/docs/7_-_Customizing_eQUEST_Weather_Data_by_Jeff_Hirsch.138125735.pdf</a></span></div>
<div><br>
</div>
<div>However, the instructions refer to an excel document that I
cannot find. I did find one here (Item 12):</div>
<div><br>
</div>
<div><a moz-do-not-send="true" href="http://bepan.info/weather">http://bepan.info/weather</a></div>
<div><br>
</div>
<div> But I am not sure if this will work. Does anyone have an
easier approach? Any advice would be much appreciated! </div>
<div> <br>
</div>
<div> Thanks, </div>
<div> Christina </div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
<br>
<div class="moz-signature">-- <br>
Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga, CA 94556
(o) (925)388-0265
(c) (510)928-2683
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
"Building energy simulations at your fingertips"</div>
</body>
</html>