<div>You might want to verify with Compare-it! or another file difference software that no other changes were inadvertently made.</div>
<div><br>
</div>
<div>Assuming none, also verify that the changes are actually from the loads and not something in the system configuration by comparing the zone <span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.292969); -webkit-composition-fill-color: rgba(175, 192, 227, 0.230469); -webkit-composition-frame-color: rgba(77, 128, 180, 0.230469); ">component </span><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.296875); -webkit-composition-fill-color: rgba(175, 192, 227, 0.230469); -webkit-composition-frame-color: rgba(77, 128, 180, 0.230469); ">load
reports for the two cases. This would help you identify an AHU controllability issue separate from the magnitude of the zone loads.</span></div>
<div><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.296875); -webkit-composition-fill-color: rgba(175, 192, 227, 0.230469); -webkit-composition-frame-color: rgba(77, 128, 180, 0.230469); "><br>
</span></div>
<div><span class="Apple-style-span" style="-webkit-tap-highlight-color: rgba(26, 26, 26, 0.296875); -webkit-composition-fill-color: rgba(175, 192, 227, 0.230469); -webkit-composition-frame-color: rgba(77, 128, 180, 0.230469); ">One thing you mention in the
original message is that the spaces with the large windows "get heated up" - did the model accurately reflect the actual and proposed IEQ for the spaces?</span></div>
<div><br>
DSE Mobile</div>
<div><br>
On Jul 15, 2012, at 8:52 PM, "CleanTech Analytics" <<a href="mailto:jeremiah@cleantechanalytics.com">jeremiah@cleantechanalytics.com</a>> wrote:<br>
<br>
</div>
<div></div>
<blockquote type="cite">
<div><font face="verdana,sans-serif" style="color:rgb(51,102,102)">So if the curve theory is correct I wonder if this would happen
</font><font>in </font><span style="color:rgb(51,102,102);font-family:verdana,sans-serif">other modeling software</span> <font color="#336666"><font face="verdana,sans-serif"> or more importantly in the real world>? --reduce internal gain and increase cooling
consumption-- or if this phenomena is only possible in the virtual world of eQuest..,,</font></font>
<div><font color="#336666" face="verdana, sans-serif"><br>
</font></div>
<div><font color="#336666" face="verdana, sans-serif">Joe-Liam-Paul what do you think >?<<br>
</font>
<div><font color="#336666"><font face="verdana,sans-serif"><br>
</font></font></div>
<div><font color="#336666"><font face="verdana,sans-serif"><br clear="all">
</font></font>
<div style="text-align:left"><font face="verdana, sans-serif" color="#999999"><i>Jeremiah D. Crossett</i></font></div>
<div style="text-align:left"><font face="verdana, sans-serif" color="#999999"><i>CleanTech Analytics</i></font></div>
<div style="text-align:left"><font face="verdana, sans-serif" color="#999999"><i>503-688-8951</i></font></div>
<div>
<div style="text-align:left"><a href="http://www.cleantechanalytics.com" target="_blank"><font face="verdana, sans-serif" color="#999999"><i>www.cleantechanalytics.com</i></font></a></div>
<div>
<div style="text-align:center"><br>
</div>
<div style="text-align:center"><img src="http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG"><br>
</div>
</div>
</div>
<div>
<div><b>
<p dir="ltr" style="text-align:center;margin-top:0pt;margin-bottom:0pt"><span style="font-size:11px;font-family:'Droid Serif';color:rgb(204,204,204);background-color:rgb(255,255,255);font-weight:normal;font-style:italic;text-decoration:none;vertical-align:baseline;white-space:pre-wrap">This
document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form without the prior written consent of CleanTech Analytics</span></p>
</b></div>
</div>
<br>
<br>
<br>
<div class="gmail_quote">On Sun, Jul 15, 2012 at 5:47 PM, Peter Baumstark <span dir="ltr">
<<a href="mailto:pbaumstark@sbcglobal.net" target="_blank">pbaumstark@sbcglobal.net</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div>
<div style="font-family:arial,helvetica,sans-serif;font-size:12pt">It's an interesting problem. With this model, no matter what I do, if I manually change the SHGC or SC (if I use the U-Value method), or if I select different glazing types from the library
(with different SHGC values), no matter what face of the building I change it, I get an increase in overall monthly energy use with a lower SHGC.<br>
<br>
I built the model through a zone by activity area method that pretty closely matches the various zones of the building. It's a VAV with terminal reheat system (1995 Trane Intellipaks), and I entered actual economizer, static pressure and SAT settings. Airflow
matches as-built design drawings.<br>
<br>
I tried using other eQUEST models I've built for other customers using similar methods, changed the location to San Jose, and ran window cases and results were as expected.<br>
<br>
I'm coming to believe that one issue with the building in question is the RTUs seem over sized relative to the use patterns and internal heat gains. This building previously had various lab areas, then was purchased by another customer with lower internal
heat load rates, but they kept the same RTUs.<br>
<br>
Could it be possible that the lower heat gains from better fenestration products could place the RTUs at a more inefficient spot on its performance curve? I've ran into similar issues with chilled water systems, but never looked at DOE-2 performance curves
for DX units.<br>
<br>
Pete<br>
<div><br>
</div>
<div style="font-family:arial,helvetica,sans-serif;font-size:12pt"><br>
<div style="font-family:times new roman,new york,times,serif;font-size:12pt"><font face="Tahoma">
<hr size="1">
<b><span style="font-weight:bold">From:</span></b> Paul Diglio <<a href="mailto:paul.diglio@sbcglobal.net" target="_blank">paul.diglio@sbcglobal.net</a>><br>
<b><span style="font-weight:bold">To:</span></b> Joe Huang <<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>>; CleanTech Analytics <<a href="mailto:jeremiah@cleantechanalytics.com" target="_blank">jeremiah@cleantechanalytics.com</a>><br>
<b><span style="font-weight:bold">Cc:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">
equest-users@lists.onebuilding.org</a><br>
<b><span style="font-weight:bold">Sent:</span></b> Sun, July 15, 2012 5:03:54 PM
<div>
<div class="h5"><br>
<b><span style="font-weight:bold">Subject:</span></b> Re: [Equest-users] Unexpected Custom SHGC Results<br>
</div>
</div>
</font>
<div>
<div class="h5"><br>
<div style="font-family:times new roman,new york,times,serif;font-size:12pt">Joe:<br>
<br>
I agree. I find the comment to be more than mildly offensive. <br>
<br>
I have the same experience that funky modeling results usually are the result of flawed inputs or depending on too many eQuest defaults.<br>
<div> </div>
Paul Diglio, CEM, CBCP<br>
<br>
<div>87 Fairmont Avenue<br>
New Haven, CT 06513<br>
<a href="tel:203-415-0082" value="+12034150082" target="_blank">203-415-0082</a></div>
<br>
<br>
<div><span><a rel="nofollow" href="http://www.pdigliollc.com" target="_blank">www.pdigliollc.com</a></span>
<div><br>
</div>
<div style="font-family:times new roman,new york,times,serif;font-size:12pt"><br>
<div style="font-family:times new roman,new york,times,serif;font-size:12pt"><font face="Tahoma">
<hr size="1">
<b><span style="font-weight:bold">From:</span></b> Joe Huang <<a href="mailto:yjhuang@whiteboxtechnologies.com" target="_blank">yjhuang@whiteboxtechnologies.com</a>><br>
<b><span style="font-weight:bold">To:</span></b> CleanTech Analytics <<a href="mailto:jeremiah@cleantechanalytics.com" target="_blank">jeremiah@cleantechanalytics.com</a>><br>
<b><span style="font-weight:bold">Cc:</span></b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">
equest-users@lists.onebuilding.org</a><br>
<b><span style="font-weight:bold">Sent:</span></b> Sun, July 15, 2012 7:21:54 PM<br>
<b><span style="font-weight:bold">Subject:</span></b> Re: [Equest-users] Unexpected Custom SHGC Results<br>
</font><br>
I've found this comment to be mildly offensive as well as showing a lack of understanding about how heat gains ultimately get translated to cooling energy consumption. It's extremely hard for me to believe that eQUEST or DOE-2 has been flawed for 25 years
in modeling something as fundamental as solar heat gain through windows. In all the decades I've used DOE-2 to analyze window performance for DOE's EnergyStar Program as well as numerous other projects, whenever the results did not match or ran counter to
first-principle expectations, it was always because there was some other factor that have been overlooked or ignored, chief among them being the size of the HVAC system, its configuration, and control strategy. Locations with mild cooling loads, such as San
Jose, are particularly sensitive to such system interactions. Were both runs done using "autosizing"? What<br>
kind of a system was modeled - VAV or CAV ? Did the model have an economizer? What were the HEAT-CONTROL and COOL-CONTROL strategies ? etc. It's far too early to lay blame on the DOE-2 algorithms.<br>
<br>
Joe<br>
<br>
On 7/14/2012 1:41 PM, CleanTech Analytics wrote:
<blockquote type="cite"><font color="#336666"><font face="verdana,sans-serif">Just admit it- eQuest is flawed, you don't have to make up things to protect it- </font></font>
<div>
<div><font color="#336666"><font face="verdana,sans-serif"><br>
</font></font></div>
<div><font color="#336666" face="verdana, sans-serif">If it is a mistake to use the percent points rather then percent reduced from the abrataty eQuest assumption from 1999 window specs than the it should have reduced solar heat gain by more then his product
even provided- Using the 33 percentage points but used the 33% should have provided him over stated cooling reduction, (and extra added heating consumption tradeoff) </font></div>
<div><font color="#336666" face="verdana, sans-serif"><br>
</font></div>
<div><span style="color:rgb(51,102,102);font-family:verdana,sans-serif">O- and FYI
</span>LBL<span style="color:rgb(51,102,102);font-family:verdana,sans-serif"> window does glass U-value not shading, ware-as
</span>LBL<font color="#336666" face="verdana, sans-serif"> optics can be used for film coefficients and used to create a custom glass type in window, but do not do any calculations for "shading"</font></div>
<div><span style="color:rgb(51,102,102);font-family:verdana,sans-serif"><br>
</span></div>
<div><font color="#336666" face="verdana, sans-serif">I say you try the same model in Energy Plus or TRNSYS and see if the results differ.</font></div>
<div><span style="color:rgb(51,102,102);font-family:verdana,sans-serif"><br>
</span></div>
<div><font color="#336666"><font face="verdana,sans-serif"><br clear="all">
</font></font>
<div style="text-align:left"><font color="#999999" face="verdana, sans-serif"><i>Jeremiah D. Crossett</i></font></div>
<div style="text-align:left"><font color="#999999" face="verdana, sans-serif"><i>CleanTech Analytics</i></font></div>
<div style="text-align:left"><font color="#999999" face="verdana, sans-serif"><i><a rel="nofollow">503-688-8951</a></i></font></div>
<div>
<div style="text-align:left"><a rel="nofollow" href="http://www.cleantechanalytics.com" target="_blank"><font color="#999999" face="verdana, sans-serif"><i>www.cleantechanalytics.com</i></font></a></div>
<div>
<div style="text-align:center"><br>
</div>
<div style="text-align:center"><img src="cid:"><br>
</div>
</div>
</div>
<div>
<div><b>
<p dir="ltr" style="text-align:center;margin-top:0pt;margin-bottom:0pt"><span>This document may contain valuable information proprietary to CleanTech Analytics which is private and confidential. It may not be shared, copied, stored or transmitted in any form
without the prior written consent of CleanTech Analytics</span></p>
</b></div>
</div>
<br>
<br>
<br>
<div class="gmail_quote">On Sat, Jul 14, 2012 at 12:42 PM, Liam O'Brien <span dir="ltr">
<<a rel="nofollow" href="mailto:obrien_liam@hotmail.com" target="_blank">obrien_liam@hotmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div>
<div dir="ltr">Hi Pete,
<div><br>
</div>
<div>I don't have a ton of experience with detailed modelling of shades in eQUEST, specifically, but two things that could be at play:</div>
<div><br>
</div>
<div>- The claim from the manufacturer sounds like it's not intended to universal in absolute terms. Also, it would be more conservative to reduce the SHGC by 3<span style="font-size:10pt">3 percent than 33</span><span style="font-size:10pt"> </span><u style="font-size:10pt">percentage
points</u><span style="font-size:10pt"> (as you did)</span><span style="font-size:10pt"> if you're going to take this simplified approach. Therefore, it would be closer to SHGC=0.44. Subtle but significant. You could try using software that specializes in
window/shade performance like LBNL Window or Parasol to try to characterize the performance of your specific shade-glazing combination</span></div>
<div>- Depending on the operating conditions and construction of the building, there's a chance your results aren't ridiculous. If shades intercept transmitted solar radiation, then a lot of that energy will almost immediately transfer to the air via convection.
If you have thermally massive interior surfaces, there's a chance your building could actually perform better without those shades because the air conditioning won't kick in till later. </div>
<div><br>
</div>
<div>Liam</div>
<div><br>
<div>
<hr>
Date: Sat, 14 Jul 2012 11:51:02 -0700<br>
From: <a rel="nofollow" href="mailto:pbaumstark@sbcglobal.net" target="_blank">pbaumstark@sbcglobal.net</a><br>
To: <a rel="nofollow" href="mailto:equest-users@lists.onebuilding.org" target="_blank">
equest-users@lists.onebuilding.org</a><br>
Subject: [Equest-users] Unexpected Custom SHGC Results
<div>
<div><br>
<br>
<div style="font-family:arial,helvetica,sans-serif;font-size:12pt">
<div>Hello,<br>
<br>
I have an "L" shaped building with the point of the "L" facing North. The inside of the "L" has both NE and NW surfaces, that include a high amount of glass, which heats up the perimeter building spaces considerably during the summer. Glazing is single pane
tinted.<br>
<br>
The customer wants to install some Verisol SilverScreen shades in these windows. According to the manufacturer, the SHGC will reduce by about 33%. I modeled in eQUEST, window properties in these windows to have an SHGC of 0.67 and ran an EEM reducing SHGC
to 0.34, and got an increase in cooling load and fan load year round, even in the summer months.<br>
<br>
Am I seeing this wrong? I can't figure out how I could possible get results like this?<br>
<br>
Thank you,<br>
Pete<br>
San Jose, CA<br>
</div>
</div>
<br>
</div>
</div>
_______________________________________________ Equest-users mailing list <a rel="nofollow" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a> To unsubscribe from this mailing list send a blank message to
<a rel="nofollow" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></div>
</div>
</div>
</div>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a rel="nofollow" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a rel="nofollow" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
</blockquote>
</div>
<br>
</div>
</div>
<br>
<fieldset></fieldset> <br>
<pre>_______________________________________________
Equest-users mailing list
<a rel="nofollow" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a rel="nofollow" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
<br>
<br>
<div>-- <br>
Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga, CA 94556 (o)
<a href="tel:%28925%29388-0265" value="+19253880265" target="_blank">(925)388-0265</a> (c)
<a href="tel:%28510%29928-2683" value="+15109282683" target="_blank">(510)928-2683</a>
<a rel="nofollow" href="http://www.whiteboxtechnologies.com" target="_blank">www.whiteboxtechnologies.com</a> "Building energy simulations at your fingertips"</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</blockquote>
</div>
<br>
</div>
</div>
</div>
</blockquote>
<blockquote type="cite">
<div><span>_______________________________________________</span><br>
<span>Equest-users mailing list</span><br>
<span><a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></span><br>
<span>To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></span><br>
</div>
</blockquote>
</body>
</html>