    <font size="+1"><font face="Times New Roman, Times, serif">You bring
        up a good point here Jeremy.  One item which is almost never
        mentioned is the amount of water in the building materials.  A
        yard of fresh concrete has a substantial amount of water in it
        which will require removal from the space.  One other item to
        consider with concrete is its ability to wick moisture from the
        surrounding earth.  You should consider a vapour barrier on the
        interface of the concrete and the surrounding soil.  Design your
        concrete to dry inwards.  It will be hard on your HVAC system
        for the first year or 2 but it will solve a big problem for the
        next century.  Moisture is expensive to evaporate and remove. 
        The possible use of temporary dehumidification equipment might
        assist in keeping your regular systems sized correctly.  Large
        internal heat gains would be best placed against the outer walls
        to use the soil as a passive heat sink.<br>
        And I thought dam builders only had these problems. <br>
        Bruce Easterbrook P.Eng.<br>
        Abode Engineering<br>
        <br>
      </font></font>
    <div class="moz-cite-prefix">On 16/07/2012 06:41 PM, Jeremy Poling
      wrote:<br>
    </div>
    <blockquote
cite="mid:CANzYtnTV+DyWFpBKdz9JOg7h+-wBAC_Rcw8ODgzyo_hYNXdDLA@mail.gmail.com"
      type="cite">
      <div>I'd recommend going with Nick's suggestion of a steady-state
        model with input from the design team as far as their load
        calculations go (assuming you aren't also the mechanical
        designer).  From Section 3 Definitions in ASHRAE 90.1-2007, both
        C-Factor and R-Value are defined by ASHRAE to be steady-state
        values and while U-Value is not, it would be safe to assume the
        intention of the standard is a steady-state model for Appendix
        G.  Also, EER values are defined as steady-state ratings for
        equipment.</div>
      <div> </div>
      <div>Genreally, the energy modeling from Appendix G is not
        intended to be an exact prediction of energy use of a building
        the year it opens, or a year after.  This is explicitly stated
        in G1.2(2):</div>
      <div> </div>
      <div>"Neither the proposed building performance nor the baseline
        building preformance are predictions of actual energy
        consumption or costs for the proposed design after
        construction.  Actual experience will differ from these
        calculations due to variations such as occupancy, building
        operation and maintenance, weather, energyuse not covered by
        this procedure, changes in energy rats between the design of the
        building and occupacy, and the precision of the calculation
        tool."</div>
      <div> </div>
      <div>Now, I don't bring up that paragraph to dredge up long
        conversations of the accuracy of energy models, but if the
        concern is really how to get an accurate model out of this
        unique circumstance, I'd suggest citing this paragraph directly,
        in additon to the references before from Section 3, when
        explaining why you used a steady-state model.</div>
      <div> </div>
      <div>The bigger curiosity for me is...what exactly are you
        building here? :)<br clear="all">
      </div>
      <div>Jeremy R. Poling, PE, LEED AP+BDC</div>
      <br>
      <div class="gmail_quote">On Mon, Jul 16, 2012 at 4:27 PM, Nick
        Caton <span dir="ltr"><<a moz-do-not-send="true"
            href="mailto:ncaton@smithboucher.com" target="_blank">ncaton@smithboucher.com</a>></span>
        wrote:<br>
        <blockquote style="margin:0px 0px 0px
0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid"
          class="gmail_quote">
          <div vlink="purple" link="blue" lang="EN-US">
            <div>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">Hi
                  Dave,</span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"> </span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">From
                  a LEED perspective, I think you have a lot of
                  liberties here to model or not model specific
                  elements.  The critical thing is for documentation to
                  be clear & open regarding the decisions you make
                  and be sure to  apply those decisions uniformly
                  between the models.</span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"> </span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">Heat
                  of curing is something you could opt to not model at
                  all – reasonably choosing to model the eventual
                  “steady state” as that should best represent the
                  building’s long term annual internal load profile.  If
                  you should choose to include this internal heat load
                  for the model - intuitively I would expect to see this
                  applied identically to both models as a uniform space
                  equipment load (assigned to a “free” meter) for all
                  affected spaces (perhaps with an annual fractional
                  profile that reduces/eliminates the load over time,
                  per your referenced calculations).</span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"> </span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">How
                  to model that future “steady state” after heat of
                  curing probably poses the more interesting conundrum –
                  I would defer to your mechanical designers to take an
                  approach to envelope loads to match their plans for
                  sizing the heating equipment.  Some might consider the
                  huge thermal lag of the earth/concrete masses to
                  render heat transfer negligible over time (which would
                  bend you towards modeling thermally massive but
                  adiabatic partitions).  Others might consider the
                  surrounding earth a constant heat drain and insulate
                  or bump heating equipment capacities accordingly.
                   From a LEED modeling perspective, best advice is to
                  not make assumptions that disagree with the rest of
                  the design team – communicate and move forward with a
                  consensus.</span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"></span></p>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">~Nick</span></p>
              <div>
                <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><img
                      alt="cid:489575314@22072009-0ABB"
                      src="cid:part2.00080903.02090007@bellnet.ca"
                      height="37" width="119"></span><b><span
                      style="color:rgb(45,77,94);font-family:"Stylus
                      BT","sans-serif";font-size:11pt"></span></b></p>
                <p class="MsoNormal"><b><span
                      style="color:rgb(45,77,94);font-family:"Stylus
                      BT","sans-serif";font-size:11pt"> </span></b></p>
                <p class="MsoNormal"><b><span
                      style="color:rgb(45,77,94);font-family:"Stylus
                      BT","sans-serif"">NICK CATON, P.E.</span></b><b><span
                      style="color:rgb(45,77,94);font-family:"Stylus
                      BT","sans-serif""></span></b></p>
                <p class="MsoNormal"><span
style="color:rgb(204,153,0);font-family:"Calibri","sans-serif";font-size:7.5pt">SENIOR
                    ENGINEER</span></p>
                <p class="MsoNormal"><span
style="color:rgb(204,153,0);font-family:"Calibri","sans-serif";font-size:7.5pt"> </span></p>
                <p class="MsoNormal"><span
style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">Smith
                    & Boucher Engineers</span><span
                    style="color:rgb(204,153,0);font-size:7.5pt"></span></p>
                <p class="MsoNormal"><span
style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">25501
                    west valley parkway, suite 200</span></p>
                <p class="MsoNormal"><span
style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">olathe,
                    ks 66061</span></p>
                <p class="MsoNormal"><span
style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">direct
                    <a moz-do-not-send="true" href="tel:913.344.0036"
                      target="_blank" value="+19133440036">913.344.0036</a></span></p>
                <p class="MsoNormal"><span
style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">fax
                    <a moz-do-not-send="true" href="tel:913.345.0617"
                      target="_blank" value="+19133450617">913.345.0617</a></span></p>
                <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><a
                      moz-do-not-send="true"
                      title="blocked::www.smithboucher.com"
                      href="http://www.smithboucher.com" target="_blank"><span
                        style="color:blue;font-size:10pt">www.smithboucher.com</span></a></span><u><span
style="color:blue;font-family:"Calibri","sans-serif";font-size:10pt">
                    </span></u><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"></span></p>
              </div>
              <p class="MsoNormal"><span
style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"> </span></p>
              <div>
                <div style="border-width:1pt medium
                  medium;border-style:solid none
                  none;border-color:rgb(181,196,223) currentColor
                  currentColor;padding:3pt 0in 0in">
                  <p class="MsoNormal"><b><span
style="font-family:"Tahoma","sans-serif";font-size:10pt">From:</span></b><span
style="font-family:"Tahoma","sans-serif";font-size:10pt">
                      <a moz-do-not-send="true"
                        href="mailto:equest-users-bounces@lists.onebuilding.org"
                        target="_blank">equest-users-bounces@lists.onebuilding.org</a>
                      [mailto:<a moz-do-not-send="true"
                        href="mailto:equest-users-bounces@lists.onebuilding.org"
                        target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
                      <b>On Behalf Of </b>Dave Weigel<br>
                      <b>Sent:</b> Monday, July 16, 2012 12:41 PM<br>
                      <b>To:</b> <a moz-do-not-send="true"
                        href="mailto:equest-users@lists.onebuilding.org"
                        target="_blank">equest-users@lists.onebuilding.org</a><br>
                      <b>Subject:</b> [Equest-users] Really thick
                      concrete walls, partitions, and floor</span></p>
                </div>
              </div>
              <div>
                <div class="h5">
                  <p class="MsoNormal"> </p>
                  <div>
                    <div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif"">Hi
                            group,</span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif""> </span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif"">I
                            have a building with 8-foot concrete floor
                            slab (50 feet below grade), 3- to 6-foot
                            below-grade exterior walls, and 3- to 8-foot
                            interior partitions in the sub-grade shells.</span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif""> </span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif"">I
                            wondered if anyone had a quick hint they
                            could give me, particularly in light of LEED
                            2009 review that will happen.  The calculus
                            is done, and the transfer function time
                            constant is so huge that the inner surface
                            temperature of the walls just isn’t going to
                            vary much.  Ground temperature is 60°F all
                            year and doesn’t vary.  After they are
                            poured, it’ll take 8 to 10 months for the
                            8-foot walls to cool down to indoor
                            (conditioned) ambient temperature just from
                            the heat of curing.</span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif""> </span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif"">Any
                            comments or experience will be most
                            appreciated.</span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif""> </span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif"">Thanks,</span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif""> </span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif"">Dave</span></p>
                      </div>
                      <div>
                        <p class="MsoNormal"><span
                            style="font-family:"Calibri","sans-serif""> </span></p>
                      </div>
                      <div>
                        <div>
                          <p class="MsoNormal"><strong><span
                                style="font-family:"times","serif"">David
                                R. Weigel, PE</span></strong><span
                              style="font-family:"Calibri","sans-serif""></span></p>
                        </div>
                        <div>
                          <p class="MsoNormal"><span
                              style="font-family:"times","serif"">Managing
                              Member</span><span
                              style="font-family:"Calibri","sans-serif""></span></p>
                        </div>
                        <div>
                          <p class="MsoNormal"><span
                              style="font-family:"times","serif"">1189
                              Golden Circle SW,  Lilburn GA 30047</span></p>
                        </div>
                        <div>
                          <p class="MsoNormal"><span
                              style="font-family:"times","serif""><a
                                moz-do-not-send="true"
                                href="tel:678-353-6941" target="_blank"
                                value="+16783536941">678-353-6941</a>
                              office       <a moz-do-not-send="true"
                                href="tel:901-619-1716" target="_blank"
                                value="+19016191716">901-619-1716</a>
                              cell</span></p>
                        </div>
                      </div>
                      <p class="MsoNormal"><span
                          style="font-family:"times","serif""><img
                            alt="wattdoxemailsiglogo"
                            src="cid:part11.08000105.01050605@bellnet.ca"
                            border="0" height="37" width="278"></span></p>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
          <br>
          _______________________________________________<br>
          Equest-users mailing list<br>
          <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
            target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
          To unsubscribe from this mailing list send  a blank message to
          <a moz-do-not-send="true"
            href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
    <br>
  </body>
</html>