<div>I'd recommend going with Nick's suggestion of a steady-state model with input from the design team as far as their load calculations go (assuming you aren't also the mechanical designer).  From Section 3 Definitions in ASHRAE 90.1-2007, both C-Factor and R-Value are defined by ASHRAE to be steady-state values and while U-Value is not, it would be safe to assume the intention of the standard is a steady-state model for Appendix G.  Also, EER values are defined as steady-state ratings for equipment.</div>
<div> </div><div>Genreally, the energy modeling from Appendix G is not intended to be an exact prediction of energy use of a building the year it opens, or a year after.  This is explicitly stated in G1.2(2):</div><div> </div>
<div>"Neither the proposed building performance nor the baseline building preformance are predictions of actual energy consumption or costs for the proposed design after construction.  Actual experience will differ from these calculations due to variations such as occupancy, building operation and maintenance, weather, energyuse not covered by this procedure, changes in energy rats between the design of the building and occupacy, and the precision of the calculation tool."</div>
<div> </div><div>Now, I don't bring up that paragraph to dredge up long conversations of the accuracy of energy models, but if the concern is really how to get an accurate model out of this unique circumstance, I'd suggest citing this paragraph directly, in additon to the references before from Section 3, when explaining why you used a steady-state model.</div>
<div> </div><div>The bigger curiosity for me is...what exactly are you building here? :)<br clear="all"></div><div>Jeremy R. Poling, PE, LEED AP+BDC</div><br><div class="gmail_quote">On Mon, Jul 16, 2012 at 4:27 PM, Nick Caton <span dir="ltr"><<a href="mailto:ncaton@smithboucher.com" target="_blank">ncaton@smithboucher.com</a>></span> wrote:<br>
<blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid" class="gmail_quote">





<div lang="EN-US" vlink="purple" link="blue">
<div>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">Hi Dave,<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">From a LEED perspective, I think you have a lot of liberties here to model or not model specific elements.  The critical thing is for documentation to be clear
 & open regarding the decisions you make and be sure to  apply those decisions uniformly between the models.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">Heat of curing is something you could opt to not model at all – reasonably choosing to model the eventual “steady state” as that should best represent the building’s
 long term annual internal load profile.  If you should choose to include this internal heat load for the model - intuitively I would expect to see this applied identically to both models as a uniform space equipment load (assigned to a “free” meter) for all
 affected spaces (perhaps with an annual fractional profile that reduces/eliminates the load over time, per your referenced calculations).<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">How to model that future “steady state” after heat of curing probably poses the more interesting conundrum – I would defer to your mechanical designers to take
 an approach to envelope loads to match their plans for sizing the heating equipment.  Some might consider the huge thermal lag of the earth/concrete masses to render heat transfer negligible over time (which would bend you towards modeling thermally massive
 but adiabatic partitions).  Others might consider the surrounding earth a constant heat drain and insulate or bump heating equipment capacities accordingly.  From a LEED modeling perspective, best advice is to not make assumptions that disagree with the rest
 of the design team – communicate and move forward with a consensus.<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">~Nick<u></u><u></u></span></p>
<div>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><img alt="cid:489575314@22072009-0ABB" src="cid:image001.jpg@01CD6369.64E86480" width="119" height="37"></span><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif";font-size:11pt"><u></u><u></u></span></b></p>

<p class="MsoNormal"><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif";font-size:11pt"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif"">NICK CATON, P.E.</span></b><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif""><u></u><u></u></span></b></p>

<p class="MsoNormal"><span style="color:rgb(204,153,0);font-family:"Calibri","sans-serif";font-size:7.5pt">SENIOR ENGINEER<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(204,153,0);font-family:"Calibri","sans-serif";font-size:7.5pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">Smith & Boucher Engineers</span><span style="color:rgb(204,153,0);font-size:7.5pt"><u></u><u></u></span></p>

<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">25501 west valley parkway, suite 200<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">olathe, ks 66061<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">direct <a href="tel:913.344.0036" target="_blank" value="+19133440036">913.344.0036</a><u></u><u></u></span></p>

<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">fax <a href="tel:913.345.0617" target="_blank" value="+19133450617">913.345.0617</a><u></u><u></u></span></p>

<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><a title="blocked::www.smithboucher.com" href="http://www.smithboucher.com" target="_blank"><span style="color:blue;font-size:10pt">www.smithboucher.com</span></a></span><u><span style="color:blue;font-family:"Calibri","sans-serif";font-size:10pt">
</span></u><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p>
</div>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<div>
<div style="border-width:1pt medium medium;border-style:solid none none;border-color:rgb(181,196,223) currentColor currentColor;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-family:"Tahoma","sans-serif";font-size:10pt">From:</span></b><span style="font-family:"Tahoma","sans-serif";font-size:10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Dave Weigel<br>
<b>Sent:</b> Monday, July 16, 2012 12:41 PM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Really thick concrete walls, partitions, and floor<u></u><u></u></span></p>
</div>
</div><div><div class="h5">
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif"">Hi group,<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif""> <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif"">I have a building with 8-foot concrete floor slab (50 feet below grade), 3- to 6-foot below-grade exterior walls, and 3- to 8-foot interior partitions in the sub-grade shells.<u></u><u></u></span></p>

</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif""> <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif"">I wondered if anyone had a quick hint they could give me, particularly in light of LEED 2009 review that will happen.  The calculus is done, and the transfer function time constant
 is so huge that the inner surface temperature of the walls just isn’t going to vary much.  Ground temperature is 60°F all year and doesn’t vary.  After they are poured, it’ll take 8 to 10 months for the 8-foot walls to cool down to indoor (conditioned) ambient
 temperature just from the heat of curing.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif""> <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif"">Any comments or experience will be most appreciated.<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif""> <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif"">Thanks,<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif""> <u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif"">Dave<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Calibri","sans-serif""> <u></u><u></u></span></p>
</div>
<div>
<div>
<p class="MsoNormal"><strong><span style="font-family:"times","serif"">David R. Weigel, PE</span></strong><span style="font-family:"Calibri","sans-serif""><u></u><u></u></span></p>

</div>
<div>
<p class="MsoNormal"><span style="font-family:"times","serif"">Managing Member</span><span style="font-family:"Calibri","sans-serif""><u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"times","serif"">1189 Golden Circle SW,  Lilburn GA 30047<u></u><u></u></span></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"times","serif""><a href="tel:678-353-6941" target="_blank" value="+16783536941">678-353-6941</a> office       <a href="tel:901-619-1716" target="_blank" value="+19016191716">901-619-1716</a> cell<u></u><u></u></span></p>

</div>
</div>
<p class="MsoNormal"><span style="font-family:"times","serif""><img border="0" alt="wattdoxemailsiglogo" src="cid:image002.png@01CD6369.64E86480" width="278" height="37"><u></u><u></u></span></p>
</div>
</div>
</div></div></div>
</div>

<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>