<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:12pt">Joe:<br><br>I agree.  I find the comment to be more than mildly offensive.  <br><br>I have the same experience that funky modeling results usually are the result of flawed inputs or depending on too many eQuest defaults.<br><div> </div>Paul Diglio, CEM, CBCP<br><br><div>87 Fairmont Avenue<br>New Haven, CT  06513<br>203-415-0082</div><br><br><div><span><a target="_blank" href="http://www.pdigliollc.com">www.pdigliollc.com</a></span><div><br></div><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><br><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><font face="Tahoma" size="2"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Joe Huang <yjhuang@whiteboxtechnologies.com><br><b><span style="font-weight:
 bold;">To:</span></b> CleanTech Analytics <jeremiah@cleantechanalytics.com><br><b><span style="font-weight: bold;">Cc:</span></b> equest-users@lists.onebuilding.org<br><b><span style="font-weight: bold;">Sent:</span></b> Sun, July 15, 2012 7:21:54 PM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [Equest-users] Unexpected Custom SHGC Results<br></font><br>
  

    
  
  
    I've found this comment to be mildly offensive as well as showing a
    lack of understanding about how heat gains ultimately get translated
    to cooling energy consumption.  It's extremely hard for me to
    believe that eQUEST or DOE-2 has been flawed for 25 years in
    modeling something as fundamental as solar heat gain through
    windows.  In all the decades I've used DOE-2 to analyze window
    performance for DOE's EnergyStar Program as well as numerous other
    projects, whenever the results did not match or ran counter to
    first-principle expectations, it was always because there was some
    other factor that have been overlooked or ignored, chief among them
    being the size of the HVAC system, its configuration, and control
    strategy.  Locations with mild cooling loads, such as San Jose,  are
    particularly sensitive to such system interactions.  Were both runs
    done using "autosizing"?  What<br>
    kind of a system was modeled - VAV or CAV ?   Did the model have an
    economizer?   What were the HEAT-CONTROL and COOL-CONTROL strategies
    ?  etc.   It's far too early to lay blame on the DOE-2 algorithms.<br>
    <br>
    Joe<br>
    <br>
    On 7/14/2012 1:41 PM, CleanTech Analytics wrote:
    <blockquote type="cite"><font color="#336666"><font face="verdana,sans-serif">Just
          admit it- eQuest is flawed, you don't have to make up things
          to protect it- </font></font>
      <div>
        <div><font color="#336666"><font face="verdana,sans-serif"><br>
            </font></font></div>
        <div><font face="verdana, sans-serif" color="#336666">If it is a
            mistake to use the percent points rather then percent
            reduced from the abrataty eQuest assumption from 1999 window
            specs than the it should have reduced solar heat gain by
            more then his product even provided- Using the 33 percentage
            points but used the 33% should have provided him over stated
            cooling reduction, (and extra added heating consumption
            tradeoff) </font></div>
        <div><font face="verdana, sans-serif" color="#336666"><br>
          </font></div>
        <div><span style="color:rgb(51,102,102);font-family:verdana, sans-serif;">O-
            and FYI </span>LBL<span style="color:rgb(51,102,102);font-family:verdana, sans-serif;">
            window does glass U-value not shading, ware-as </span>LBL<font face="verdana, sans-serif" color="#336666"> optics can be
            used for film coefficients and used to create a custom glass
            type in window, but do not do any calculations for "shading"</font></div>
        <div><span style="color:rgb(51,102,102);font-family:verdana, sans-serif;"><br>
          </span></div>
        <div><font face="verdana, sans-serif" color="#336666">I say you
            try the same model in Energy Plus or TRNSYS and see if the
            results differ.</font></div>
        <div><span style="color:rgb(51,102,102);font-family:verdana, sans-serif;"><br>
          </span></div>
        <div><font color="#336666"><font face="verdana,sans-serif"><br clear="all">
            </font></font>
          <div style="text-align:left;"><font face="verdana, sans-serif" color="#999999"><i>Jeremiah D. Crossett</i></font></div>
          <div style="text-align:left;"><font face="verdana, sans-serif" color="#999999"><i>CleanTech Analytics</i></font></div>
          <div style="text-align:left;"><font face="verdana, sans-serif" color="#999999"><i><a rel="nofollow">503-688-8951</a></i></font></div>
          <div>
            <div style="text-align:left;"><a rel="nofollow" target="_blank" href="http://www.cleantechanalytics.com"><font face="verdana, sans-serif" color="#999999"><i>www.cleantechanalytics.com</i></font></a></div>
            <div>
              <div style="text-align:center;">
                <br>
              </div>
              <div style="text-align:center;"><img src="http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG"><br>
              </div>
            </div>
          </div>
          <div>
            <div><b>
                <p dir="ltr" style="text-align:center;margin-top:0pt;margin-bottom:0pt;">
                  <span style="vertical-align:baseline;color:rgb(204,204,204);font-style:italic;font-size:11px;white-space:pre-wrap;text-decoration:none;font-family:'Droid
                    Serif';font-weight:normal;">This document may contain
                    valuable information proprietary to CleanTech
                    Analytics which is private and confidential. It may
                    not be shared, copied, stored or transmitted in any
                    form without the prior written consent of CleanTech
                    Analytics</span></p>
              </b></div>
          </div>
          <br>
          <br>
          <br>
          <div class="gmail_quote">On Sat, Jul 14, 2012 at 12:42 PM,
            Liam O'Brien <span dir="ltr"><<a rel="nofollow" ymailto="mailto:obrien_liam@hotmail.com" target="_blank" href="mailto:obrien_liam@hotmail.com">obrien_liam@hotmail.com</a>></span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
              <div>
                <div dir="ltr">
                  Hi Pete,
                  <div><br>
                  </div>
                  <div>I don't have a ton of experience with detailed
                    modelling of shades in eQUEST, specifically, but two
                    things that could be at play:</div>
                  <div><br>
                  </div>
                  <div>- The claim from the manufacturer sounds like
                    it's not intended to universal in absolute terms.
                    Also, it would be more conservative to reduce the
                    SHGC by 3<span style="font-size:10pt;">3 percent than
                      33</span><span style="font-size:10pt;"> </span><u style="font-size:10pt;">percentage points</u><span style="font-size:10pt;"> (as you did)</span><span style="font-size:10pt;"> if you're going to take
                      this simplified approach. Therefore, it would be
                      closer to SHGC=0.44. Subtle but significant. You
                      could try using software that specializes in
                      window/shade performance like LBNL Window or
                      Parasol to try to characterize the performance of
                      your specific shade-glazing combination</span></div>
                  <div>- Depending on the operating conditions and
                    construction of the building, there's a chance your
                    results aren't ridiculous. If shades intercept
                    transmitted solar radiation, then a lot of that
                    energy will almost immediately transfer to the air
                    via convection. If you have thermally massive
                    interior surfaces, there's a chance your building
                    could actually perform better without those shades
                    because the air conditioning won't kick in till
                    later. </div>
                  <div><br>
                  </div>
                  <div>Liam</div>
                  <div><br>
                    <div>
                      <hr>Date: Sat, 14 Jul 2012 11:51:02 -0700<br>
                      From: <a rel="nofollow" ymailto="mailto:pbaumstark@sbcglobal.net" target="_blank" href="mailto:pbaumstark@sbcglobal.net">pbaumstark@sbcglobal.net</a><br>
                      To: <a rel="nofollow" ymailto="mailto:equest-users@lists.onebuilding.org" target="_blank" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                      Subject: [Equest-users] Unexpected Custom SHGC
                      Results
                      <div>
                        <div><br>
                          <br>
                          <div style="font-family:arial, helvetica, sans-serif;font-size:12pt;">
                            <div>Hello,<br>
                              <br>
                              I have an "L" shaped building with the
                              point of the "L" facing North.  The inside
                              of the "L" has both NE and NW surfaces,
                              that include a high amount of glass, which
                              heats up the perimeter building spaces
                              considerably during the summer.  Glazing
                              is single pane tinted.<br>
                              <br>
                              The customer wants to install some Verisol
                              SilverScreen shades in these windows. 
                              According to the manufacturer, the SHGC
                              will reduce by about 33%.  I modeled in
                              eQUEST, window properties in these windows
                              to have an SHGC of 0.67 and ran an EEM
                              reducing SHGC to 0.34, and got an increase
                              in cooling load and fan load year round,
                              even in the summer months.<br>
                              <br>
                              Am I seeing this wrong?  I can't figure
                              out how I could possible get results like
                              this?<br>
                              <br>
                              Thank you,<br>
                              Pete<br>
                              San Jose, CA<br>
                            </div>
                          </div>
                          <br>
                        </div>
                      </div>
                      _______________________________________________
                      Equest-users mailing list
                      <a rel="nofollow" target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
                      To unsubscribe from this mailing list send a blank
                      message to <a rel="nofollow" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a></div>
                  </div>
                </div>
              </div>
              <br>
              _______________________________________________<br>
              Equest-users mailing list<br>
              <a rel="nofollow" target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
              To unsubscribe from this mailing list send  a blank
              message to <a rel="nofollow" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              <br>
            </blockquote>
          </div>
          <br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre>_______________________________________________
Equest-users mailing list
<a rel="nofollow" class="moz-txt-link-freetext" target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a rel="nofollow" class="moz-txt-link-abbreviated" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
    <br>
    <div class="moz-signature">-- <br>
      Joe Huang
      White Box Technologies, Inc.
      346 Rheem Blvd., Suite 108D
      Moraga, CA 94556
      (o) (925)388-0265
      (c) (510)928-2683
      <a rel="nofollow" class="moz-txt-link-abbreviated" target="_blank" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
      "Building energy simulations at your fingertips"</div>
  

</div></div></div>



</div></body></html>