<!DOCTYPE HTML PUBLIC "-//W3C//DTD HTML 4.0 Transitional//EN">
<HTML xmlns="http://www.w3.org/TR/REC-html40" xmlns:v = 
"urn:schemas-microsoft-com:vml" xmlns:o = 
"urn:schemas-microsoft-com:office:office" xmlns:w = 
"urn:schemas-microsoft-com:office:word" xmlns:m = 
"http://schemas.microsoft.com/office/2004/12/omml"><HEAD>
<META content="text/html; charset=us-ascii" http-equiv=Content-Type>
<META name=GENERATOR content="MSHTML 8.00.6001.19258"><!--[if !mso]>
<STYLE>v\:* {
        BEHAVIOR: url(#default#VML)
}
o\:* {
        BEHAVIOR: url(#default#VML)
}
w\:* {
        BEHAVIOR: url(#default#VML)
}
.shape {
        BEHAVIOR: url(#default#VML)
}
</STYLE>
<![endif]-->
<STYLE>@font-face {
        font-family: MS Mincho;
}
@font-face {
        font-family: MS Mincho;
}
@font-face {
        font-family: Calibri;
}
@font-face {
        font-family: Tahoma;
}
@font-face {
        font-family: Stylus BT;
}
@font-face {
        font-family: @MS Mincho;
}
@page WordSection1 {size: 8.5in 11.0in; margin: 1.0in 1.0in 1.0in 1.0in; }
P.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"; FONT-SIZE: 12pt
}
LI.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"; FONT-SIZE: 12pt
}
DIV.MsoNormal {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Times New Roman","serif"; FONT-SIZE: 12pt
}
A:link {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlink {
        COLOR: blue; TEXT-DECORATION: underline; mso-style-priority: 99
}
A:visited {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
SPAN.MsoHyperlinkFollowed {
        COLOR: purple; TEXT-DECORATION: underline; mso-style-priority: 99
}
P.MsoAcetate {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; FONT-SIZE: 8pt; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
LI.MsoAcetate {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; FONT-SIZE: 8pt; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
DIV.MsoAcetate {
        MARGIN: 0in 0in 0pt; FONT-FAMILY: "Tahoma","sans-serif"; FONT-SIZE: 8pt; mso-style-priority: 99; mso-style-link: "Balloon Text Char"
}
SPAN.BalloonTextChar {
        FONT-FAMILY: "Tahoma","sans-serif"; mso-style-priority: 99; mso-style-link: "Balloon Text"; mso-style-name: "Balloon Text Char"
}
SPAN.EmailStyle19 {
        FONT-FAMILY: "Calibri","sans-serif"; COLOR: #1f497d; mso-style-type: personal
}
SPAN.EmailStyle20 {
        FONT-FAMILY: "Calibri","sans-serif"; COLOR: #1f497d; mso-style-type: personal-reply
}
.MsoChpDefault {
        FONT-SIZE: 10pt; mso-style-type: export-only
}
DIV.WordSection1 {
        page: WordSection1
}
</STYLE>
<!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]--></HEAD>
<BODY lang=EN-US link=blue vLink=purple>
<DIV dir=ltr align=left><SPAN class=719135215-15062012><FONT color=#0000ff 
size=2 face=Arial>RE - The greyed out area - The system is a basic PSZ with gas 
heat/DX cooling.  Equest defaults to DX for this system type and so the 
greyed out issue is sort of non-relevant I've found.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=719135215-15062012><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=719135215-15062012><FONT color=#0000ff 
size=2 face=Arial>The other space indicating no cooling on the SSA report I 
haven't figured out yet.  I changed the space temperature settings and no 
difference was made, when I went from 90 to 55.  I've already reviewed the 
SSO reports to do the same you suggested.  I'll continue looking at a few 
other items as well.</FONT></SPAN></DIV>
<DIV dir=ltr align=left><SPAN class=719135215-15062012><FONT color=#0000ff 
size=2 face=Arial></FONT></SPAN> </DIV>
<DIV dir=ltr align=left><SPAN class=719135215-15062012><FONT color=#0000ff 
size=2 face=Arial>Thx</FONT></SPAN></DIV><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> Nick Caton 
[mailto:ncaton@smithboucher.com] <BR><B>Sent:</B> Friday, June 15, 2012 10:51 
AM<BR><B>To:</B> Eric Hethcoat; 
equest-users@lists.onebuilding.org<BR><B>Subject:</B> RE: DX Cooling 
Option<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV class=WordSection1>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Hi 
Eric,<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Re-reading 
your posts, I’m now uncertain I understand the context of your concerns… are you 
getting unmet cooling hours, or if not how/where are you observing cooling “not 
occuring?”  When you say “if any cooling shows,” how/where are you making 
that observation?  <o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">If 
the heart of your concerns is the greyed-out “n/a” input for cooling option in 
the detailed edit windows, you’ll find that input is only applicable to certain 
system types on reading the associated help entry – this can be a non-concern if 
conditioning is occurring.  <o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">One 
means of confirming heating/cooling is occurring is to examine SS-O report 
“space temperature summary,” keeping in mind a correctly operating system 
without unmet hours should float around and between your heating/cooling 
setpoints.  In climates like ours (KS), if cooling is not occurring at all 
you’ll probably observe a majority of hours above the 75-80 bin.  A more 
detailed means of observing space temperature behavior is to generate an hourly 
report for the zone(s) in question.<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Another 
interpretation I have for your situation suggests pointing out you can define 
more than one system type in the wizards, and assign to zones accordingly using 
the zone allocation screens – you aren’t restricted to one system per shell or 
anything.<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Hope 
something here hits the mark =)!<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">~Nick<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG 
id=_x0000_i1027 alt=cid:489575314@22072009-0ABB 
src="cid:719135215@15062012-002B" width=119 height=37></SPAN><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></B></P>
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e">NICK CATON, 
P.E.</SPAN></B><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt">SENIOR 
ENGINEER<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">Smith 
& Boucher Engineers</SPAN><SPAN 
style="COLOR: #cc9900; FONT-SIZE: 7.5pt"><o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">25501 
west valley parkway, suite 200<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">olathe, 
ks 66061<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">direct 
913.344.0036<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">fax 
913.345.0617<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><A 
title=blocked::www.smithboucher.com href="www.smithboucher.com"><SPAN 
style="FONT-SIZE: 10pt">www.smithboucher.com</SPAN></A></SPAN><U><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: blue; FONT-SIZE: 10pt"> 
</SPAN></U><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p></o:p></SPAN></P></DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<DIV>
<DIV 
style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> Eric Hethcoat 
[mailto:EHethcoat@lsapa.com] <BR><B>Sent:</B> Thursday, June 14, 2012 7:44 
PM<BR><B>To:</B> Nick Caton; 
equest-users@lists.onebuilding.org<BR><B>Subject:</B> RE: DX Cooling 
Option<o:p></o:p></SPAN></P></DIV></DIV>
<P class=MsoNormal><o:p> </o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt">Checked 
all schedules first.  All are the same.</SPAN><o:p></o:p></P>
<P class=MsoNormal> <o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt">Went 
back into the Wizard.  It was selected as furnace with no cooling.  
Changed to furnace with DX as a PSZ.  reran the file and again same 
result.  I presume that if any cooling shows, then it is indeed modeling it 
- correctly?  </SPAN><o:p></o:p></P>
<P class=MsoNormal> <o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt">The 
space with no cooling is identical in all but physical size to the other spaces 
that do have a cooling load associated to them in the simulation 
output.</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt"><BR>Eric</SPAN><o:p></o:p></P>
<P class=MsoNormal><o:p> </o:p></P>
<DIV style="TEXT-ALIGN: center" class=MsoNormal align=center>
<HR align=center SIZE=2 width="100%">
</DIV>
<P style="MARGIN-BOTTOM: 12pt" class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> Nick Caton [<A 
href="mailto:ncaton@smithboucher.com">mailto:ncaton@smithboucher.com</A>] 
<BR><B>Sent:</B> Thursday, June 14, 2012 4:52 PM<BR><B>To:</B> Eric Hethcoat; <A 
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> 
RE: DX Cooling Option</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Hi 
Eric,<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><BR>First 
thought is if you chose “no cooling” in the wizards, the wizards may have 
assigned a system type (there are many) which cannot be assigned any cooling 
function no matter what you do.  You may need to review and re-assign the 
system type as a result.<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><BR>If 
this could be the case and you’re still gaining familiarity, it can be 
instructive to save a ‘dummy’ copy of your project, then go back to wizards, 
re-create the system you’re thinking of (with cooling), and observe what the 
wizards generate as a result for edits in your ‘actual’ 
project.<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">If 
the system is correctly defined, an easy miss might be defining cooling 
thermostat inputs (scheduling) for the zones to be 
conditioned.<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">Best 
of luck!<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt">~Nick<o:p></o:p></SPAN></P>
<DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><IMG 
id=Picture_x0020_1 border=0 alt=cid:489575314@22072009-0ABB 
src="cid:719135215@15062012-002B" width=119 height=37></SPAN><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"><o:p></o:p></SPAN></B></P>
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></B></P>
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: #2d4d5e">NICK CATON, 
P.E.<o:p></o:p></SPAN></B></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt">SENIOR 
ENGINEER<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #cc9900; FONT-SIZE: 7.5pt"><o:p> </o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">Smith 
& Boucher Engineers</SPAN><SPAN 
style="COLOR: #cc9900; FONT-SIZE: 7.5pt"><o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">25501 
west valley parkway, suite 200<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">olathe, 
ks 66061<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">direct 
913.344.0036<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #2d4d5e; FONT-SIZE: 10pt">fax 
913.345.0617<o:p></o:p></SPAN></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><A 
title=blocked::www.smithboucher.com href="www.smithboucher.com"><SPAN 
style="FONT-SIZE: 10pt">www.smithboucher.com</SPAN></A></SPAN><U><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: blue; FONT-SIZE: 10pt"> 
</SPAN></U><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p></o:p></SPAN></P></DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: #1f497d; FONT-SIZE: 11pt"><o:p> </o:p></SPAN></P>
<DIV>
<DIV 
style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: #b5c4df 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN 
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN 
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> <A 
href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</A> 
[<A 
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</A>] 
<B>On Behalf Of </B>Eric Hethcoat<BR><B>Sent:</B> Thursday, June 14, 2012 4:17 
PM<BR><B>To:</B> <A 
href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> 
[Equest-users] DX Cooling Option<o:p></o:p></SPAN></P></DIV></DIV>
<P class=MsoNormal><o:p> </o:p></P>
<DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">I've got a baseline 
and proposed model for a project set up.  I've been thru every wizard mode 
input, then changed several items in the detailed input mode.  Successful 
runs for both.  </SPAN><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal> <o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">The one thing that is 
not showing up on only a single zone for one system between both models is 
cooling.  In the wizard mode - it is entered as "no cooling".  I 
understand this limits what systems can be chosen - in wizard 
mode.</SPAN><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal> <o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">In the detailed mode 
I've been thru every cooling tab to ensure all cooling properties are correctly 
indicated as if we had DX - however under the air-side system tab, the 
selection of chilled water or DX is not available - and is greyed out to 
N/A.  I've played with zone temps, schedules, etc. and none have any change 
in the result for cooling in this area.</SPAN><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal> <o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">How can I ensure that 
I have the proper cooling?  I only have standard gas fired heating/DX 
cooling PSZ equipment.  No heat pump.  </SPAN><o:p></o:p></P></DIV>
<DIV>
<P class=MsoNormal> <o:p></o:p></P></DIV>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">Eric Hethcoat, 
P.E.</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">Partner</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">Latimer, Sommers 
& Associates, P.A.</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">3639 SW Summerfield 
Dr., Suite A</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">Topeka, KS  
66614</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">c.  
913.481.3256</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">w.  
785.233.3232</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt">f.  
785.233.0647</SPAN><o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 10pt"><A 
href="mailto:ehethcoat@lsapa.com">ehethcoat@lsapa.com</A></SPAN><o:p></o:p></P>
<P class=MsoNormal> <o:p></o:p></P>
<P class=MsoNormal><SPAN 
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 7.5pt">This message and any 
attachments included here-in, are solely for the intended recipient and may 
contain confidential or privileged information.  If you are not the 
intended recipient, any review, disclosure, copying, use, forwarding, or 
distribution of the information included in this message and any attachments is 
prohibited.  If you have received this communication in error, please 
notify the sender by reply e-mail and immediately and permanently delete this 
message and any attachments.  Thank you.</SPAN><o:p></o:p></P>
<DIV>
<P class=MsoNormal> <o:p></o:p></P></DIV></DIV></BODY></HTML>