face=Calibri>Matt,</FONT></SPAN></DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff
face=Calibri></FONT></SPAN> </DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff face=Calibri>Before
looking into the Systems, I would suggest taking a closer look at the inputs on
the building shell and internal loads. </FONT></SPAN></DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff face=Calibri>For
example, you are using 0.025 w/sf as equipment/plug load for many of your
classroom </FONT></SPAN><SPAN class=450090718-06062012><FONT color=#0000ff
face=Calibri>spaces, which is too low. Depending on</FONT></SPAN></DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff face=Calibri>the type of
equipment (TV, Computers, Projection Eq., SmartBoards), the plug loads could
range between 0.25-0.5 w/sf for an </FONT></SPAN><SPAN
class=450090718-06062012><FONT color=#0000ff face=Calibri>elementary
school.</FONT></SPAN></DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff
face=Calibri></FONT></SPAN> </DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff face=Calibri>Also, I
noticed your glazing types have U-value > 0.7.</FONT></SPAN></DIV>
<DIV><SPAN class=450090718-06062012><FONT color=#0000ff
face=Calibri></FONT></SPAN> </DIV><FONT color=#0000ff
face=Calibri></FONT><FONT color=#0000ff face=Calibri></FONT><FONT color=#0000ff
face=Calibri></FONT><BR>
<DIV dir=ltr lang=en-us class=OutlookMessageHeader align=left>
<HR tabIndex=-1>
<FONT size=2 face=Tahoma><B>From:</B> equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>R
B<BR><B>Sent:</B> Tuesday, June 05, 2012 4:11 PM<BR><B>To:</B> Matt
Clough<BR><B>Cc:</B> eQUEST Users List<BR><B>Subject:</B> Re: [Equest-users]
LEED system 5<BR></FONT><BR></DIV>
<DIV></DIV>
<DIV>I ran the file you sent - it has heating consumption values, unmet hours is
just 200. Strange thing is that the % of hours should be 2.2% or so, instead it
is 8.2% - not sure why that is happening - may be the calc
procedures have changed for the % calcs?</DIV>
<DIV>-Rohini<BR><BR></DIV>
<DIV class=gmail_quote>On Tue, Jun 5, 2012 at 2:37 PM, Matt Clough <SPAN
dir=ltr><<A href="mailto:mclough@kme-inc.com"
target=_blank>mclough@kme-inc.com</A>></SPAN> wrote:<BR>
<BLOCKQUOTE
style="BORDER-LEFT: rgb(204,204,204) 1px solid; MARGIN: 0px 0px 0px 0.8ex; PADDING-LEFT: 1ex"
class=gmail_quote>
<DIV lang=EN-US link="blue" vlink="purple">
<DIV>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)">I have attached the
.pd2 and .inp for the baseline building. <U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)">I have changed the
reheat deltaT, but this has not decreased the unmet hours (which explains the
lack of energy used for heating)<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P><PRE><SPAN style="FONT-FAMILY: 'Calibri','sans-serif'; COLOR: rgb(31,73,125)">I’m fiddling with </SPAN>HMAX-FLOW-RATIO <SPAN style="FONT-FAMILY: 'Calibri','sans-serif'">at the suggestion from the archives, and may try increasing the boiler capacity incrementally.<U></U><U></U></SPAN></PRE><PRE><SPAN style="FONT-FAMILY: 'Calibri','sans-serif'">But I’m feeling pretty stuck on this one. Just have to keep reading.<U></U><U></U></SPAN></PRE><PRE><SPAN style="FONT-FAMILY: 'Calibri','sans-serif'"><U></U> <U></U></SPAN></PRE><PRE><SPAN style="FONT-FAMILY: 'Calibri','sans-serif'">Thanks for the help<U></U><U></U></SPAN></PRE>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<DIV>
<DIV
style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> Sami, Vikram
[mailto:<A href="mailto:Vikram.Sami@perkinswill.com"
target=_blank>Vikram.Sami@perkinswill.com</A>] <BR><B>Sent:</B> Tuesday, June
05, 2012 10:13 AM<BR><B>To:</B> Nick Caton; Howe, Timothy; Matt Clough; <A
href="mailto:equest-users@lists.onebuilding.org"
target=_blank>equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> RE:
LEED system 5<U></U><U></U></SPAN></P></DIV></DIV>
<DIV>
<DIV class=h5>
<P class=MsoNormal><U></U><U></U> </P>
<P><U></U><SPAN style="COLOR: rgb(31,73,125)"><SPAN>1.<SPAN
style="FONT: 7pt 'Times New Roman'; font-size-adjust: none; font-stretch: normal">
</SPAN></SPAN></SPAN><U></U><SPAN style="COLOR: rgb(31,73,125)">Make sure your
systems are set to cycle on any<U></U><U></U></SPAN></P>
<P><U></U><SPAN style="COLOR: rgb(31,73,125)"><SPAN>2.<SPAN
style="FONT: 7pt 'Times New Roman'; font-size-adjust: none; font-stretch: normal">
</SPAN></SPAN></SPAN><U></U><SPAN style="COLOR: rgb(31,73,125)">Make sure you
have your reheat Delta T Set correctly. <U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)">This should take care
of the problem – otherwise its probably something more sinister.
<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<DIV>
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: rgb(220,170,44); FONT-SIZE: 10pt"><U></U><U></U></SPAN></B> </P>
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Vikram
Sami</SPAN></B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">, LEED
AP BD+C<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Sustainable
Design Analyst<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">1315
Peachtree St. NE, Atlanta, GA 30309<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">t: <A
href="tel:404-443-7462" target=_blank
value="+14044437462">404-443-7462</A> f: </SPAN><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt"
lang=ES><A href="tel:404.892.5823" target=_blank
value="+14048925823">404.892.5823</A> </SPAN><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">
e: <A href="mailto:vikram.sami@perkinswill.com"
target=_blank>vikram.sami@perkinswill.com</A> </SPAN><SPAN
style="COLOR: rgb(31,73,125)"><A href="http://www.perkinswill.com/"
target=_blank><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt; TEXT-DECORATION: none">www.perkinswill.com</SPAN></A></SPAN><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt"><U></U><U></U></SPAN></P>
<P style="MARGIN-BOTTOM: 3pt" class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">Perkins+Will.</SPAN></B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">
</SPAN><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: rgb(173,212,37); FONT-SIZE: 9pt">Ideas
+ buildings that honor the broader goals of society</SPAN><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: green; FONT-SIZE: 9pt"><U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P></DIV>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<DIV>
<DIV
style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> <A
href="mailto:equest-users-bounces@lists.onebuilding.org"
target=_blank>equest-users-bounces@lists.onebuilding.org</A> [mailto:<A
href="mailto:equest-users-bounces@lists.onebuilding.org"
target=_blank>equest-users-bounces@lists.onebuilding.org</A>] <B>On Behalf Of
</B>Nick Caton<BR><B>Sent:</B> Tuesday, June 05, 2012 10:57 AM<BR><B>To:</B>
Howe, Timothy; Matt Clough; <A
href="mailto:equest-users@lists.onebuilding.org"
target=_blank>equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> Re:
[Equest-users] LEED system 5<U></U><U></U></SPAN></P></DIV></DIV>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)">Unmet heating hours
will probably go away once you get your heating operational. I’d caution
against internally justifying/rationalizing one set of unmet hours with
another – keep in mind unmet hours are an indicator/symptom of a problem, not
a problem in and of themselves.<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)">For HW consumption,
open both models and review the DHW loop, schedules, process loads, and
equipment. Generally everything should be identical excepting HW heater
efficiency inputs.<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)">Reheat coils are set up
at the terminal units (zone inputs). Those relying on wizards can easily
miss some required edits to make reheat operate correctly – see attached
discussion from the [Bldg-sim] archives for a recap.<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)">~Nick<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<DIV>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)"><IMG border=0
alt=cid:489575314@22072009-0ABB width=119 height=37></SPAN><B><SPAN
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: rgb(45,77,94)"><U></U><U></U></SPAN></B></P>
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: rgb(45,77,94)"><U></U><U></U></SPAN></B> </P>
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Stylus BT','sans-serif'; COLOR: rgb(45,77,94); FONT-SIZE: 12pt">NICK
CATON, P.E.<U></U><U></U></SPAN></B></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(204,153,0); FONT-SIZE: 7.5pt">SENIOR
ENGINEER<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="COLOR: rgb(204,153,0); FONT-SIZE: 7.5pt"><U></U><U></U></SPAN> </P>
<P class=MsoNormal><SPAN style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">Smith
& Boucher Engineers</SPAN><SPAN
style="FONT-FAMILY: 'Times New Roman','serif'; COLOR: rgb(204,153,0); FONT-SIZE: 7.5pt"><U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">25501
west valley parkway, suite 200<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">olathe,
ks 66061<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">direct
<A href="tel:913.344.0036" target=_blank
value="+19133440036">913.344.0036</A><U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: rgb(45,77,94); FONT-SIZE: 10pt">fax <A
href="tel:913.345.0617" target=_blank
value="+19133450617">913.345.0617</A><U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN style="COLOR: rgb(31,73,125)"><A
title=blocked::www.smithboucher.com href="http://www.smithboucher.com"
target=_blank><SPAN
style="FONT-SIZE: 10pt">www.smithboucher.com</SPAN></A></SPAN><U><SPAN
style="COLOR: blue; FONT-SIZE: 10pt"> </SPAN></U><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN></P></DIV>
<P class=MsoNormal><SPAN
style="COLOR: rgb(31,73,125)"><U></U><U></U></SPAN> </P>
<DIV>
<DIV
style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> <A
href="mailto:equest-users-bounces@lists.onebuilding.org"
target=_blank>equest-users-bounces@lists.onebuilding.org</A> [mailto:<A
href="mailto:equest-users-bounces@lists.onebuilding.org"
target=_blank>equest-users-bounces@lists.onebuilding.org</A>] <B>On Behalf Of
</B>Howe, Timothy<BR><B>Sent:</B> Tuesday, June 05, 2012 9:26 AM<BR><B>To:</B>
Matt Clough; <A href="mailto:equest-users@lists.onebuilding.org"
target=_blank>equest-users@lists.onebuilding.org</A><BR><B>Subject:</B> Re:
[Equest-users] LEED system 5<U></U><U></U></SPAN></P></DIV></DIV>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt">Post
the .pd2 and .inp file for this project and we may be able to help you
better.<U></U><U></U></SPAN></P>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt"><U></U><U></U></SPAN> </P>
<DIV>
<DIV>
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 9pt">Timothy Howe, MS,
LEED® AP BD+C</SPAN></B><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 9pt"><BR>Mechanical
Engineer<BR>Stantec<U></U><U></U></SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: gray; FONT-SIZE: 9pt">61
Commercial Street<BR>Rochester NY 14614<BR>Ph: <A
href="tel:%28585%29%20413-5347" target=_blank value="+15854135347">(585)
413-5347</A><BR>Fx: <A href="tel:%28585%29%20272-1814"
target=_blank value="+15852721814">(585) 272-1814</A><BR>Cell: <A
href="tel:%28585%29%20330-8681" target=_blank value="+15853308681">(585)
330-8681</A><U></U><U></U></SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial Narrow','sans-serif'; COLOR: blue; FONT-SIZE: 13pt"><A
href="http://www.stantec.com" target=_blank><B><SPAN
style="COLOR: rgb(153,51,51); TEXT-DECORATION: none">stantec</SPAN></B><SPAN
style="COLOR: rgb(0,63,110); TEXT-DECORATION: none">.com</SPAN></A>
<U></U><U></U></SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 9pt"><U></U><U></U></SPAN> </P></DIV>
<DIV>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 9pt">The content of this
email is the confidential property of Stantec and should not be copied,
modified, retransmitted, or used for any purpose except with Stantec's written
authorization. If you are not the intended recipient, please delete all copies
and notify us immediately.<U></U><U></U></SPAN></P></DIV>
<DIV>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; FONT-SIZE: 9pt"><U></U><U></U></SPAN> </P></DIV></DIV>
<P class=MsoNormal><SPAN
style="FONT-FAMILY: Webdings; COLOR: rgb(0,128,64); FONT-SIZE: 13.5pt">ü</SPAN><SPAN
style="FONT-FAMILY: 'Times New Roman','serif'; COLOR: blue; FONT-SIZE: 12pt"> </SPAN><SPAN
style="FONT-FAMILY: 'Arial Narrow','sans-serif'; COLOR: rgb(0,128,64); FONT-SIZE: 10pt">Please
consider the environment before printing this email.</SPAN><SPAN
style="FONT-FAMILY: 'Times New Roman','serif'; COLOR: blue; FONT-SIZE: 12pt">
</SPAN><SPAN
style="FONT-FAMILY: 'Arial','sans-serif'; COLOR: blue; FONT-SIZE: 10pt"><U></U><U></U></SPAN></P>
<DIV>
<DIV
style="BORDER-BOTTOM: medium none; BORDER-LEFT: medium none; PADDING-BOTTOM: 0in; PADDING-LEFT: 0in; PADDING-RIGHT: 0in; BORDER-TOP: rgb(181,196,223) 1pt solid; BORDER-RIGHT: medium none; PADDING-TOP: 3pt">
<P class=MsoNormal><B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt">From:</SPAN></B><SPAN
style="FONT-FAMILY: 'Tahoma','sans-serif'; FONT-SIZE: 10pt"> <A
href="mailto:equest-users-bounces@lists.onebuilding.org"
target=_blank>equest-users-bounces@lists.onebuilding.org</A> [<A
href="mailto:equest-users-bounces@lists.onebuilding.org"
target=_blank>mailto:equest-users-bounces@lists.onebuilding.org</A>] <B>On
Behalf Of </B>Matt Clough<BR><B>Sent:</B> Tuesday, June 05, 2012 10:24
AM<BR><B>To:</B> <A href="mailto:equest-users@lists.onebuilding.org"
target=_blank>equest-users@lists.onebuilding.org</A><BR><B>Subject:</B>
[Equest-users] LEED system 5<U></U><U></U></SPAN></P></DIV></DIV>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal>Salutations!<U></U><U></U></P>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal>I just completed a LEED model, but after reviewing the data
results, I think something is wrong.<U></U><U></U></P>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal>The baseline building is showing no energy used for space
heating, heat rejection, and service water heating. I have the 2 boilers
modeled, per G3.1.3.2. This sort of makes sense because the model was
showing high unmet heating hours, while the proposed building had had unmet
cooling hours (successfully resolved). <U></U><U></U></P>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal>I set up the system 5 equipment (Packaged VAV with reheat)
in the wizard, but it doesn’t seem to show a heating component in the
DDE. I’m going to keep looking, but wanted to see if someone could point
me in the right direction.<U></U><U></U></P>
<P class=MsoNormal><U></U><U></U> </P>
<P class=MsoNormal>Regards,<U></U><U></U></P>
<P class=MsoNormal>Matt
Clough<U></U><U></U></P></DIV></DIV></DIV></DIV><BR>_______________________________________________<BR>Equest-users
mailing list<BR><A
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
target=_blank>http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</A><BR>To
unsubscribe from this mailing list send a blank message to <A
href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</A><BR><BR></BLOCKQUOTE></DIV><BR></BODY></HTML>