    ashrae 62.1-2004 section 5.4 ventilation controls.  mechanical
    ventilation systems shall include controls, manual or automatic,
    that enable the fan system to operate whenever the spaces served are
    occupied.  the system shall be designed to maintain the minimum
    outdoor airflow as required by section 6 under any load condition. 
    note:  vav systems with fixed outdoor air damper positions must
    comply with this requirement at minimum airflow.<br>
    <br>
    ashrae 62.1-2007 user's manual, page 5-11.  user's manual example
    also explains why the 'auto' setting for fan on a basic thermostat
    does not meet the requirement to provide outdoor air when the spaces
    is occupied - the fan will cycle off when setpoint is reached and no
    outdoor air will be supplied until the next call for cooling &
    the fan comes back on.<br>
    <br>
    On 6/6/12 10:25 AM, John Aulbach wrote:
    <blockquote
      cite="mid:1339003538.11240.YahooMailNeo@web126103.mail.ne1.yahoo.com"
      type="cite">
      <div style="color:#000; background-color:#fff; font-family:times
        new roman, new york, times, serif;font-size:12pt">
        <div style="font-family: 'times new roman', 'new york', times,
          serif; font-size: 12pt; ">Gang:</div>
        <div style="font-family: 'times new roman', 'new york', times,
          serif; font-size: 12pt; "><br>
        </div>
        <div style="font-family: 'times new roman', 'new york', times,
          serif; font-size: 12pt; ">I am trying to find where in the
          Texas Health and Safety Code where is says you must OPERATE
          ventilation in a certain manner, not just design a system to
          provide such ventilation. Tells me if i can reduce or
          eliminate exhaust air during certain times of the day (eQuest
          EEM).</div>
        <div style="font-family: 'times new roman', 'new york', times,
          serif; font-size: 12pt; "><br>
        </div>
        <div style="font-family: 'times new roman', 'new york', times,
          serif; font-size: 12pt; ">California Title-24, Subchapter 3,
          Section 121.c.1 specifically states:</div>
        <div style="font-family: 'times new roman', 'new york', times,
          serif; font-size: 12pt; "><br>
        </div>
        <div>
          <div><font face="times new roman, new york, times, serif">1.
              Times of occupancy. The minimum rate of outdoor air
              required by Section 121(b)2 shall be supplied to each</font></div>
          <div><font face="times new roman, new york, times, serif">space
              at all times when the space is usually occupied.</font></div>
          <div><font face="times new roman, new york, times, serif">EXCEPTION
              1 to Section 121(c)1: Demand control ventilation. In
              intermittently occupied spaces that do not</font></div>
          <div><font face="times new roman, new york, times, serif">have
              processes or operations that generate dusts, fumes, mists,
              vapors or gasses and are not provided with local</font></div>
          <div><font face="times new roman, new york, times, serif">exhaust
              ventilation (such as indoor operation of internal
              combustion engines or areas designated for unvented</font></div>
          <div><font face="times new roman, new york, times, serif">food
              service preparation), the rate of outdoor air may be
              reduced if the ventilation system serving the space is</font></div>
          <div><font face="times new roman, new york, times, serif">controlled
              by a demand control ventilation device complying with
              Section 121(c)4.</font></div>
          <div><font face="times new roman, new york, times, serif">EXCEPTION
              2 to Section 121(c)1: Temporary reduction. The rate of
              outdoor air provided to a space may be</font></div>
          <div><font face="times new roman, new york, times, serif">reduced
              below the level required by Section 121(b)2 for up to 5
              minutes each hour if the average rate for each</font></div>
          <div><font face="times new roman, new york, times, serif">hour
              is equal to or greater than the required ventilation rate.</font></div>
          <div><font face="times new roman, new york, times, serif">NOTE:
              VAV must comply with Section 121(c)1 at minimum supply
              airflow.</font></div>
          <div><font face="times new roman, new york, times, serif"><br>
            </font></div>
          <div><font face="times new roman, new york, times, serif">I am
              trying to find a similar edict for the State of Texas.</font></div>
          <div><font face="times new roman, new york, times, serif"><br>
            </font></div>
          <div><font face="times new roman, new york, times, serif">Any
              takers?</font></div>
          <div><font face="times new roman, new york, times, serif"><br>
            </font></div>
          <div>
            <div class="MsoNormal"><a moz-do-not-send="true"
                name="_MailAutoSig"><span
                  style="mso-fareast-font-family:
                  "Times New
                  Roman";mso-fareast-theme-font:minor-fareast;color:#1F497D;
                  mso-no-proof:yes">John R. Aulbach, PE, CEM<o:p></o:p></span></a></div>
            <div class="MsoNormal"><span
                style="mso-fareast-font-family:"Times New
                Roman";mso-fareast-theme-font:minor-fareast;
                color:#1F497D;mso-no-proof:yes">Senior Energy Engineer<o:p></o:p></span></div>
            <div class="MsoNormal"><span
                style="mso-fareast-font-family:"Times New
                Roman";color:#17365D;mso-no-proof:
                yes">
                <hr align="left" noshade="noshade" size="2" width="30%">
              </span></div>
            <div class="MsoNormal"><b><span
                  style="mso-fareast-font-family:"Times New
                  Roman";mso-fareast-theme-font:minor-fareast;
                  font-variant:small-caps;color:navy;mso-no-proof:yes">Partner</span></b><b><span
                  style="mso-fareast-font-family:"Times New
                  Roman";
mso-fareast-theme-font:minor-fareast;font-variant:small-caps;color:green;
                  mso-no-proof:yes"> </span></b><b><span
                  style="mso-fareast-font-family:"Times New
                  Roman";mso-fareast-theme-font:minor-fareast;
font-variant:small-caps;color:#006600;mso-no-proof:yes">Energy</span><span
style="font-variant:small-caps;color:navy;mso-no-proof:yes"><o:p></o:p></span></b></div>
            <div class="MsoNormal"><span
                style="mso-fareast-font-family:"Times New
                Roman";mso-fareast-theme-font:minor-fareast;
                color:#1F497D;mso-no-proof:yes">2154 Torrance Blvd, Ste.
                100, Torrance, CA 90501<br>
                W: 888-826-1216, X254| D: 310-765-7295 | F: 310-817-2745<o:p></o:p></span></div>
            <div class="MsoNormal"><a moz-do-not-send="true"
                href="http://www.ptrenergy.com/">www.ptrenergy.com</a><span
                style="mso-fareast-font-family:"Times New
                Roman";mso-fareast-theme-font:minor-fareast;
                color:#1F497D;mso-no-proof:yes"> </span><a
                moz-do-not-send="true"
                href="mailto:%7C%20jaulbach@ptrenergy.com">|
                jaulbach@ptrenergy.com</a><span
                style="mso-fareast-font-family:"Times New
                Roman";mso-fareast-theme-font:minor-fareast;
                color:#1F497D;mso-no-proof:yes"><o:p></o:p></span></div>
          </div>
          <div><font face="times new roman, new york, times, serif"><br>
            </font></div>
          <div><font face="times new roman, new york, times, serif"><br>
            </font></div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
    <br>
  </body>
</html>