    Xavier,<br>
    <br>
    It looks like the eQUEST converter is finding a numerical problem in
    the EPW version of the SWEC Barcelona weather file.<br>
    According to the documentation, the SWEC weather files were
    originally developed in DOE-2 *.BIN format, so perhaps<br>
    you could contact the developer listed and see if you can get a copy
    of the *.BIN weather file.<br>
    <br>
    I all read from the documentation that the SWEC weather files were
    generated from monthly statistics, and has constant<br>
    wind speeds for all hours.  Therefore, you should evaluate whether
    the use of these data is appropriate for your needs.<br>
    For example, you should not use the SWEC weather files to study
    natural ventilation !<br>
    <br>
    There are both IWEC and IWEC2 weather files for Barcelonia,
    developed by ASHRAE.   The IWEC version is available on<br>
    the EnergyPlus Weather web site, so you could also try converting
    that file instead to *.BIN.   The IWEC2 weather files<br>
    are currently available only on a DVD from ASHRAE and contains
    weather files for 3,012 stations.  See
    <a class="moz-txt-link-abbreviated" href="http://www.techstreet.com/cgi-bin/detail?product_id=1823067">www.techstreet.com/cgi-bin/detail?product_id=1823067</a> for details.<br>
    <br>
    Joe<br>
    <br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 5/11/2012 3:42 AM, Xavier Rigol wrote:
    <blockquote
cite="mid:!~!UENERkVCMDkAAQACAAAAAAAAAAAAAAAAABgAAAAAAAAANhIZ01RTD0axz5VE0xB5jMKAAAAQAAAAa9qgPeent0S5jXRsTRwiTAEAAAAA@ambsol.com"
      type="cite">
      <meta http-equiv="Context-Type" content="text/html;
        charset=us-ascii">
      <div>
        <p> <span>Hello, </span> </p>
        <p> <span>   </span> </p>
        <p> <span lang="EN-GB">I’m Xavi from Barcelona and I’m a
            recently eQuest user.
            I’m trying to convert the SWEC Barcelona weather file
            (*.epw) to a .BIN
            file and I get an error, yo can see it below. </span> </p>
        <p> <span lang="EN-GB"><img
              src="cid:part1.08060900.07070603@whiteboxtechnologies.com">
          </span> </p>
        <p> <span lang="EN-GB">   </span> </p>
        <p> <span lang="EN-GB">I don’t know what can I do. Does anybody
            can
            help me. Is there any webpage to get a Barcelona.BIN file,
            as I do with .epw
            files? </span> </p>
        <p> <span lang="EN-GB">   </span> </p>
        <p> <span lang="EN-GB">Thank you!!   </span> </p>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>