I don't have a chiller project handy but I quickly, and poorly created an
example boiler load management schedule.  The building has three
boilers, each sized at 0.23 MBH.<br><br>
"Equipment Control 1" =
EQUIP-CTRL      <br>
  
TYPE            
= HEATING<br>
   CIRCULATION-LOOP = "Hot Water Loop"<br>
   LOADS-THRU-1     = 0.23<br>
   LOADS-THRU-2     = 0.4<br>
   LOADS-THRU-3     = 999<br>
   BOILERS-1        = (
"Boiler1", "Boiler2" )<br>
   BOILERS-2        = (
"Boiler 3", "Boiler2" )<br>
   BOILERS-3        = (
"Boiler2", "Boiler1", "Boiler 3" )<br>
   MAX-LOAD-1       = ( 0.15,
0.14 )<br>
   MAX-LOAD-2       = ( 0.2, 0.21
)<br>
   MAX-LOAD-3       = ( 0.22,
0.22, 0.22 )<br>
   ..<br><br>
As you can see, I have boilers coming on and off with little thought to
over lapping.  Boiler 2 is on for all three stages.  <br>
The interface allows for five stages with up to 10 pieces of equipment
defined in each stage.  I am not sure if that covers your
requirements.<br><br>
<br>
At 11:25 AM 08/05/2012, Janne Kairento wrote:<br>
<blockquote type=cite class=cite cite="">Content-Language: en-US<br>
Content-Type: multipart/alternative;<br>
<x-tab>        </x-tab>
boundary="_000_E5A7104ECDC89A42975CEB90789258B6052D07E98541B2QSE01b2ql_"<br>
<br>
Hello,<br>
 <br>
I have building with 6 chillers (2 different capacities) and I would like
to model them with 14 stages of operation.  How can I independently
control the increment (add chiller) and decrement (stop lag chiller) of
an individual chiller stage. I was using equipment control, however, the
saw tooth approach does not account for the overlap of plant stages.
Thank you for your time.<br>
 <br>
Regards,<br>
 <br>
<b>Janne Kairento LEED AP, EIT<br>
</b>Designer<br>
<b>B2Q Associates, Inc.<br>
</b>146 Main Street<br>
North Andover, MA 01845<br>
Office: 978.208.0609 x209<br>
Fax: 978.719.6339<br>
Mobile: 978.210.7397<br>
<a href="http://www.b2qassociates.com/">www.b2qassociates.com</a><br>
 <br>
The contents of this e-mail and any attachments are confidential and the
property of the B2Q Associates, Inc. The e-mail contents are only to be
used by the intended recipient of the e-mail. If you are not the intended
recipient then use, disclosure, copying, distribution or reliance on the
e-mail is prohibited. All professional advice from us should be obtained
in writing (not e-mail).<br>
 <br>
 <br>
 <br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" eudora="autourl">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
<br>
To unsubscribe from this mailing list send  a blank message to
EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</blockquote>
<x-sigsep><p></x-sigsep>
>><br>
Christopher Jones, P.Eng.<br>
Suite 1801, 1 Yonge Street<br>
Toronto, ON M5E1W7<br>
Tel. 416-203-7465<br>
Fax. 416-946-1005<br>
email cj@enersave.ca<br>
</body>
</html>