    Instead of setting SYSTEM:COOLING-CAPACITY, set
    ZONE:COOLING-CAPACITY with this expression and it should work. SPACE
    is a directly referenced command from the ZONE command, not the
    SYSTEM command. Do not input anything for SYSTEM:COOLING-CAPACITY.
    PTAC is a zonal system. Each zone underneath a SYSTEM of TYPE = PTAC
    gets its own system. All capacity inputs at the SYSTEM command for
    PTAC only serve as defaults for the individual zonal systems. So if
    your capacity varies by each individual PTAC, which this expression
    implies, then COOLING-CAPACITY should be input at the ZONE.<br>
    <pre class="moz-signature" cols="72">Kevin</pre>
    <br>
    On 5/2/2012 1:12 PM, Vipul Babriya wrote:
    <blockquote
      cite="mid:8CEF6B701BFD48A-960-233E6@webmail-m064.sysops.aol.com"
      type="cite"><font color="black" face="Arial, Helvetica,
        sans-serif" size="2"><font color="black" face="Arial, Helvetica,
          sans-serif" size="2">Hello All,<br>
          <br>
          I am trying to set up user expression for defining the cooling
          capacity @ system level based on total cooling SF, total
          cooling capacity and local space area. i have PTAC system and
          it is system per zone. <br>
          For Example, <br>
          Total Project Cooling cap = X<br>
          Total Project Area = Y<br>
          <br>
          Cooling capacity for each system = #pa("</font><font
          color="black" face="Arial, Helvetica, sans-serif" size="2">Total
          Project Cooling cap")/</font><font color="black" face="Arial,
          Helvetica, sans-serif" size="2"> #pa("</font><font
          color="black" face="Arial, Helvetica, sans-serif" size="2">Total
          Project Area</font><font color="black" face="Arial, Helvetica,
          sans-serif" size="2">")* <span style="background-color:
            chartreuse;">#LR("SPACE","AREA") <span
              style="background-color: white;"><br>
              <br>
              Above expression does not work since i am referencing
              local space @ system level.<br>
              <br>
              Do anybody have any idea how to recall local space area @
              system level.<br>
              <br>
              Thanks in advance.<br>
              <br>
              Vipul<br>
            </span><font bgcolor="white"><font color="white"><br>
                <br>
                <br>
                <br>
              </font></font></span></font></font>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>