    <font size="+1"><tt>Current ASHRAE fundamentals 2009 has this
        information in Chapter 16.  Various testing indicates a
        magnitude of 10 between tight and loose.  The older the building
        the more leaky it typically is.  I have seen testing with
        magnitude differences of 20 on homes between 5 and 25 years old.
          You also have wind and stack effects.  A blower door test is a
        quick and cheap way to get a effective air leakage area.  It
        will give you better results in predicting the economic impacts
        of improvements and sizing your systems.  The blower door
        operator can also take a smoke generator and in a few minutes
        give you an idea of your major leakage points.  Sometimes a tube
        of caulking is paid for in less time than it takes to install.<br>
        Bruce Easterbrook P.Eng.<br>
        Abode Engineering<br>
      </tt></font><br>
    On 24/04/2012 01:07 PM, Nick Caton wrote:
    <blockquote
cite="mid:ECDF361A89E5FA479BE7E64C658B52050CAF8FC2@SANDBINC4.sbi.smithboucher.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"Stylus BT";
        panose-1:2 14 4 2 2 2 6 2 3 4;}
@font-face
        {font-family:Verdana;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:"Droid Serif";
        panose-1:0 0 0 0 0 0 0 0 0 0;}
@font-face
        {font-family:"\@MS Mincho";
        panose-1:2 2 6 9 4 2 5 8 3 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0in;
        mso-margin-bottom-alt:auto;
        margin-left:0in;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0in;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";}
span.EmailStyle18
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="2050" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">For
            an “old townhouse,” I think you may want to reference the
            ASHRAE fundamentals table for residential constructions
            (Fundamentals 2001, Ch28, Table 7)…  they surveyed a bunch
            of homes that were up to a few decades old to come up with a
            table that shows varying ACH rates, for “tight” to “loose”
            construction, varying with the OADT. 
            <u>The tightest value given is 0.41</u>.  Again this isn’t a
            standard but rather based on real-world measurements.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">A
            very good (and long) discussion thread is in the
            equest-users archives discussing alternate infiltration
            resources as well:  thread title was “Basic stuff –
            Infiltration”<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">~Nick<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><img
              id="Picture_x0020_1"
              src="cid:part1.07050709.01020002@bellnet.ca"
              alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span
              style="font-size:11.0pt;font-family:"Stylus
              BT","sans-serif";color:#2D4D5E"><o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:11.0pt;font-family:"Stylus
              BT","sans-serif";color:#2D4D5E"><o:p> </o:p></span></b></p>
        <p class="MsoNormal"><b><span style="font-family:"Stylus
              BT","sans-serif";color:#2D4D5E">NICK CATON,
              P.E.</span></b><b><span style="font-family:"Stylus
              BT","sans-serif";color:#2D4D5E"><o:p></o:p></span></b></p>
        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900">SENIOR
            ENGINEER<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Calibri","sans-serif";color:#CC9900"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">Smith
            & Boucher Engineers</span><span
            style="font-size:7.5pt;color:#CC9900"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">25501
            west valley parkway, suite 200<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">olathe,
            ks 66061<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">direct
            913.344.0036<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:#2D4D5E">fax
            913.345.0617<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><a
              moz-do-not-send="true" href="www.smithboucher.com"
              title="blocked::www.smithboucher.com"><span
                style="font-size:10.0pt">www.smithboucher.com</span></a></span><u><span
style="font-size:10.0pt;font-family:"Calibri","sans-serif";color:blue">
            </span></u><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div style="border:none;border-top:solid #B5C4DF
          1.0pt;padding:3.0pt 0in 0in 0in">
          <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif"">
              <a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
              [<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
              <b>On Behalf Of </b>CleanTech Analytics<br>
              <b>Sent:</b> Tuesday, April 24, 2012 2:32 AM<br>
              <b>To:</b> xiaoyang shi<br>
              <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
              <b>Subject:</b> Re: [Equest-users] infiltration rate<o:p></o:p></span></p>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal"><span
style="font-family:"Verdana","sans-serif";color:#336666">.35
            ACH is the BPI standard, any tighter and mechanical
            ventilation is required..</span><o:p></o:p></p>
        <div>
          <p class="MsoNormal"><span
style="font-family:"Verdana","sans-serif";color:#336666"><br
                clear="all">
            </span><o:p></o:p></p>
          <p class="MsoNormal"><i><span
style="font-family:"Verdana","sans-serif";color:#999999">Jeremiah
                D. Crossett</span></i><o:p></o:p></p>
          <p class="MsoNormal"><i><span
style="font-family:"Verdana","sans-serif";color:#999999">CleanTech
                Analytics</span></i><o:p></o:p></p>
          <p class="MsoNormal"><i><span
style="font-family:"Verdana","sans-serif";color:#999999">503-688-8951</span></i><o:p></o:p></p>
          <div>
            <p class="MsoNormal"><a moz-do-not-send="true"
                href="http://www.cleantechanalytics.com" target="_blank"><i><span
style="font-family:"Verdana","sans-serif";color:#999999">www.cleantechanalytics.com</span></i></a><o:p></o:p></p>
            <div>
              <p class="MsoNormal" style="text-align:center"
                align="center"><o:p> </o:p></p>
              <p class="MsoNormal" style="text-align:center"
                align="center"><img moz-do-not-send="true"
                  id="_x0000_i1025"
src="http://cleantechanalytics.com/images/stories/cleantech%20analytics%20120.PNG"
                  border="0"><o:p></o:p></p>
            </div>
          </div>
          <div>
            <div>
              <p
                style="margin:0in;margin-bottom:.0001pt;text-align:center"
                align="center"><i><span
                    style="font-size:8.5pt;font-family:"Droid
                    Serif","serif";color:#CCCCCC;background:white">This
                    document may contain valuable information
                    proprietary to CleanTech Analytics which is private
                    and confidential. It may not be shared, copied,
                    stored or transmitted in any form without the prior
                    written consent of CleanTech Analytics</span></i><b><o:p></o:p></b></p>
            </div>
          </div>
          <p class="MsoNormal"><o:p> </o:p></p>
          <div>
            <p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
            <div>
              <p class="MsoNormal">On Mon, Apr 23, 2012 at 11:54 PM,
                xiaoyang shi <<a moz-do-not-send="true"
                  href="mailto:xs2144@gmail.com" target="_blank">xs2144@gmail.com</a>>
                wrote:<o:p></o:p></p>
              <p class="MsoNormal">Hi guys,<o:p></o:p></p>
              <div>
                <p class="MsoNormal"><o:p> </o:p></p>
              </div>
              <div>
                <p class="MsoNormal">Could I ask what is the about
                  infiltration rate of old townhouse in NYC? Where could
                  I find the standard?<o:p></o:p></p>
              </div>
              <div>
                <p class="MsoNormal"><o:p> </o:p></p>
              </div>
              <div>
                <p class="MsoNormal">0.2cfm/ft2? Is it correct?<o:p></o:p></p>
              </div>
              <div>
                <p class="MsoNormal"><o:p> </o:p></p>
              </div>
              <div>
                <p class="MsoNormal">Thanks<o:p></o:p></p>
              </div>
              <div>
                <p class="MsoNormal"><o:p> </o:p></p>
              </div>
              <div>
                <p class="MsoNormal">Yang<o:p></o:p></p>
              </div>
              <p class="MsoNormal" style="margin-bottom:12.0pt"><br>
                _______________________________________________<br>
                Equest-users mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                  target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">
                  EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><o:p></o:p></p>
            </div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>