<div class="gmail_extra"><br>Use Powered induction for the system type, and in the cooling source under the cooling->coil capacity/control tab cool source as electric DX. If eQuest is not allowing that, maybe you don't have the latest version (actually this has been possible for quite some time).</div>
<div class="gmail_extra">-Rohini<br></div><div class="gmail_quote">On Wed, Apr 25, 2012 at 10:00 AM, Caleb Freeman <span dir="ltr"><<a href="mailto:calebsfreeman@gmail.com" target="_blank">calebsfreeman@gmail.com</a>></span> wrote:<br>
<blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid" class="gmail_quote"><div>I am modeling an ASHRAE system type 6 and cannot seem to get equest to model this system type. I have tried to user override the VAV to parallel but that does not work. The default expression is set up to only allow parallel piu boxes for a piu system, but the only available piu system type is chilled water. Any suggestions to override the VAV box type or the system type to DX from CHW would be helpful.</div>
<div> </div>
<div>Thanks in advance,</div>
<div><br>Caleb</div>