<div><font color="#3333ff" face="verdana, sans-serif">Dear Sambhav,</font></div><div><font color="#3333ff" face="verdana, sans-serif"><br></font></div><div><font color="#3333ff" face="verdana, sans-serif">You have specified Duct losses without a </font><span style="color:rgb(51,51,255);font-family:verdana,sans-serif"><u>DUCT-LOSS-ZONE</u></span><span style="color:rgb(51,51,255);font-family:verdana,sans-serif">. Find revised file as an </span><span style="color:rgb(51,51,255);font-family:verdana,sans-serif">attachment</span><span style="color:rgb(51,51,255);font-family:verdana,sans-serif">. </span></div>
<div><font color="#3333ff" face="verdana, sans-serif"><br></font></div><div><h5>DUCT-AIR-LOSS</h5>
<p class="MsoBodyText">Fraction of the supply air that is lost from the ductwork,
thereby reducing the design supply air at the zones. Air lost from the ductwork
will change the temperature of the zone specified by DUCT-ZONE, which must be a
plenum or unconditioned space. </p>
<p class="MsoBodyText">If the DUCT-ZONE is a plenum, then the duct air loss
changes the temperature of the return air entering the plenum. If the DUCT-ZONE
is an unconditioned space the duct air loss acts to change the temperature of
the zone. The program does not currently simulate duct losses to conditioned
spaces.</p></div><font color="#3333ff"><font face="verdana,sans-serif"><div><font color="#3333ff"><font face="verdana,sans-serif"><br></font></font></div><div><br></div><div> ***ERROR***********************************************************************</div>
<div> Duct losses are specified without a DUCT-LOSS-ZONE;</div><div> No plenum exists for default duct losses.</div><div><br></div><div><br></div><div>I hope some senior HVAC/Modeling consultant can shed some light on this.</div>
<div><br></div><div>Thanks!</div><div><br></div><div><br></div></font></font><br><div class="gmail_quote">On Thu, Apr 19, 2012 at 12:10 PM, sambhav tiwari <span dir="ltr"><<a href="mailto:tiwari.sambhav@gmail.com">tiwari.sambhav@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Hi All,<br>
I was done with model and was simulating it ,in between<br>
simulation i am having program run terminated due to error but when i<br>
checked the building description it is showing no error neither while<br>
opening the pd2 file any error is coming then what can be the reason.<br>
<br>
Only it shown when the run terminated" standard file writing" error<br>
but i dont know what is that.<br>
<br>
please if someone can respond its very urgent. attached the file also<br>
<br>
<br>
Thanks<br>
<span class="HOEnZb"><font color="#888888">Sambhav<br>
</font></span><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div style="TEXT-ALIGN:left"><span style="BACKGROUND-COLOR:rgb(51,51,255)"><font face="verdana, sans-serif"><font style="BACKGROUND-COLOR:#ffffff"></font><br>
</font></span></div><font style="BACKGROUND-COLOR:rgb(51,51,255)" face="verdana, sans-serif">
<div style="TEXT-ALIGN:left"><span style="COLOR:rgb(0,0,153)"><br></span></div><font color="#000099">
<div style="TEXT-ALIGN:left"><font style="BACKGROUND-COLOR:#ffffff">Javed Iqbal, LEED AP, CEA</font></div>
<div style="TEXT-ALIGN:left"><font style="BACKGROUND-COLOR:#ffffff"><font color="#000099">Energy Analyst </font><font style="COLOR:rgb(102,102,102)" size="2"> </font></font></div></font></font>
<div style="TEXT-ALIGN:left"><br></div><br>