If you leave the thermostats in the space as undefined and the fan schedule in the HVAC tab, the results should show that the HVAC never turns on, and give you the results you are wishing to see.<div><br></div><div>Hope this helps,</div>
<div>Rob<br><br><div class="gmail_quote">On Wed, Apr 18, 2012 at 3:08 PM, <span dir="ltr"><<a href="mailto:bfountain@greensim.com">bfountain@greensim.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
If the fan schedule is off (and fan control isn't cycle at night) eQUEST doesn't really look at space temp.<br>
<br>
My inclination would be to create a psz system serving your space with very small cooling capacity (e.g. 1 BTU/hr -- 0 will cause it to autosize) an an 'always on' fan schedule. Fan volume would depend on whether you wanted to introduce OA.<br>
Brian Fountain<br>
<a href="mailto:bfountain@greensim.com">bfountain@greensim.com</a><br>
<br>
-----Original Message-----<br>
From: Ekaterina Tzekova <<a href="mailto:ekaterina.tzekova@mail.utoronto.ca">ekaterina.tzekova@mail.utoronto.ca</a>><br>
Sender: equest-users-bounces@lists.onebuilding.orgDate: Wed, 18 Apr 2012 18:38:35<br>
To: <a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><<a href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a>><br>
Subject: [Equest-users] Interior Space Temperature<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br>
<br>
_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
</blockquote></div><br><br clear="all"><div><br></div>-- <br>Rob Hudson<br>
</div>