<tt><font size="+1">You don't always get an increase in cooling by
increasing your tonnage. You airflow only has a certain
capacity with the delta T you have set. Try leaving your model
on auto size, go to your thermal zones in the air-side HVAC
tab. One base specifications tab middle right side try
increasing your min design flow. Default is 0.6 which in many
cases is to low. Energy savings dictate you only move as much
air as you need to do the job. Try increasing this value.
eQuest will itself increase the tonnage and this should start
reducing your unmet hours.<br>
Bruce Easterbrook P.Eng.<br>
Abode Engineering<br>
</font></tt><br>
On 18/04/2012 07:15 AM, ramesh buddhi wrote:
<blockquote
cite="mid:1334747716.94318.YahooMailNeo@web2710.biz.mail.sg3.yahoo.com"
type="cite">
<div style="color:#000; background-color:#fff;
font-family:verdana, helvetica, sans-serif;font-size:10pt"><b><span
style="font-weight:bold;"></span></b>
<div style="font-family: verdana, helvetica, sans-serif;
font-size: 10pt;">
<div style="font-family: times new roman, new york, times,
serif; font-size: 12pt;">
<div id="yiv1908685305">
<div>
<div
style="color:#000;background-color:#fff;font-family:verdana,
helvetica, sans-serif;font-size:10pt;">
<div><span>Dear Folks</span></div>
<div><br>
<span></span></div>
<div><span>I am running an multistorey two bedroom <span
id="yiv1908685305misspell-1"
class="yiv1908685305"><span>apartment</span></span>
house, I considered two bedroom in each unit
(Flat) as <span id="yiv1908685305misspell-2"
class="yiv1908685305"><span>air-conditioned</span></span>,
I had separated conditioned and non-conditioned
into two separate zones and arrived at an overall
tonnage of about 120. When i tried to check the
Load unmet hours in the detailed report for
conditioned zone it shows some x hours as unmet,
then i increased the tonnage so that i can get
into an stage where there will not have any unmet
hours but even i increased the total tonnage the <span
id="yiv1908685305misspell-3"
class="yiv1908685305"><span>results</span></span>
shows the same amount of unmet hours. Can any one
help me out on this, I had attached the eQuest
file for your reference. Thanks a lot in advance.</span></div>
<div><span><br>
</span></div>
<div><span>Regards</span></div>
<div><span>Ramesh BR</span> <br>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>