This is a topic that I have explored. Although DOE-2 (the core
engine for eQUEST) does not explicitly solve for the inside surface
temperatures, researchers at EMPA in Switzerland back in the late
90's added a routine to DOE-2.1E to back-calculate the inside
surface temperatures (think of it as doing a heat balance
calculation in reverse). This featured is documented in DOE-2.1E
update package 2 (version 107), but I only have a hard copy of the
report. In 2003, I used this feature to do exactly what Jason is
asking, i.e., calculate<br>
the PMV for naturally ventilated buildings in Egypt. Recently, I've
also used the same feature to estimate the amount of radiant heat<br>
transfer from attics to the conditioned space, something that is
ignored in the weighting factor model in DOE-2. <br>
<br>
The bad news, though, is that this feature has not been carried over
from DOE-2.1E to DOE-2.2, although I've had some discussions<br>
with members of the development team about resurrecting it. <br>
<br>
Joe<br>
<pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
<br>
On 4/11/2012 3:42 PM, Alex Krickx wrote:
<blockquote
cite="mid:B8B836A09111F041A16C8A3690FB3563FEEDACAA95@EXVMBX015-6.exch015.msoutlookonline.net"
type="cite">
<meta http-equiv="Context-Type" content="text/html;
charset=us-ascii">
<div>
<p><span>Hi Jason, </span></p>
<p><span> </span></p>
<p><span>I’m under the impression that eQUEST can’t output
surface temperatures which are needed to calculate PMV
values. </span></p>
<p><span> </span></p>
<p><span>I think an EnergyPlus based program might be a better
place to look. I would ask on the Bldg-Sim list for
recommendations as it has a broader user-base (this list is
eQUEST specific). </span></p>
<p><span> </span></p>
<p><span>Good luck, </span></p>
<p><span>Alex </span></p>
<p><span> </span></p>
<p><span>Alex Krickx, LEED AP </span></p>
<p><span>Building Energy Specialist </span></p>
<p><span>Serious Energy, Inc. </span></p>
<p><span>1250 Elko Dr, Sunnyvale, CA 94089 </span></p>
<p><span>(t) 408.541.8124 </span></p>
<p><span><a class="moz-txt-link-abbreviated" href="mailto:akrickx@seriousenergy.com">akrickx@seriousenergy.com</a> </span></p>
<p><span> </span></p>
<p><i><span>The information contained in this e-mail and any
attachments may be confidential, proprietary and/or
privileged. If you are not the intended recipient then you
have received it in error and any review, distribution or
copying of this message and any attachments is prohibited
and you are to notify the sender immediately by reply
e-mail and delete immediately this message and any
attachments.</span></i><span> </span></p>
<p><span> </span></p>
<p><span> </span></p>
<div>
<p><b><span>From:</span></b><span>
<a class="moz-txt-link-abbreviated" href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
[<a class="moz-txt-link-freetext" href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>] <b>On
Behalf Of </b>Jason Quinn<br>
<b>Sent:</b> Wednesday, April 11, 2012 3:36 PM<br>
<b>To:</b> <a class="moz-txt-link-abbreviated" href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Can you use eQuest for PMV
calculations? </span></p>
</div>
<p> </p>
<p>Is it possible to use an eQuest model to do thermal comfort
PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884? </p>
<p>If not are there any recommendations? </p>
</div>
<pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>