    Varkie,<br>
    <br>
    That's interesting, so at least there are three people who've used
    the the EMPA surface temperature calculation in DOE-2.1E (EMPA, you,
    and me) :-)<br>
    <br>
    In case anyone's interested, I'm attaching some more information on
    this feature in 2.1E:<br>
    (1) original documentation by Markus Koschenz of EMPA from the 2.1
    Update, Version 107<br>
    (2) my description of  the comfort calculator that I implemented in
    2003 as a User Function to 2.1E.<br>
        <br>
    Call me old style, but I really like the User Function in DOE-2.1E,
    because it allowed me to add features and tweaks to the program to
    get the information that I need, instead of just waiting for<br>
    the next release of whatever program you're using.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 4/12/2012 7:06 AM, Varkie C Thomas wrote:
    <blockquote cite="mid:faed8986a6df.4f869b11@iit.edu" type="cite">
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><font
          face="Calibri"><b style=""><span style="font-size: 14pt;">DOE-2
              Supplement Version 21E</span></b><span style="font-size:
            12pt;"><o:p></o:p></span></font></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">December 1993<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><o:p></o:p></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">Appendix A<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">Hourly Report
            Variables<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">Page<span
              style="">    </span>A10<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><o:p><font face="Calibri"> </font></o:p></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">LOADS<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">Variable-Type =
            u-name of EXTERIOR-WALL<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><o:p></o:p></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">Variable List
            Number<span style=""> </span>5<span style="">         </span>Q<span
              style="">         </span>Heat transfer from wall to the
            zone un-weighted (Btu/hr)<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">Variable List
            Number<span style=""> </span>6<span style="">          </span>T<span
              style="">          </span>Outside surface temperature
            (Rankine)<o:p></o:p></font></span></p>
      <br>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><o:p></o:p></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri">The outside
            surface temp was used to calculate the inside surface temp
            in this example<o:p></o:p></font></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><a moz-do-not-send="true"
            href="http://bepan.info/contents"><font color="#0000ff"
              face="Calibri">http://bepan.info/contents</font></a><o:p></o:p></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><a moz-do-not-send="true"
            href="http://bepan.info/proj-doe21e/p22_kuwait-shell-mrt"><font
              color="#0000ff" face="Calibri">http://bepan.info/proj-doe21e/p22_kuwait-shell-mrt</font></a><o:p></o:p></span></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><font face="Calibri"></font></span><a
          moz-do-not-send="true"
href="http://bepan.info/yahoo_site_admin/assets/docs/Kuwait-Envelope-Temps-MRT-Systems-Study.14972445.pdf"
          type="4" _mce_href=""><font color="#0000ff"><font
              face="Calibri">Proj-22 -
              Kuwait-Envelope-Temps-MRT-Systems-Study<span
                style="overflow: hidden;" id="mce_0_end"
                data-mce-type="bookmark"></span></font></font></a><o:p></o:p></p>
      <p style="margin: 0in 0in 0pt;" class="MsoNoSpacing"><span
          style="font-size: 12pt;"><o:p><font face="Calibri"> </font></o:p></span></p>
      <br>
      <br>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      This is a topic that I have explored.  Although DOE-2 (the core
      engine for eQUEST) does not explicitly solve for the inside
      surface temperatures, researchers at EMPA in Switzerland back in
      the late 90's added a routine to DOE-2.1E to back-calculate the
      inside surface temperatures (think of it as doing a heat balance
      calculation in reverse).  This featured is documented in DOE-2.1E
      update package 2 (version 107), but I only have a hard copy of the
      report.   In 2003, I used this feature to do exactly what Jason is
      asking, i.e., calculate<br>
      the PMV for naturally ventilated buildings in Egypt.  Recently,
      I've also used the same feature to estimate the amount of radiant
      heat<br>
      transfer from attics to the conditioned space, something that is
      ignored in the weighting factor model in DOE-2.  <br>
      <br>
      The bad news, though, is that this feature has not been carried
      over from DOE-2.1E to DOE-2.2, although I've had some discussions<br>
      with members of the development team about resurrecting it.  <br>
      <br>
      Joe<br>
      <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
      <br>
      On 4/11/2012 3:42 PM, Alex Krickx wrote:
      <blockquote
cite="mid:B8B836A09111F041A16C8A3690FB3563FEEDACAA95@EXVMBX015-6.exch015.msoutlookonline.net"
        type="cite">
        <meta http-equiv="Context-Type" content="text/html;
          charset=us-ascii">
        <div>
          <p><span>Hi Jason, </span></p>
          <p><span>   </span></p>
          <p><span>I’m under the impression that eQUEST can’t output
              surface temperatures which are needed to calculate PMV
              values. </span></p>
          <p><span>   </span></p>
          <p><span>I think an EnergyPlus based program might be a better
              place to look. I would ask on the Bldg-Sim list for
              recommendations as it has a broader user-base (this list
              is eQUEST specific). </span></p>
          <p><span>   </span></p>
          <p><span>Good luck, </span></p>
          <p><span>Alex </span></p>
          <p><span>   </span></p>
          <p><span>Alex Krickx, LEED AP </span></p>
          <p><span>Building Energy Specialist </span></p>
          <p><span>Serious Energy, Inc. </span></p>
          <p><span>1250 Elko Dr, Sunnyvale, CA 94089 </span></p>
          <p><span>(t) 408.541.8124 </span></p>
          <p><span><a moz-do-not-send="true"
                class="moz-txt-link-abbreviated"
                href="mailto:akrickx@seriousenergy.com">akrickx@seriousenergy.com</a>
            </span></p>
          <p><span>   </span></p>
          <p><i><span>The information contained in this e-mail and any
                attachments may be confidential, proprietary and/or
                privileged. If you are not the intended recipient then
                you have received it in error and any review,
                distribution or copying of this message and any
                attachments is prohibited and you are to notify the
                sender immediately by reply e-mail and delete
                immediately this message and any attachments.</span></i><span>
            </span></p>
          <p><span>   </span></p>
          <p><span>   </span></p>
          <div>
            <p><b><span>From:</span></b><span> <a
                  moz-do-not-send="true"
                  class="moz-txt-link-abbreviated"
                  href="mailto:equest-users-bounces@lists.onebuilding.org">equest-users-bounces@lists.onebuilding.org</a>
                [<a moz-do-not-send="true" class="moz-txt-link-freetext"
href="mailto:equest-users-bounces@lists.onebuilding.org">mailto:equest-users-bounces@lists.onebuilding.org</a>]
                <b>On Behalf Of </b>Jason Quinn<br>
                <b>Sent:</b> Wednesday, April 11, 2012 3:36 PM<br>
                <b>To:</b> <a moz-do-not-send="true"
                  class="moz-txt-link-abbreviated"
                  href="mailto:equest-users@lists.onebuilding.org">equest-users@lists.onebuilding.org</a><br>
                <b>Subject:</b> [Equest-users] Can you use eQuest for
                PMV calculations? </span></p>
          </div>
          <p>   </p>
          <p>Is it possible to use an eQuest model to do thermal comfort
            PMV (Predicted Mean Vote) calculations per ASHRAE 55/RP884?
          </p>
          <p>If not are there any recommendations? </p>
        </div>
        <pre wrap=""><fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
      </blockquote>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>