<html>
  <head>
    <meta content="text/html; charset=ISO-8859-1"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <font size="+1"><tt>Auto sizing is to ball park your system.  There
        is no computer program which with the press of a button will
        design your building for you.  You have unmet hours because you
        have conflicts in your design. You now have to identify the
        conflicts and resolve them.  eQuest works by prioritizing the
        cooling system, hence when you have conflicts they show up
        mostly as unheated hours.  eQuest has a low default on airflow,
        0.5 cfm/SF, this many times is a good place to start.  Depending
        on where you are 0.75 or 1.0 could work better.  You can also
        vary the flow to different zones independently.  You can't put
        0.5 cfm into 20 spaces from the same AHU and expect the heating
        and cooling needs of each space to be met 100% of the time.  Get
        into your sim file and figure out where the spaces are with
        large unmet hours, figure out why and start adjusting the inputs
        to reduce them.<br>
        There is no point to average the 4 orientations, nor is it
        allowed, just LEED mumbo jumbo.  It just illustrates how the
        orientation of your building effects the energy consumption to
        run it.  Most modellers get a building, a street, a front and
        back with no option on orientation.  That is your base case.  It
        can be handy to illustrate design flaws if there is a large
        difference in energy consumption in different directions.  Just
        don't call it that when you are telling the architect a 20 story
        atrium is not a great idea on the north side of a building. lol.<br>
      </tt></font><font size="+1"><tt>Bruce Easterbrook P.Eng.<br>
        Abode Engineering</tt></font><br>
    <br>
    On 10/04/2012 02:53 PM, Yusuf Turab wrote:
    <blockquote
cite="mid:CACVeg1XXC-bH98HcYcF5sK9_zyuRtB8UH9caTH0y3s6GVvFD_A@mail.gmail.com"
      type="cite">Hello Group<br>
      <ul>
        <li>Why do I get unmet hours even when I select the auto size
          option in the HVAC system? What is the point of auto sizing?<br>
        </li>
        <li>Is there a way to simulate all 4 orientations and get an
          average result for the base case?</li>
      </ul>
      <p>Thanks<br>
      </p>
      Yusuf Turab<br>
      IGBC Accredited Professional, LEED Green Associate & GRIHA
      Trainer<br>
      Y T Enterprises<br>
      18 A, Hamsa Layout ¦ R.S Puram ¦ Coimbatore - 641002<br>
      <br>
      <a moz-do-not-send="true" href="http://www.ytenterprises.com/"
        target="_blank">http://www.ytenterprises.com/</a><br>
      <br>
      ***** Email confidentiality notice *****<br>
      The information contained in this email and any attachments is
      intended for the name recipients only. It may contain privileged
      and confidential information and if you are not the intended
      recipient, you must not copy distribute or take any action in
      reliance on it. If you have received this email in error, please
      return it to the sender advising of the error and delete all
      copies from your system.<br>
      <br>
      <br>
      <div class="gmail_quote">On 10 April 2012 00:54, Yusuf Turab <span
          dir="ltr"><<a moz-do-not-send="true"
            href="mailto:yusuf@ytenterprises.com">yusuf@ytenterprises.com</a>></span>
        wrote:<br>
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">
          Hello Group<br>
          <br>
                       I have just started working on my first energy
          modeling project. I have two questions:<br>
          <ul>
            <li>How do I model roof reflectivity. I want to model a roof
              of 4 inch concrete with 1 inch stucco at the bottom and
              top and cover the roof with cool roof tiles. I am not sure
              how I can account for the energy efficiency gains compared
              to base case through a high SRI roof.</li>
            <li>I am trying to model a large gated community with 330
              villas and 7 other common buildings. As someone suggested
              on this group I am modeling each building type separately
              and using excel to come up with a total energy usage. But
              I am not sure how to model the street lighting and
              landscape lighting at the exteriors. We plan to use solar
              street lights and I want to demonstrate the savings
              through use of solar energy.</li>
          </ul>
          Many Thanks<br>
           <br>
          Yusuf Turab<br>
          <br>
          <br>
          <br>
          <div class="gmail_quote">On 10 April 2012 00:32, nirupama
            lakshminarasimhan <span dir="ltr"><<a
                moz-do-not-send="true"
                href="mailto:nirupamalnarasimhan@gmail.com"
                target="_blank">nirupamalnarasimhan@gmail.com</a>></span>
            wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <p>I am modeling a big public school with a lot of systems
                and custom windows. The equest file we have right now is
                taking too long to load. I've tried opening it from
                different locations- the default equest project folder
                on C: , the public server, external HDD, etc. It is just
                too slow in "importing project data" when it opens. The
                last time this happened, it was taking too long to load
                the BDL file and I ended up deleting a host of systems
                and starting from scratch. All my files- the .inp, .pd2,
                etc are in the same path. I just cannot get it to work
                faster. I'm trying to calibrate the model and it is an
                awfully long wait for each simulation. Does someone have
                any thoughts on how I could get this to work faster? </p>
              <p> </p>
              <p>Thank you.</p>
              <span><font color="#888888">
                  <p>Nirupama</p>
                </font></span><br>
              _______________________________________________<br>
              Equest-users mailing list<br>
              <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
                target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
              To unsubscribe from this mailing list send  a blank
              message to <a moz-do-not-send="true"
                href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG"
                target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              <br>
            </blockquote>
          </div>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>