<div>Is this a regular chiller and and are you using heat recovered from it to heat the hw loop? If yes, you can use the heat recovery field on the chiller tab and set it to the hw loop, with the heat recovery % at 80%-85%.</div>
<div>-Rohini<br><br></div><div class="gmail_quote">2012/3/21 Jimmy Law <span dir="ltr"><<a href="mailto:lawchh@gmail.com">lawchh@gmail.com</a>></span><br><blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid" class="gmail_quote">
<u></u>





<div style="margin:10px;font-family:verdana;font-size:10pt">
<div><font face="Verdana">Dear all, </font></div>
<div> </div>
<div>Recently I am trying to do heat-pump screw chiller with a fluid 
cooling tower for a commercial building in a sub-tropical area, which means it 
will mostly run like a normal chiller and will supply HW in 40 degreeC for 
heating in just two or three month. Meanswhile, whenever I 
chose Loop-Loop Heat Pump and just Heat Pump for chiller 
type, the chiller obviously can not be connected to the CW loop but only to 
LAKE/WELL loop. Can anyone please give me any advice to solve this issue 
and simulate this system?</div>
<div><font face="Verdana"></font> </div>
<div>Thank you!</div>
<div> </div>
<div><font face="Verdana"><font color="#c0c0c0" face="Verdana"><span><font face="@Arial Unicode MS"><span style="font:13px/normal Tahoma;text-transform:none;text-indent:0px;letter-spacing:normal;word-spacing:0px;float:none;display:inline!important;white-space:normal;font-size-adjust:none;font-stretch:normal"><span style="text-indent:0px!important"><span style="text-indent:0px!important;font-family:Arial,sans-serif;font-size:12pt" lang="EN-US"><font face="@Arial Unicode MS">Regards, 
</font></span></span></span></font></span></font></font></div>
<div>
<div>
<p style="margin:0px 0cm 0pt;padding:0px!important;text-align:left;text-indent:0px!important" align="left"><span style="text-indent:0px!important"><span style="text-indent:0px!important;font-family:Arial,sans-serif;font-size:12pt" lang="EN-US"><font face="@Arial Unicode MS">Jimmy</font></span></span></p>

<div style="font:13px/normal Tahoma;text-transform:none;text-indent:0px;letter-spacing:normal;word-spacing:0px;white-space:normal;font-size-adjust:none;font-stretch:normal">
<div style="text-indent:0px!important" dir="ltr">
<div style="text-indent:0px!important">———————————</div>
<div style="text-indent:0px!important">
<p style="margin:0px 0cm 0pt;padding:0px!important;text-align:left;text-indent:0px!important" align="left"><span style="text-indent:0px!important"><span style="text-indent:0px!important;font-family:Arial,sans-serif;font-size:12pt" lang="EN-US"><font style="text-indent:0px!important" size="2"><font style="text-indent:0px!important" face="@Arial Unicode MS">Jimmy Ching Hin 
LAW</font></font></span></span></p>
<p style="margin:0px 0cm 0pt;padding:0px!important;text-align:left;text-indent:0px!important" align="left"><span style="text-indent:0px!important"><span style="text-indent:0px!important;font-family:Arial,sans-serif;font-size:12pt" lang="EN-US"><font style="text-indent:0px!important" size="2"><font style="text-indent:0px!important" face="@Arial Unicode MS">Mechanical 
Engineer, LEED Green 
Associate</font></font></span></span></p></div></div></div></div></div></div>