Without spending time on your input files, my first guess is to check our heat exchanger fan static pressure. i had a similar situation on a model i was working on in the past few months, and once i entered in 0 for my fan energy (my heat exchanger worked as a DOAS for my system, and therefore the supply fan was accounting for the HX fan) everything went back to normal.<div>
<br></div><div>Hope you find this helpful.</div><div><br></div><div>Rob<br><br><div class="gmail_quote">On Wed, Mar 28, 2012 at 6:31 AM, Jason Quinn <span dir="ltr"><<a href="mailto:jason.e.quinn@gmail.com">jason.e.quinn@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">So this is pretty odd I'm running a simple SD wizard generated office<br>
building and adding the DOAS to it in DD edit mode. The DOAS works as<br>
expected (Thanks to Brian Fountain) slightly lowering the space<br>
heating & increasing vent. Fans. over a case without the DOAS. Now<br>
when I add a heat exchanger to the DOAS (PVVT) it causes the fan usage<br>
to go nuts increasing Vent. Fans from 0.2E6 kWh to 6.5E6 kWh while the<br>
space heating drops from a resonable (I think) 3.7E9BTU to 0.4E9BTU.<br>
<br>
If someone could point me in the right direction to sort out why the<br>
heat exchanger is causing such a huge increase I'd really appreciate<br>
it.<br>
<br>
I have played with the DOAS fan schedules and can effect the increase<br>
downwards but not enough to make this reasonable. I've attached the<br>
DOAS with Heat exchanger .pd2 & .inp file. To see the results without<br>
the heat exchanger just turn it off. I'll attach my weather file as<br>
well so that it's easier to look at my file.<br>
<br>
Thank you for the help.<br>
<span class="HOEnZb"><font color="#888888">Jason<br>
</font></span><br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Rob Hudson<br>
</div>