<html><head><style type="text/css"><!-- DIV {margin:0px;} --></style></head><body><div style="font-family:times new roman,new york,times,serif;font-size:12pt">Michael:<br><br>For the past year every model I have worked on is a VRV system with ERV(s) included to supply ventilation air. I originally was modeling the VRV system as a PVVT as recommended in the Energy Trust slide presentation. I am not sure why a PVVT system was suggested since all of the VRV fan coils I have modeled are equipped with constant volume fan motors.<br><br>I have since switched to using an air-cooled PTAC with heat-pump heating as the system type for the VRV system, especially in projects where the baseline system is a PTAC. You can specify that the PTAC has a variable speed compressor and can plug in the custom curves that you create. The results are what I expect, with an 8%-10% HVAC savings over a 90.1 baseline compliant HVAC system. The overall
building improvements range from 28.5% to 35%, depending on the other improvements to the building, such as a better envelope and glazing. <br><br>The heat recovery savings depend on the building design. Most of the projects I have worked on do not have a core that requires cooling when the perimeter spaces require heating, or vice versa, so the heat recovery savings calculated by the exceptional method outlined in the slides, is minimal.<br><div> </div>Paul Diglio, CEM, CBCP<br><br><div>87 Fairmont Avenue<br>New Haven, CT 06513<br>203-415-0082</div><br><br><div><span><a target="_blank" href="http://www.pdigliollc.com">www.pdigliollc.com</a></span><div><br></div><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><br><div style="font-family:times new roman, new york, times, serif;font-size:12pt"><font face="Tahoma" size="2"><hr size="1"><b><span style="font-weight: bold;">From:</span></b> Daniel Knapp
<danielk@arborus.ca><br><b><span style="font-weight: bold;">To:</span></b> equest-users <equest-users@lists.onebuilding.org><br><b><span style="font-weight: bold;">Sent:</span></b> Mon, March 12, 2012 9:52:24 AM<br><b><span style="font-weight: bold;">Subject:</span></b> Re: [Equest-users] Modeling VRV System<br></font><br>
<base>On the subject of modelling VRF systems, I recently did some tests on a box-model in Ontario (climate zone 6) and compared the results of using PVVT and the WSHP systems. I found that the ability to use variable speed compressors in the PVVT systems – which are not available to the WSHP systems – made a huge difference to the energy savings and that the PVVT performed much better than the WSHP. In this case I was modelling the Mitsubishi system with no heat recovery and was using the performance curves from the “Application for Adoption of Variable Refrigerant Flow Systems Under the Tile 24-2008 Nonresidential ACM Procedures”. <div><br></div><div>Your mileage may vary, and I would strongly recommend building a test building using the wizard that allows you to test your performance curves and VRF modelling approach to make sure you are getting the results you are looking for.
<div><br></div><div>Cheers,</div><div>Dan</div></div><div>
<span class="Apple-style-span" style="border-collapse:separate;color:rgb(0, 0, 0);font-family:Verdana;font-style:normal;font-variant:normal;font-weight:normal;letter-spacing:normal;line-height:normal;orphans:2;text-indent:0px;text-transform:none;white-space:normal;widows:2;word-spacing:0px;font-size:medium;"><div><div>—</div><div>Daniel Knapp, PhD, LEED® AP O+M</div><div><a rel="nofollow" ymailto="mailto:danielk@arborus.ca" target="_blank" href="mailto:danielk@arborus.ca">danielk@arborus.ca</a></div><div><br></div><div>Arborus Consulting</div><div>Energy Strategies for the Built Environment</div><div><a rel="nofollow" target="_blank" href="http://www.arborus.ca">www.arborus.ca</a></div><div>76 Chamberlain Avenue </div><div>Ottawa, ON, K1S 1V9 </div><div>Phone: (613) 234-7178 ext. 113</div><div>Fax: (613) 234-0740</div></div><div><br></div></span><br class="Apple-interchange-newline">
</div>
<br><div><div>On 2012-03-12, at 9:37 AM, Michael Marvin wrote:</div><br class="Apple-interchange-newline"><blockquote type="cite"><span class="Apple-style-span" style="border-collapse:separate;font-family:Verdana;font-style:normal;font-variant:normal;font-weight:normal;letter-spacing:normal;line-height:normal;orphans:2;text-indent:0px;text-transform:none;white-space:normal;widows:2;word-spacing:0px;font-size:medium;"><div lang="EN-US"><div class="WordSection1" style=""><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span style="font-size:10pt;font-family:Arial, sans-serif;" lang="EN-GB">Hi Everyone,</span></div><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span style="font-size:10pt;font-family:Arial, sans-serif;" lang="EN-GB"> </span></div><div
style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span style="font-size:10pt;font-family:Arial, sans-serif;" lang="EN-GB">I know that there’s been some chatter about this in the past, but has anyone determined a good way to simulate a VRV system accurately in eQuest? I’ve seen posts where some people have recommended using PVVT or the Water Heat Pump System, but I’m curious to hear if anyone has found a workaround that they feel works better than the others.</span></div><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span style="font-size:10pt;font-family:Arial, sans-serif;" lang="EN-GB"> </span></div><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span style="font-size:10pt;font-family:Arial,
sans-serif;" lang="EN-GB">Thanks,</span></div><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><b><span style="font-size:8pt;font-family:Arial, sans-serif;">Michael Marvin</span></b><span style="font-size:8pt;font-family:Arial, sans-serif;">, LEED AP<b><br></b>Buro Happold<br>100 Broadway<span class="Apple-converted-space"> </span><br>New York, NY 10005<br>USA<br><br>Tel: (+1) 212 334 2025<br>Email: <a rel="nofollow" title="blocked::mailto:chris.donnell@burohappold.com
mailto:chris.donnell@burohappold.com
mailto:firstname.lastname@burohappold.com" style="color:blue;text-decoration:underline;"><span style="color:windowtext;">michael.marvin@burohappold.com</span></a><br><a rel="nofollow" title="blocked::http://www.burohappold.com/
http://www.burohappold.com/" style="color:blue;text-decoration:underline;"><span style="color:windowtext;">www.burohappold.com</span></a></span></div><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span style="font-size:7pt;font-family:Arial, sans-serif;color:rgb(166, 166, 166);">This transmission is confidential and intended solely for the person or organisation to whom it is correctly addressed. If you are not the intended recipient of this transmission, you should not take any action in reliance on it.Further, this transmission may contain confidential design and other information owned by Buro Happold Ltd. You should not copy, distribute, use, offer for sale or hire such information or in any way infringe the design and intellectual property rights of Buro Happold Ltd. It is intended that communication by email from Buro Happold Ltd or its employees is limited to
communications connected to the services provided by Buro Happold Ltd. Buro Happold Ltd accepts no liability for any communications not connected to the services it provides. Computer viruses may be transmitted or downloaded onto your computer system via email communication. It is the recipient’s responsibility to take any action necessary to prevent computer viruses being transmitted in this way. Accordingly, Buro Happold Ltd dsclaims all responsibility which arises directly or indirectly from such transmission of computer viruses. Buro Happold Ltd. Registered in England: 2049511. Registered Office: Camden Mill, Lower Bristol Road, Bath BA2 3DQ.</span><span style="font-size:7pt;color:rgb(166, 166, 166);"></span></div><div style="margin-top:0in;margin-right:0in;margin-left:0in;margin-bottom:0.0001pt;font-size:11pt;font-family:Calibri, sans-serif;"><span lang="EN-GB"> </span></div></div>
_______________________________________________<br>Equest-users mailing list<br><span><a target="_blank" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a></span><br>To unsubscribe from this mailing list send a blank message to<span class="Apple-converted-space"> </span><a rel="nofollow" ymailto="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" style="color:blue;text-decoration:underline;">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br></div></span></blockquote></div><br></div></div></div>