Using <i>equipment controls</i> you can specify when the chiller
and when the chilled water meter satisfy the load under different
load conditions. However, as you are looking for seasonal control,
you will need to set up a <i>load management</i> for the chilled
water loop. Load management lets you specify which equipment
control strategy is in control based on a schedule, loop load, zone
temp or OAT. So you will have 2 equipment controls - 1 where the
chilled water meter serves the loop and 1 where the building chiller
serves (you also can have a combination). You will also have a load
management which points to the chilled water meter equip control in
the summer (based on a schedule or OAT) and to the chiller equip
control in the winter.<br>
<br>
I do not believe you can have multiple chilled water coils in eQUEST
AHUs.<br>
<br>
Brian<br>
<br>
<br>
<br>
On 3/8/2012 6:03 PM, Jason L. Curtis wrote:
<blockquote
cite="mid:FE42F90348662D4AA5177E97E20458AB73C939303C@Jupiter-B.BVHis.org"
type="cite">
<meta http-equiv="Content-Type" content="text/html;
charset=ISO-8859-1">
<meta name="Generator" content="Microsoft Word 12 (filtered
medium)">
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri","sans-serif";}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:blue;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:purple;
text-decoration:underline;}
span.EmailStyle17
{mso-style-type:personal-compose;
font-family:"Calibri","sans-serif";
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal">I have a building that uses an on-site
chiller during the summer months, but uses chilled water from
a central plant for small dehumidification loads during the
winter and shoulder seasons. Both sources of CHW serve the
same coils in AHUs. Does anyone know how to model this????<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">My issue is that I cannot apply operating
schedules to chillers or to CHW meters!<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Responses are much appreciated!!<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal" style="line-height:150%"><b><span
style="font-size:8.0pt;line-height:150%;font-family:"Arial","sans-serif";color:#244061">Jason
Curtis, Mechanical Engineer I BVH Integrated Services,
Inc.<o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#262626">50
Griffin Road South, Bloomfield, CT 06002 <b>I</b>
860.286.9171 <o:p></o:p></span></p>
<p class="MsoNormal" style="margin-bottom:6.0pt"><span
style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#262626">One
Gateway Center, Suite 701, Newton, MA 02458 <b>I</b>
617.658.9008 <o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#262626"><a
moz-do-not-send="true" href="http://www.bvhis.com/"><span
style="color:#262626;text-decoration:none">bvhis.com</span></a>
I <a moz-do-not-send="true" href="www.twitter.com/bvhis%A0"><span
style="color:#262626;text-decoration:none">twitter.com/bvhis </span></a><b><o:p></o:p></b></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
</blockquote>
</body>
</html>