    John,<br>
    <br>
    This does not surprise me at all.  How are you controlling the
    evaporative coolers?  Many things change when<br>
    you use an evaporative cooler (100% OA, more pre-cooling, etc.) , so
    you may be leaving the building at the lower temperature at the
    beginning of  the next day that then necessitates more heating.  I'd
    suggest you take a look at the indoor temperatures and compare them
    to those with a RTU.  As to what to do about it, it depends on
    what's your objective - to minimize energy cost or electricity, no
    increase in heating fuel, etc.  Achieving that would <br>
    require some tweaking of the operations.<br>
    <br>
    Joe<br>
    <pre class="moz-signature" cols="90">Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
<a class="moz-txt-link-abbreviated" href="mailto:yjhuang@whiteboxtechnologies.com">yjhuang@whiteboxtechnologies.com</a>
<a class="moz-txt-link-abbreviated" href="http://www.whiteboxtechnologies.com">www.whiteboxtechnologies.com</a>
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"
</pre>
    <br>
    On 3/7/2012 4:24 PM, John Aulbach wrote:
    <blockquote
      cite="mid:1331166288.59464.YahooMailNeo@web126103.mail.ne1.yahoo.com"
      type="cite">
      <div style="color: rgb(0, 0, 0); background-color: rgb(255, 255,
        255); font-family: times new roman,new york,times,serif;
        font-size: 12pt;">
        <div style="right: auto;">I took several RTU units and replaced
          them with Evaporative Cooling in the Los Angeles area. In some
          zones, my heating consumption went UP. Any suggestions?</div>
        <div style="right: auto;"> </div>
        <div style="right: auto;">John Aulbach</div>
        <div style="right: auto;">Partner Energy<var id="yui-ie-cursor"></var></div>
      </div>
      <pre wrap="">
<fieldset class="mimeAttachmentHeader"></fieldset>
_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>