When using the VAV or PVAV system types the heating coil can be sized by using the leaving air temperature conditions, but never turns on. The true way to use a heating coil for a VAV is to call it a preheat coil, and specify a leaving air temperature close to what you have in reality. Occasionally, the reality is higher than what eQuest allows (something like 70 degree F) and then you need to "fake" it by making up the rest of the heating load in the reheat coils.<div>
<br></div><div>Hope this helps!</div><div><br></div><div>Rob H.</div><div><br></div><div><br></div><div><br></div><div><br></div><div><br><br><div class="gmail_quote">On Wed, Feb 15, 2012 at 2:31 PM, R B <span dir="ltr"><<a href="mailto:slv3sat@gmail.com">slv3sat@gmail.com</a>></span> wrote:<br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex"><div>I have a system with VFD on the fan, central heating and cooling coils (no reheat), and chilled water for cooling. Curious to see how others would model this, or if I am missing something very obvious.</div>
<div> </div>
<div>If I use VAV, even though there is central coil, it does not come on. The heating seems to be only through the reheat coil. I could do the warmest zone control, but I think this uses only return air, not heating coil for the </div>
<div> </div><div>If I use single zone reheat, cannot get the fan to be variable speed. </div><div> </div><div>PVVVT might work (never tried it) but it does not use chilled water.</div><div> </div><div>I could use a dual duct single fan and the min flows be zero fo both ducts?</div>
<div> </div><div> </div><div>Thanks</div><div>-Rohini</div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br>Rob Hudson<br>