Bob<br><br>     I understand where you are coming from. Indian developers have the same dilemma. Unfortunately, for the prescriptive approach you do not have a choice. You have to design as per the standard even though the ROI is very poor. I suggest you follow the whole building simulation method. You will be able to demonstrate significant savings using simple strategies like shading, high performance glass, optimised orientation etc. This might help you do away with insulating the walls. <br>

<br>Hope this helps<br clear="all">Yusuf Turab<br><br><br><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"></span><div class="gmail_quote"><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">

<div class="gmail_quote"><blockquote style="margin:0px 0px 0px 0.8ex;padding-left:1ex;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid" class="gmail_quote"><div><div class="h5"><div vlink="purple" link="blue" lang="EN-US">

<div>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">Turning that around:<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">“Where you are not required to have insulation, 5.8.1.1-9 does not come into play.”<u></u><u></u></span></p>



<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">I don’t believe this is a “follow either A or B” statement – more like “if A, then B.”<u></u><u></u></span></p>



<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt">~Nick</span><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif";font-size:11pt"><u></u><u></u></span></b></p>



<p class="MsoNormal"><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif";font-size:11pt"><u></u> <u></u></span></b></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><img src="" alt="cid:489575314@22072009-0ABB" height="37" width="119"></span><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif";font-size:11pt"><u></u><u></u></span></b></p>



<p class="MsoNormal"><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif"">NICK CATON, P.E.</span></b><b><span style="color:rgb(45,77,94);font-family:"Stylus BT","sans-serif""><u></u><u></u></span></b></p>



<p class="MsoNormal"><span style="color:rgb(204,153,0);font-family:"Calibri","sans-serif";font-size:7.5pt">SENIOR ENGINEER<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(204,153,0);font-family:"Calibri","sans-serif";font-size:7.5pt"><u></u> <u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">Smith & Boucher Engineers</span><span style="color:rgb(204,153,0);font-size:7.5pt"><u></u><u></u></span></p>



<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">25501 west valley parkway, suite 200<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">olathe, ks 66061<u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">direct <a href="tel:913.344.0036" value="+19133440036" target="_blank">913.344.0036</a><u></u><u></u></span></p>



<p class="MsoNormal"><span style="color:rgb(45,77,94);font-family:"Calibri","sans-serif";font-size:10pt">fax <a href="tel:913.345.0617" value="+19133450617" target="_blank">913.345.0617</a><u></u><u></u></span></p>



<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><a title="blocked::www.smithboucher.com" href="http://www.smithboucher.com" target="_blank"><span style="color:blue;font-size:10pt">www.smithboucher.com</span></a></span><u><span style="color:blue;font-family:"Calibri","sans-serif";font-size:10pt">
</span></u><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u><u></u></span></p>
<p class="MsoNormal"><span style="color:rgb(31,73,125);font-family:"Calibri","sans-serif";font-size:11pt"><u></u> <u></u></span></p>
<div style="border-width:1pt medium medium;border-style:solid none none;border-color:rgb(181,196,223) currentColor currentColor;padding:3pt 0in 0in">
<p class="MsoNormal"><b><span style="font-family:"Tahoma","sans-serif";font-size:10pt">From:</span></b><span style="font-family:"Tahoma","sans-serif";font-size:10pt"> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [mailto:<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>]
<b>On Behalf Of </b>Ty Law<br>
<b>Sent:</b> Tuesday, February 07, 2012 2:28 AM<br>
<b>To:</b> <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> [Equest-users] Fwd: Fw: Mandatory Provisions 5.4<u></u><u></u></span></p>
</div><div><div></div><div>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt">Hi Everyone,</span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"> <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt">I am quite confused between what the ASHRAE 90.1 and the user’s manual tell us about Building Envelope Mandatory Provisions:</span><u></u><u></u></p>



</div>
<div>
<div>
<div>
<div>
<div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt"> </span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><b><i><span style="font-family:"Arial","sans-serif";font-size:10pt">5.4 Mandatory Provisions</span></i></b><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><b><i><span style="font-family:"Arial","sans-serif";font-size:10pt">“5.4.1 Insulation.</span></i></b><i><span style="font-family:"Arial","sans-serif";font-size:10pt"> Where insulation is required in Section</span></i><u></u><u></u></p>



</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">5.5 or 5.6, it shall comply with the requirements found in Sections</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">5.8.1.1 through 5.8.1.9.<b>”</b> - ASHRAE 90.1-2007</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt"> </span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt"> </span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><b><i><span style="font-family:"Arial","sans-serif";font-size:10pt">Insulation (§ 5.8.1)</span></i></b><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><b><i><span style="font-family:"Arial","sans-serif";font-size:10pt">“</span></i></b><i><span style="font-family:"Arial","sans-serif";font-size:10pt">The first set of mandatory requirements</span></i><u></u><u></u></p>



</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">addresses the proper installation and</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">protection of insulation materials. Issues</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">that are covered include compression of</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">insulation, installing insulation on sloping</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">ceilings and around recessed equipment,</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">and protecting insulation from physical or</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt">moisture damage.<b>”</b>- ASHRAE 90.1-2007-User’s Manual</span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><i><span style="font-family:"Arial","sans-serif";font-size:10pt"> </span></i><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt"> </span><u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt">Does this mean that we could use insulation that is not as efficient as indicated in Table 5.5-1 through 5.5-8 as long as it complies with Section 5.8.1.1 through 5.8.1.9?</span><u></u><u></u></p>



</div>
<div>
<p class="MsoNormal"> <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><span style="font-family:"Arial","sans-serif";font-size:10pt">Your thoughts are highly appreciated.</span><u></u><u></u></p>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<p style="margin-bottom:12pt" class="MsoNormal"><u></u> <u></u></p>
</div>
</div>
</div>
</div>
</div>
<p class="MsoNormal"><u></u> <u></u></p>
</div></div></div>
</div>

<br></div></div>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br>