[From nobody Tue Feb  7 13:24:10 2012
From: Nick Caton &lt;ncaton@smithboucher.com&gt;
To: &quot;atowell@cxegroup.com&quot; &lt;atowell@cxegroup.com&gt;, Sheri
	&lt;Sheri@fireandicegeo.com&gt;, &quot;equest-users@lists.onebuilding.org&quot;
	&lt;equest-users@lists.onebuilding.org&gt;
Subject: Re: [Equest-users] multiple floor zones
Thread-Topic: [Equest-users] multiple floor zones
Thread-Index: AcvztdU2y1/VvRtUQG6KVL8fT57ilwAB/88gAAF5tNA=
Sender: &quot;equest-users-bounces@lists.onebuilding.org&quot;
	&lt;equest-users-bounces@lists.onebuilding.org&gt;
Content-Class: urn:content-classes:message
Date: Tue, 5 Apr 2011 19:43:13 +0000
Message-ID: &lt;FCEBC0C28321F7479789B25A13030F69032C88FF@sandbinc2.sbi.smithboucher.com&gt;
References: &lt;48C8675CDF205845B2F609B6F89F83C5035D8F@SERVER.fireice.local&gt;&lt;11CFD2AEFF72D842BB23C529D3E1038F3E540F6A05@P3PW5EX1MB01.EX1.SECURESERVER.NET&gt;
List-Help: &lt;mailto:equest-users-request@lists.onebuilding.org?subject=help&gt;
List-Subscribe: &lt;http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org&gt;,
	&lt;mailto:equest-users-request@lists.onebuilding.org?subject=subscribe&gt;
List-Unsubscribe: &lt;http://lists.onebuilding.org/options.cgi/equest-users-onebuilding.org&gt;,
	&lt;mailto:equest-users-request@lists.onebuilding.org?subject=unsubscribe&gt;
In-Reply-To: &lt;11CFD2AEFF72D842BB23C529D3E1038F3E540F6A05@P3PW5EX1MB01.EX1.SECURESERVER.NET&gt;
Content-Language: en-US
X-MS-Has-Attach: yes
X-Auto-Response-Suppress: All
X-MS-TNEF-Correlator: 
Content-Type: multipart/mixed;
	boundary=&quot;_006_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_&quot;
MIME-Version: 1.0

--_006_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_
Content-Type: multipart/related;
	boundary=&quot;_005_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_&quot;;
	type=&quot;multipart/alternative&quot;

--_005_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_
Content-Type: multipart/alternative;
	boundary=&quot;_000_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_&quot;

--_000_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_
Content-Type: text/plain; charset=&quot;iso-8859-1&quot;
Content-Transfer-Encoding: quoted-printable

Sheri et al,



When you define a shell as a more than 1-story - you are simultaneously mak=
ing the decision that each story will have a matching &quot;typical&quot; zoning layo=
ut.  What you define at the custom zoning screen will be mirrored for each =
level.  This approach/simplification has the advantages of simplifying the =
model, saving input time and also permits the wizards to automatically gene=
rate inter-floor heat transfer surfaces.



If you wish to model distinct zoning patterns for each level (and this is n=
ot uncommon), you should instead create a separate shell for each distinct =
pattern.  For clarity/context, to define multiple shells as described, you =
should convert to DD wizards from SD if you aren't already there.



Some extra pointers for those new to the &quot;shell-per-floor&quot; approach:



1.       Fully &quot;sandwiched&quot; floors defined using separate shells should sel=
ect no (adiabatic) floor and roof constructions, lest you end up multiplyin=
g your roof or ground-perimeter envelope loads.  Do define your roof and fl=
oor surfaces for your top and ground level shells.

2.       If you feel inter-floor heat transfer is critical for the energy m=
odel, or if you have should partially exposed (exterior) roofs/floors for a=
 given shell/level, you can have your cake and eat it too.  Search the arch=
ives for alternative wizard/detailed-mode approaches (my name will be in a =
few of them).  In those cases, you'd define such roof and/or floor construc=
tions for the entire shell/floor, then later either delete or replace &quot;sand=
wiched&quot; surfaces with interior partitions as required in detailed mode.

3.       For any multi-shell project, I would suggest first completing the =
rest of the inputs for the first shell shared by the rest of the building, =
(ex: envelope properties, typical window layouts, whole building LPD's... e=
tc.) before copying to create the next shell.  This will minimize redundant=
 inputs that take extra time and invite human error (i.e. selecting the wal=
l construction inputs in 3 places instead of once).  This advice becomes cr=
itical for projects with many shells.



Best of luck!



~Nick



cid:489575314@22072009-0ABB



NICK CATON, E.I.T.

PROJECT ENGINEER

Smith &amp; Boucher Engineers

25501 west valley parkway

olathe ks 66061

direct 913 344.0036

fax 913 345.0617

www.smithboucher.com



From: equest-users-bounces@lists.onebuilding.org [mailto:equest-users-bounc=
es@lists.onebuilding.org] On Behalf Of atowell@cxegroup.com
Sent: Tuesday, April 05, 2011 1:19 PM
To: Sheri; eQuest List(equest-users@lists.onebuilding.org)
Subject: Re: [Equest-users] multiple floor zones



Sheri-



The best way that I have seen to do this is to create a separate shell for =
each floor, then zone each floor individually. I hope this helps!



Adam Towell

CxE Group, LLC

618-659-9461



From: equest-users-bounces@lists.onebuilding.org [mailto:equest-users-bounc=
es@lists.onebuilding.org] On Behalf Of Sheri
Sent: Tuesday, April 05, 2011 12:21 PM
To: equest-users@lists.onebuilding.org
Subject: [Equest-users] multiple floor zones



Hello,



I have a 3 story building that each floor has multiple zones. How do I do t=
his? When I go into the zoning pattern (which I have selected custom) it br=
ings up my footprint so I can draw out my zones, but how do I know which fl=
oor I am on &amp; how do I switch between floors?



Thank you,



Sheri Rice,

Assistant General Manager

Fire &amp; Ice Geothermal, LLC

198276 E County Road 41

Woodward, OK 73801

580-256-9439 Voice

580-256-7080 Fax

580-216-1005 Cell




--_000_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_
Content-Type: text/html; charset=&quot;iso-8859-1&quot;
Content-Transfer-Encoding: quoted-printable

&lt;html xmlns:v=3D&quot;urn:schemas-microsoft-com:vml&quot; xmlns:o=3D&quot;urn:schemas-micr=
osoft-com:office:office&quot; xmlns:w=3D&quot;urn:schemas-microsoft-com:office:word&quot; =
xmlns:x=3D&quot;urn:schemas-microsoft-com:office:excel&quot; xmlns:p=3D&quot;urn:schemas-m=
icrosoft-com:office:powerpoint&quot; xmlns:a=3D&quot;urn:schemas-microsoft-com:office=
:access&quot; xmlns:dt=3D&quot;uuid:C2F41010-65B3-11d1-A29F-00AA00C14882&quot; xmlns:s=3D&quot;=
uuid:BDC6E3F0-6DA3-11d1-A2A3-00AA00C14882&quot; xmlns:rs=3D&quot;urn:schemas-microsof=
t-com:rowset&quot; xmlns:z=3D&quot;#RowsetSchema&quot; xmlns:b=3D&quot;urn:schemas-microsoft-co=
m:office:publisher&quot; xmlns:ss=3D&quot;urn:schemas-microsoft-com:office:spreadshee=
t&quot; xmlns:c=3D&quot;urn:schemas-microsoft-com:office:component:spreadsheet&quot; xmlns=
:odc=3D&quot;urn:schemas-microsoft-com:office:odc&quot; xmlns:oa=3D&quot;urn:schemas-micro=
soft-com:office:activation&quot; xmlns:html=3D&quot;http://www.w3.org/TR/REC-html40&quot; =
xmlns:q=3D&quot;http://schemas.xmlsoap.org/soap/envelope/&quot; xmlns:rtc=3D&quot;http://m=
icrosoft.com/officenet/conferencing&quot; xmlns:D=3D&quot;DAV:&quot; xmlns:Repl=3D&quot;http://=
schemas.microsoft.com/repl/&quot; xmlns:mt=3D&quot;http://schemas.microsoft.com/share=
point/soap/meetings/&quot; xmlns:x2=3D&quot;http://schemas.microsoft.com/office/excel=
/2003/xml&quot; xmlns:ppda=3D&quot;http://www.passport.com/NameSpace.xsd&quot; xmlns:ois=
=3D&quot;http://schemas.microsoft.com/sharepoint/soap/ois/&quot; xmlns:dir=3D&quot;http://=
schemas.microsoft.com/sharepoint/soap/directory/&quot; xmlns:ds=3D&quot;http://www.w3=
.org/2000/09/xmldsig#&quot; xmlns:dsp=3D&quot;http://schemas.microsoft.com/sharepoint=
/dsp&quot; xmlns:udc=3D&quot;http://schemas.microsoft.com/data/udc&quot; xmlns:xsd=3D&quot;http=
://www.w3.org/2001/XMLSchema&quot; xmlns:sub=3D&quot;http://schemas.microsoft.com/sha=
repoint/soap/2002/1/alerts/&quot; xmlns:ec=3D&quot;http://www.w3.org/2001/04/xmlenc#&quot;=
 xmlns:sp=3D&quot;http://schemas.microsoft.com/sharepoint/&quot; xmlns:sps=3D&quot;http://=
schemas.microsoft.com/sharepoint/soap/&quot; xmlns:xsi=3D&quot;http://www.w3.org/2001=
/XMLSchema-instance&quot; xmlns:udcs=3D&quot;http://schemas.microsoft.com/data/udc/so=
ap&quot; xmlns:udcxf=3D&quot;http://schemas.microsoft.com/data/udc/xmlfile&quot; xmlns:udc=
p2p=3D&quot;http://schemas.microsoft.com/data/udc/parttopart&quot; xmlns:wf=3D&quot;http:/=
/schemas.microsoft.com/sharepoint/soap/workflow/&quot; xmlns:dsss=3D&quot;http://sche=
mas.microsoft.com/office/2006/digsig-setup&quot; xmlns:dssi=3D&quot;http://schemas.mi=
crosoft.com/office/2006/digsig&quot; xmlns:mdssi=3D&quot;http://schemas.openxmlformat=
s.org/package/2006/digital-signature&quot; xmlns:mver=3D&quot;http://schemas.openxmlf=
ormats.org/markup-compatibility/2006&quot; xmlns:m=3D&quot;http://schemas.microsoft.c=
om/office/2004/12/omml&quot; xmlns:mrels=3D&quot;http://schemas.openxmlformats.org/pa=
ckage/2006/relationships&quot; xmlns:spwp=3D&quot;http://microsoft.com/sharepoint/web=
partpages&quot; xmlns:ex12t=3D&quot;http://schemas.microsoft.com/exchange/services/20=
06/types&quot; xmlns:ex12m=3D&quot;http://schemas.microsoft.com/exchange/services/200=
6/messages&quot; xmlns:pptsl=3D&quot;http://schemas.microsoft.com/sharepoint/soap/Sli=
deLibrary/&quot; xmlns:spsl=3D&quot;http://microsoft.com/webservices/SharePointPortal=
Server/PublishedLinksService&quot; xmlns:Z=3D&quot;urn:schemas-microsoft-com:&quot; xmlns:=
st=3D&quot;&#1;&quot; xmlns=3D&quot;http://www.w3.org/TR/REC-html40&quot;&gt;
&lt;head&gt;
&lt;meta http-equiv=3D&quot;Content-Type&quot; content=3D&quot;text/html; charset=3Diso-8859-=
1&quot;&gt;
&lt;meta name=3D&quot;Generator&quot; content=3D&quot;Microsoft Word 12 (filtered medium)&quot;&gt;
&lt;!--[if !mso]&gt;
&lt;style&gt;
v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
&lt;/style&gt;
&lt;![endif]--&gt;&lt;style&gt;
&lt;!--
 /* Font Definitions */
 @font-face
	{font-family:&quot;MS Mincho&quot;;
	panose-1:2 2 6 9 4 2 5 8 3 4;}
@font-face
	{font-family:&quot;Cambria Math&quot;;
	panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
	{font-family:Calibri;
	panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
	{font-family:Tahoma;
	panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
	{font-family:&quot;Stylus BT&quot;;
	panose-1:2 14 4 2 2 2 6 2 3 4;}
@font-face
	{font-family:&quot;Comic Sans MS&quot;;
	panose-1:3 15 7 2 3 3 2 2 2 4;}
@font-face
	{font-family:&quot;Century Gothic&quot;;
	panose-1:2 11 5 2 2 2 2 2 2 4;}
@font-face
	{font-family:&quot;\@MS Mincho&quot;;
	panose-1:2 2 6 9 4 2 5 8 3 4;}
 /* Style Definitions */
 p.MsoNormal, li.MsoNormal, div.MsoNormal
	{margin:0in;
	margin-bottom:.0001pt;
	font-size:12.0pt;
	font-family:&quot;Times New Roman&quot;,&quot;serif&quot;;}
a:link, span.MsoHyperlink
	{mso-style-priority:99;
	color:blue;
	text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
	{mso-style-priority:99;
	color:purple;
	text-decoration:underline;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
	{mso-style-priority:99;
	mso-style-link:&quot;Balloon Text Char&quot;;
	margin:0in;
	margin-bottom:.0001pt;
	font-size:8.0pt;
	font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;;}
p.MsoListParagraph, li.MsoListParagraph, div.MsoListParagraph
	{mso-style-priority:34;
	margin-top:0in;
	margin-right:0in;
	margin-bottom:0in;
	margin-left:.5in;
	margin-bottom:.0001pt;
	font-size:12.0pt;
	font-family:&quot;Times New Roman&quot;,&quot;serif&quot;;}
span.EmailStyle17
	{mso-style-type:personal;
	font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;
	color:windowtext;}
span.EmailStyle18
	{mso-style-type:personal;
	font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;
	color:#1F497D;}
span.EmailStyle20
	{mso-style-type:personal-reply;
	font-family:&quot;Calibri&quot;,&quot;sans-serif&quot;;
	color:#1F497D;}
span.BalloonTextChar
	{mso-style-name:&quot;Balloon Text Char&quot;;
	mso-style-priority:99;
	mso-style-link:&quot;Balloon Text&quot;;
	font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;;}
.MsoChpDefault
	{mso-style-type:export-only;
	font-size:10.0pt;}
@page Section1
	{size:8.5in 11.0in;
	margin:1.0in 1.25in 1.0in 1.25in;}
div.Section1
	{page:Section1;}
 /* List Definitions */
 @list l0
	{mso-list-id:433550510;
	mso-list-type:hybrid;
	mso-list-template-ids:1776845046 67698703 67698713 67698715 67698703 67698=
713 67698715 67698703 67698713 67698715;}
@list l0:level1
	{mso-level-tab-stop:none;
	mso-level-number-position:left;
	text-indent:-.25in;}
ol
	{margin-bottom:0in;}
ul
	{margin-bottom:0in;}
--&gt;
&lt;/style&gt;&lt;!--[if gte mso 9]&gt;&lt;xml&gt;
 &lt;o:shapedefaults v:ext=3D&quot;edit&quot; spidmax=3D&quot;2050&quot; /&gt;
&lt;/xml&gt;&lt;![endif]--&gt;&lt;!--[if gte mso 9]&gt;&lt;xml&gt;
 &lt;o:shapelayout v:ext=3D&quot;edit&quot;&gt;
  &lt;o:idmap v:ext=3D&quot;edit&quot; data=3D&quot;1&quot; /&gt;
 &lt;/o:shapelayout&gt;&lt;/xml&gt;&lt;![endif]--&gt;
&lt;/head&gt;
&lt;body lang=3D&quot;EN-US&quot; link=3D&quot;blue&quot; vlink=3D&quot;purple&quot;&gt;
&lt;div class=3D&quot;Section1&quot;&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;Sheri et al,&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;When you define a shell as a more than 1-story &#8211; you a=
re simultaneously making the decision that each story will have a matching =
&#8220;typical&#8221; zoning layout.&nbsp;
 What you define at the custom zoning screen will be mirrored for each leve=
l.&nbsp; This approach/simplification has the advantages of simplifying the=
 model, saving input time and also permits the wizards to automatically gen=
erate inter-floor heat transfer surfaces.&nbsp;
&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&nbsp;&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;If you wish to model distinct zoning patterns for each level=
 (and this is not uncommon), you should instead create a separate shell for=
 each distinct pattern.&nbsp;
 For clarity/context, to define multiple shells as described, you should co=
nvert to DD wizards from SD if you aren&#8217;t already there.&lt;o:p&gt;&lt;/o:p&gt;&lt;/=
span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;Some extra pointers for those new to the &#8220;shell-per-fl=
oor&#8221; approach:
&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoListParagraph&quot; style=3D&quot;text-indent:-.25in;mso-list:l0 level=
1 lfo1&quot;&gt;&lt;![if !supportLists]&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&amp;q=
uot;Calibri&quot;,&quot;sans-serif&quot;;color:#1F497D&quot;&gt;&lt;span style=3D&quot;mso-=
list:Ignore&quot;&gt;1.&lt;span style=3D&quot;font:7.0pt &quot;Times New Roman&quot;&quot;&gt;&amp;nbsp=
;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
&lt;/span&gt;&lt;/span&gt;&lt;/span&gt;&lt;![endif]&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:=
&quot;Calibri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;Fully &#8220;sandwiched&#8221; floors defined using separate=
 shells should select no (adiabatic) floor and roof constructions, lest you=
 end up multiplying your
 roof or ground-perimeter envelope loads.&nbsp; Do define your roof and flo=
or surfaces for your top and ground level shells.&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoListParagraph&quot; style=3D&quot;text-indent:-.25in;mso-list:l0 level=
1 lfo1&quot;&gt;&lt;![if !supportLists]&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&amp;q=
uot;Calibri&quot;,&quot;sans-serif&quot;;color:#1F497D&quot;&gt;&lt;span style=3D&quot;mso-=
list:Ignore&quot;&gt;2.&lt;span style=3D&quot;font:7.0pt &quot;Times New Roman&quot;&quot;&gt;&amp;nbsp=
;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
&lt;/span&gt;&lt;/span&gt;&lt;/span&gt;&lt;![endif]&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:=
&quot;Calibri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;If you feel inter-floor heat transfer is critical for the en=
ergy model, or if you have should partially exposed (exterior) roofs/floors=
 for a given
 shell/level, you can have your cake and eat it too.&nbsp; Search the archi=
ves for alternative wizard/detailed-mode approaches (my name will be in a f=
ew of them).&nbsp; In those cases, you&#8217;d define such roof and/or floo=
r constructions for the entire shell/floor, then
 later either delete or replace &#8220;sandwiched&#8221; surfaces with inte=
rior partitions as required in detailed mode.&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoListParagraph&quot; style=3D&quot;text-indent:-.25in;mso-list:l0 level=
1 lfo1&quot;&gt;&lt;![if !supportLists]&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&amp;q=
uot;Calibri&quot;,&quot;sans-serif&quot;;color:#1F497D&quot;&gt;&lt;span style=3D&quot;mso-=
list:Ignore&quot;&gt;3.&lt;span style=3D&quot;font:7.0pt &quot;Times New Roman&quot;&quot;&gt;&amp;nbsp=
;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;
&lt;/span&gt;&lt;/span&gt;&lt;/span&gt;&lt;![endif]&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:=
&quot;Calibri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;For any multi-shell project, I would suggest first completin=
g the rest of the inputs for the first shell shared by the rest of the buil=
ding, (ex:
 envelope properties, typical window layouts, whole building LPD&#8217;s&amp;#8=
230; etc.) before copying to create the next shell.&nbsp; This will minimiz=
e redundant inputs that take extra time and invite human error (i.e. select=
ing the wall construction inputs in 3 places instead
 of once). &nbsp;This advice becomes critical for projects with many shells=
.&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;Best of luck!&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;~Nick&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;div&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;img width=3D&quot;119&quot; height=3D&quot;37&quot; id=3D&quot;Picture_x0020_1&quot; src=
=3D&quot;cid:image001.jpg@01CBF39A.70DF32E0&quot; alt=3D&quot;cid:489575314@22072009-0ABB&quot;=
&gt;&lt;/span&gt;&lt;b&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Stylus BT&amp;quot=
;,&quot;sans-serif&quot;;color:#2D4D5E&quot;&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/b&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;b&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&amp;quot=
;Stylus BT&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/b&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;b&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&amp;quot=
;Stylus BT&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;NICK CATON, E.I.T.&lt;/span&gt;&lt;/b&gt;&lt;b&gt;&lt;span style=3D&quot;font-family:&amp;=
quot;Stylus BT&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/b&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:7.5pt;font-family:&quot;Cal=
ibri&quot;,&quot;sans-serif&quot;;
color:#CC9900&quot;&gt;PROJECT ENGINEER&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;Smith &amp; Boucher Engineers&lt;/span&gt;&lt;span style=3D&quot;font-size=
:7.5pt;
color:#CC9900&quot;&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;25501 west valley parkway&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;olathe ks 66061&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;direct 913 344.0036&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#2D4D5E&quot;&gt;fax 913 345.0617&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;a href=3D&quot;www.smithboucher.com&quot; title=3D&quot;blocked::www.smith=
boucher.com&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt&quot;&gt;www.smithboucher.com&lt;/span&gt;&lt;/=
a&gt;&lt;/span&gt;&lt;u&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Calibri&quot;=
,&quot;sans-serif&quot;;color:blue&quot;&gt;
&lt;/span&gt;&lt;/u&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Calibri&quot;,=
&quot;sans-serif&quot;;color:#1F497D&quot;&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;/div&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;div&gt;
&lt;div style=3D&quot;border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in =
0in 0in&quot;&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;b&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&amp;quot=
;Tahoma&quot;,&quot;sans-serif&quot;&quot;&gt;From:&lt;/span&gt;&lt;/b&gt;&lt;span style=3D&quot;font-s=
ize:10.0pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;&quot;&gt; equest-u=
sers-bounces@lists.onebuilding.org [mailto:equest-users-bounces@lists.onebu=
ilding.org]
&lt;b&gt;On Behalf Of &lt;/b&gt;atowell@cxegroup.com&lt;br&gt;
&lt;b&gt;Sent:&lt;/b&gt; Tuesday, April 05, 2011 1:19 PM&lt;br&gt;
&lt;b&gt;To:&lt;/b&gt; Sheri; eQuest List(equest-users@lists.onebuilding.org)&lt;br&gt;
&lt;b&gt;Subject:&lt;/b&gt; Re: [Equest-users] multiple floor zones&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/=
p&gt;
&lt;/div&gt;
&lt;/div&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;Sheri-&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;The best way that I have seen to do this is to create a sepa=
rate shell for each floor, then zone each floor individually. I hope this h=
elps!&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;div&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;Adam Towell&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;CxE Group, LLC&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;618-659-9461&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;/div&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:11.0pt;font-family:&quot;Ca=
libri&quot;,&quot;sans-serif&quot;;
color:#1F497D&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;div&gt;
&lt;div style=3D&quot;border:none;border-top:solid #B5C4DF 1.0pt;padding:3.0pt 0in =
0in 0in&quot;&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;b&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&amp;quot=
;Tahoma&quot;,&quot;sans-serif&quot;&quot;&gt;From:&lt;/span&gt;&lt;/b&gt;&lt;span style=3D&quot;font-s=
ize:10.0pt;font-family:&quot;Tahoma&quot;,&quot;sans-serif&quot;&quot;&gt; equest-u=
sers-bounces@lists.onebuilding.org [mailto:equest-users-bounces@lists.onebu=
ilding.org]
&lt;b&gt;On Behalf Of &lt;/b&gt;Sheri&lt;br&gt;
&lt;b&gt;Sent:&lt;/b&gt; Tuesday, April 05, 2011 12:21 PM&lt;br&gt;
&lt;b&gt;To:&lt;/b&gt; equest-users@lists.onebuilding.org&lt;br&gt;
&lt;b&gt;Subject:&lt;/b&gt; [Equest-users] multiple floor zones&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;/div&gt;
&lt;/div&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ar=
ial&quot;,&quot;sans-serif&quot;&quot;&gt;Hello,&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ar=
ial&quot;,&quot;sans-serif&quot;&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ar=
ial&quot;,&quot;sans-serif&quot;&quot;&gt;I have a 3 story building that each floor=
 has multiple zones. How do I do this? When I go into the zoning pattern (w=
hich I have selected custom) it brings up my footprint so
 I can draw out my zones, but how do I know which floor I am on &amp; how d=
o I switch between floors?&lt;o:p&gt;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ar=
ial&quot;,&quot;sans-serif&quot;&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/span&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ar=
ial&quot;,&quot;sans-serif&quot;;
color:black&quot;&gt;Thank you,&lt;/span&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&nbsp;&lt;o:p&gt;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;;
color:maroon&quot;&gt;Sheri Rice,&lt;/span&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;;
color:maroon&quot;&gt;Assistant General Manager&lt;/span&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;strong&gt;&lt;span style=3D&quot;font-family:&quot;Comic Sans =
MS&quot;;color:red&quot;&gt;Fire
&lt;/span&gt;&lt;/strong&gt;&lt;strong&gt;&lt;span style=3D&quot;font-family:&quot;Comic Sans MS&amp;quot=
;;color:black&quot;&gt;&amp; &lt;/span&gt;
&lt;/strong&gt;&lt;strong&gt;&lt;span style=3D&quot;font-family:&quot;Comic Sans MS&quot;;color=
:blue&quot;&gt;Ice&lt;/span&gt;&lt;/strong&gt;&lt;strong&gt;&lt;span style=3D&quot;font-family:&quot;Comic Sa=
ns MS&quot;&quot;&gt;
&lt;/span&gt;&lt;/strong&gt;&lt;span style=3D&quot;font-family:
&quot;Comic Sans MS&quot;;color:black&quot;&gt;Geothermal, LLC&lt;/span&gt;&lt;o:p&gt;&lt;/o:p&gt;&lt;/p=
&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;&quot;&gt;198276 E County Road 41&lt;/span&gt;&lt;o=
:p&gt;&lt;/o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;&quot;&gt;Woodward, OK 73801&lt;/span&gt;&lt;o:p&gt;&lt;/=
o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;&quot;&gt;580-256-9439 Voice&lt;/span&gt;&lt;o:p&gt;&lt;/=
o:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;&quot;&gt;580-256-7080 Fax&lt;/span&gt;&lt;o:p&gt;&lt;/o:=
p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;span style=3D&quot;font-size:10.0pt;font-family:&quot;Ce=
ntury Gothic&quot;,&quot;sans-serif&quot;&quot;&gt;580-216-1005 Cell&lt;/span&gt;&lt;o:p&gt;&lt;/o=
:p&gt;&lt;/p&gt;
&lt;p class=3D&quot;MsoNormal&quot;&gt;&lt;o:p&gt;&nbsp;&lt;/o:p&gt;&lt;/p&gt;
&lt;/div&gt;
&lt;/body&gt;
&lt;/html&gt;

--_000_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_--

--_005_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_
Content-Type: image/jpeg; name=&quot;image001.jpg&quot;
Content-Description: image001.jpg
Content-Disposition: inline; filename=&quot;image001.jpg&quot;; size=1459;
	creation-date=&quot;Tue, 05 Apr 2011 19:44:22 GMT&quot;;
	modification-date=&quot;Tue, 05 Apr 2011 19:44:22 GMT&quot;
Content-ID: &lt;image001.jpg@01CBF39A.70DF32E0&gt;
Content-Location: image001.jpg
Content-Transfer-Encoding: base64
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--_005_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_--

--_006_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_
Content-Type: text/plain; name=&quot;ATT03288.txt&quot;
Content-Description: ATT03288.txt
Content-Disposition: attachment; filename=&quot;ATT03288.txt&quot;; size=253;
	creation-date=&quot;Tue, 05 Apr 2011 19:44:22 GMT&quot;;
	modification-date=&quot;Tue, 05 Apr 2011 19:44:22 GMT&quot;
Content-Transfer-Encoding: base64

X19fX19fX19fX19fX19fX19fX19fX19fX19fX19fX19fX19fX19fX19fX19fX18NCkVxdWVzdC11
c2VycyBtYWlsaW5nIGxpc3QNCmh0dHA6Ly9saXN0cy5vbmVidWlsZGluZy5vcmcvbGlzdGluZm8u
Y2dpL2VxdWVzdC11c2Vycy1vbmVidWlsZGluZy5vcmcNClRvIHVuc3Vic2NyaWJlIGZyb20gdGhp
cyBtYWlsaW5nIGxpc3Qgc2VuZCAgYSBibGFuayBtZXNzYWdlIHRvIEVRVUVTVC1VU0VSUy1VTlNV
QlNDUklCRUBPTkVCVUlMRElORy5PUkcNCg==

--_006_FCEBC0C28321F7479789B25A13030F69032C88FFsandbinc2sbismi_--
]