    Michael-<br>
    <br>
    For zonal systems, I'd suggest reviewing the ZONE heating and
    cooling SS-P reports as another way to see what is going on.  I just
    reviewed these reports for a current project, and found that I get
    nearly the same results for both DOE-2 system types HP and PTAC
    using these two fan control options:<br>
    <ol>
      <li>No outside air specified at SYSTEM or ZONE level, FAN-SCHEDULE
        set to all 1's, and FAN-CONTROL = CYCLING</li>
      <li>No outside air specified at SYSTEM or ZONE level, and as Robby
        suggested, FAN-SCHEDULE set to all 0's and NIGHT-CYCLE-CONTROL =
        CYCLE-ON-ANY<br>
      </li>
    </ol>
    Attached is an xlsx summary for one zone using one of these
    scenarios.  As you can see, the system fans are not running 8760. 
    The report indicates 6010 run hrs.  However, as indicated part-load
    hour summary, the there are many values lower in the range,
    indicating the system is only cycling on for a fraction of the
    hour.  The total annual effective full load hours is only 1166.<br>
    <br>
    A couple things to try:<br>
    <ul>
      <li>What DOE-2 system type are you using?  A zonal system, such as
        HP or PTAC?  If you are using a single-zone system, such as PSZ
        or PVVT, then FAN-CONTROL = CYCLING has no impact.  If you only
        want the system to cycle on to meet loads, you have to set
        INDOOR-FAN-MODE = INTERMITTENT (CONSTANT is the DOE-2 default).</li>
      <li>Do you specify outdoor air at the SYSTEM or ZONE level?  If
        you truly want no OA supplied by the system, I would default all
        OA related keywords to "no_default"; a zero value may still be
        recognized by the program as a value and hence, cause the system
        to run 24/7. </li>
    </ul>
    <p>Also, related to the night-cycle control option, remember to
      define a MIN-AIR-SCH with 0's during unoccupied hours.  Otherwise,
      when the system cycles on at night to meet the setback temp, the
      OA dampers will remain open.  This is a bit of a tradeoff, since
      it also disables the economizer.  But for heating dominated
      climates, where cycling is most often to meet heating load, this
      is typically the best way to go.  Otherwise, if you are comparing
      two designs (i.e. proposed and LEED basline), the design with
      better envelope performance is more likely to not have as many
      night cycle hours, and hence, use less energy heating (or possibly
      cooling) ventilation air.   This oversight can have a huge impact
      on savings comparisons...<br>
    </p>
    Hope this helps,<br>
    - David<br>
    <br>
    <br>
    On 2/1/2012 11:35 AM, Michael Mantai wrote:
    <blockquote cite="mid:CB4EFE4E.305AC%25mmantai@systemworcx.com"
      type="cite">
      <title>Re: [Equest-users] Fan Cycling Indication in Detailed
        Report?</title>
      <font face="Calibri, Verdana, Helvetica, Arial"><span
          style="font-size:11pt">I tried this but it had no effect.  My
          annual kWh equals my total fan power times 8760, so I’m
          certain that the fans are on continuously.  There must be
          something that is keeping them on, but I cannot find it.<br>
          <br>
          <br>
          On 2/1/12 1:52 PM, "Robby Oylear" <<a
            moz-do-not-send="true" href="robbyoylear@gmail.com">robbyoylear@gmail.com</a>>
          wrote:<br>
          <br>
        </span></font>
      <blockquote><font face="Calibri, Verdana, Helvetica, Arial"><span
            style="font-size:11pt">Michael,<br>
            <br>
            On a recent project I modeled this same situation.  The way
            I was able to force the system to only operate during a call
            for cooling or heating was by defining a fan schedule with
            all hours set to 0.  Per the DOE2.2 help documentation on
            fan schedules:<br>
            - </span></font><span style="font-size:11pt"><font
            face="Symbol">  </font><font face="Calibri, Verdana,
            Helvetica, Arial">If the value is 0, the fans are off but
            may be turned on by NIGHT-CYCLE-CTRL if zone temperatures
            warrant it. <br>
            <br>
            Make sure to allow night cycle control (cycle on any).  This
            basically defines all hours of the day to be "night" and the
            fan will cycle on to meet the load in the space.  <br>
            <br>
            Robby Oylear, </font></span><font face="Calibri, Verdana,
          Helvetica, Arial"><font size="2"><span style="font-size:10pt">LEED
              AP<br>
            </span></font></font><font size="1"><font face="Verdana,
            Helvetica, Arial"><span style="font-size:8pt"><i>Mechanical
                Project Engineer<br>
                Senior Energy Analyst<br>
                 <br>
              </i></span></font><span style="font-size:8pt"><font
              face="Calibri, Verdana, Helvetica, Arial"><b>D</b> </font><font
              face="Verdana, Helvetica, Arial">206-788-4571<br>
            </font><font face="Calibri, Verdana, Helvetica, Arial"><b><i><a class="moz-txt-link-abbreviated" href="http://www.rushingco.com">www.rushingco.com</a></i></b></font></span></font><font
          face="Calibri, Verdana, Helvetica, Arial"><span
            style="font-size:11pt"> <<a moz-do-not-send="true"
              href="http://www.rushingco.com/">http://www.rushingco.com/</a>>
            <br>
            <br>
            On Wed, Feb 1, 2012 at 10:00 AM, Chris Hadlock <<a
              moz-do-not-send="true" href="cjhadlock@gmail.com">cjhadlock@gmail.com</a>>
            wrote:<br>
          </span></font>
        <blockquote><font face="Calibri, Verdana, Helvetica, Arial"><span
              style="font-size:11pt">Hi Michael,<br>
              <br>
              I would just run an hourly report for one of your heat
              pump systems and pick up hourly flow rate and fan energy.
              This way you can see how often your fans are running and
              whether they are cycling or running continuously. With
              heat pump systems, there are key words under the Fans tab
              (for a given system) that will indicate the control on the
              fans. One is night cycle control and the other is indoor
              fan mode (within the Flow Parameters tab). If your fans
              are not cycling, it is likely due to those two key words
              (or the fan schedule you have specified).<br>
              <font color="#888888"><br>
                Chris<br>
              </font><br>
              <br>
              On Wed, Feb 1, 2012 at 12:44 PM, Michael Mantai <<a
                moz-do-not-send="true" href="mmantai@systemworcx.com">mmantai@systemworcx.com</a>>
              wrote:<br>
            </span></font>
          <blockquote><font face="Calibri, Verdana, Helvetica, Arial"><span
                style="font-size:11pt">I'm modeling a 6-story hotel.
                 Baseline is PTAC.  I set up the baseline to<br>
                have outside air at each PTAC with the fans running
                continuously.  The<br>
                Proposed Case is watersource heat pumps.  Outside air is
                through dedicated<br>
                units at the corridors.  I've set (at least I am trying
                to set) the heat<br>
                pump fans to cycle on the thermostat.  I've set the heat
                pumps to 0 CFM<br>
                outside air.  When I run the two models, the ventilation
                fan energy is<br>
                nearly identical.  I expected to see some fan energy
                savings with the heat<br>
                pump fans cycling.  When I look at the detailed output
                report, the SS-C for<br>
                the heat pumps seems like it is showing fans running
                continuously.  I say<br>
                this because the "hours floating" are less than the
                "hours fans on", and the<br>
                "hours fans cycle on" is zero.  This implies to me that
                the fans are running<br>
                continuously.  However, when I look at the reports that
                show fan energy<br>
                consumption, the months with floating hours show
                significantly reduced fan<br>
                energy, which to me implies that they are cycling.  The
                total fan kW in the<br>
                proposed model is about twice that of the baseline, so
                from that standpoint<br>
                maybe the kWh being about the same is correct.  I set up
                the PTAC units at<br>
                .3 watts/CFM per ASHRAE.  I set up the heat pumps fans
                with a static<br>
                pressure input from the design drawings rather than
                input the fan motor<br>
                sizes (used .2" w.g. Static).<br>
                <br>
                Also, my space cooling energy is higher in the proposed
                case than the<br>
                baseline, even though the envelope is better, the
                watersource heat pumps<br>
                have a lower EIR and the design lighting power density
                is 30% lower.  I<br>
                haven't dug into that yet because I'm still trying to
                verify my fan cycling<br>
                is working.<br>
                <br>
                My questions are, can anyone explain how to interpret
                the SS-C reports in<br>
                terms of fan cycling, or point me to which report I
                should look to really<br>
                verify the fans are cycling?  And anyone modeled a
                similar comparison, and<br>
                if so, what type of results did you get with respect to
                cooling energy and<br>
                fan power consumption?  Seems like I should be seeing
                savings.<br>
                <br>
                <br>
                _______________________________________________<br>
                Equest-users mailing list<br>
                <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
                To unsubscribe from this mailing list send  a blank
                message to <a moz-do-not-send="true"
                  href="EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              </span></font></blockquote>
          <font face="Calibri, Verdana, Helvetica, Arial"><span
              style="font-size:11pt"><br>
              <br>
              _______________________________________________<br>
              Equest-users mailing list<br>
              <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
              To unsubscribe from this mailing list send  a blank
              message to <a moz-do-not-send="true"
                href="EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
              <br>
            </span></font></blockquote>
        <font face="Calibri, Verdana, Helvetica, Arial"><span
            style="font-size:11pt"><br>
            <br>
          </span></font></blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>