<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012>Norm,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012>Is your simulation going through successfully?
Typically, just creating a skylight in an existing roof (which I am guessing is
currently attached to your core plenum space) gives you an error.
</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012>You will have to create a new roof for the core space,
use 'Skylt Roof Construction' as the construction, and then create the skylight
in this new roof. </SPAN></FONT><FONT color=#0000ff size=2
face="Trebuchet MS"><SPAN class=153355915-24012012>See if this
works.</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012>Regards,</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012>Umesh</SPAN></FONT></DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012></SPAN></FONT> </DIV>
<DIV dir=ltr align=left><FONT color=#0000ff size=2 face="Trebuchet MS"><SPAN
class=153355915-24012012></SPAN></FONT> </DIV>
<DIV dir=ltr align=left>
<HR tabIndex=-1>
</DIV>
<DIV dir=ltr align=left><FONT size=2 face=Tahoma><B>From:</B>
equest-users-bounces@lists.onebuilding.org
[mailto:equest-users-bounces@lists.onebuilding.org] <B>On Behalf Of </B>norman
wheatley<BR><B>Sent:</B> Saturday, January 21, 2012 6:07 PM<BR><B>To:</B>
equest-users@lists.onebuilding.org<BR><B>Subject:</B> [Equest-users] light tubes
and light wells<BR></FONT><BR></DIV>
<DIV></DIV>Hi,<BR><BR>I'm trying to model a light tube and a light well in
eQuest. I'd like to bring light into the core and maybe a lower level and have
this reduce the lighting required.<BR><BR>so, I create a window in the roof,
change the window to "Tubular Daylighting device" and have a daylighting sensor
in the space below (a core zone).<BR>But there is no effect on the lighting
energy. This is the same if I use a skylight (aka a light well).<BR><BR>Has
anyone used this successully?<BR><BR>thanks<BR>Norm<BR><BR><BR></BODY></HTML>