    Without looking at the model, it would seem that eQUEST cannot size
    the heating loop.  The default for loop sizing is "secondary" where
    eQUEST simply adds up the capacity of the coils attached to the loop
    (not good I know -- apparently that is in the works in an upcoming
    version).  The error message suggests there is no heating elements
    to count up.<br>
    <br>
    The issue I have had with loop-to-loop heat pumps is and imbalance
    between the loads/temperatures.  On the 4th tab/screen of the
    loop-to-loop chiller type there are 4 temperatures (OK 2 temps and 2
    delta T's) that are key to getting this system to work.  When I set
    those to the values in the help file, my model ran.  I am no expert
    on this system type but did get "reasonable" (or at least so I
    thought) values in the 1 building I did create that used it.<br>
    <br>
    If you send your .inp and .pd2 I may be able to have a quick look.<br>
    <br>
    Brian<br>
    <br>
    On 12/21/2011 5:22 AM, Chen, Ke-Huang wrote:
    <blockquote
cite="mid:56508317F4254A4099ECD9A850C0FE5D047FF970@TPET038A.tw001.siemens.net"
      type="cite">
      <meta content="text/html; charset=ISO-8859-1"
        http-equiv="Content-Type">
      <meta name="GENERATOR" content="MSHTML 8.00.6001.19154">
      <div><font size="2" face="Arial"><span class="329413609-21122011">Dear
            eQUEST users,</span></font></div>
      <div><font size="2" face="Arial"><span class="329413609-21122011"></span></font> </div>
      <div><font size="2" face="Arial"><span class="329413609-21122011">I
            am modeling a loop to loop heat pump in the eQUEST and
            it needs to attach hot water loop&pump, chilled water
            loop&pump, condenser water loop&pump. After I create
            these loops and pumps, there is an error in simulation shows
            "Hot water loop has zero design flow. Check input for
            consistency, or specify design loads.". But I did connect
            heat pump to hot water loop. Is there anything I need to
            input so that the simulation will be successful? Does anyone
            have the experience of modeling a loop to loop heat pump?
            It's my first time model heat pump, any help and suggestion
            will be appreciated.</span></font></div>
      <div><font size="2" face="Arial"><span class="329413609-21122011"></span></font> </div>
      <div><font size="2" face="Arial"><span class="329413609-21122011">Best
            regards,</span></font></div>
      <div><font size="2" face="Arial"><span class="329413609-21122011"></span></font> </div>
      <div> </div>
      <div align="left"><font size="2" face="Arial"><strong>KeHuang Chen</strong></font></div>
      <div><strong><font size="2" face="Arial">System Engineer</font></strong></div>
      <div><strong><font size="2" face="Arial">IC BT Division</font></strong></div>
      <div><strong><font size="2" face="Arial">Siemens Limited Taiwan</font></strong></div>
      <div><strong></strong> </div>
      <div><strong><font size="2" face="Arial">Tel : (+886)2-2652-8888
            ext. 896</font></strong></div>
      <div><strong><font size="2" face="Arial">Mobile : (+886)960548011</font></strong></div>
      <div><strong><font size="2" face="Arial">Fax : (+886)2-2652-8824</font></strong></div>
      <div> </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>