<P>Thanks. The supply air temp was too low. What CHWS temp does eQUEST assume? This should be an input value too, besides temp rise.</P>
<P>Varkie<BR><B></B></P>
<P><B>----- Original Message -----</B></P>
<P></P><B>From</B>: Kelsey VanTassel <KVanTassel@sustaineng.com>
<P></P><B>Date</B>: Thursday, December 15, 2011 3:24 pm
<P></P><B>Subject</B>: RE: [Equest-users] CHW error message
<P></P>
<P></P>> Either your supply air temperature is set too low or your chilled <BR>> water supply temperature is set too high. <BR>> <BR>> Kelsey Van Tassel <BR>> Project Engineer | <BR>> kvantassel@sustaineng.com<mailto:kvantassel@sustaineng.com>608.836.4488 ext. 20 | Fax: 608.836.4477 <BR>> [cid:image001.jpg@01CCBB3D.A32C4B50] <BR>> Sustainable Engineering Group <BR>> 901 Deming Way, Suite 201 <BR>> Madison, WI 53717 <BR>> www.sustaineng.com<http://www.sustaineng.com/> <BR>> <BR>> <BR>> From: equest-users-bounces@lists.onebuilding.org [mailto:equest- <BR>> users-bounces@lists.onebuilding.org] On Behalf Of Varkie C Thomas <BR>> Sent: Thursday, December 15, 2011 3:27 PM <BR>> To: equest-users@lists.onebuilding.org <BR>> Subject: [Equest-users] CHW error message <BR>> <BR>> <BR>> What causes the error below? The CHW input used all eQUEST <BR>
> defaults. The bldg is high-rise residential. The systems used <BR>> defaults also (4-pipe FCU). Varkie Thomas <BR>> <BR>> pro Maslak sim <BR>> DOE-2.2-47h2 12/15/2011 15:03:51 BDL RUN 7 <BR>> <BR>> <BR>> <BR>> REPORT- ATTN Simulation Messages For Review HVAC Program <BR>> WEATHER FILE- EPW ISTANBUL,-,TUR <BR>> <BR>
> ------------------------------------------------------------------- <BR>> -------------------------------------------------------------- <BR>> <BR>> <BR>> <BR>> <BR>> <BR>> ***ERROR*********************************************************************** <BR>> <BR>> In EL1 Sys1 (FC) , cooling coil <BR>> leaving temperature must <BR>> <BR>> be at least 6F higher than entering water temp. <BR>> <BR>> <BR>> <BR>> ***ERROR*********************************************************************** <BR>> <BR>
> In EL1 Sys1 (FC) , cooling coil <BR>> leaving temperature must <BR>> <BR>> be at least 6F higher than entering water temp. <BR>> <BR>> <BR>> <BR>> ***ERROR*********************************************************************** <BR>> <BR>> In EL1 Sys1 (FC) , cooling coil <BR>> leaving temperature must <BR>> <BR>> be at least 6F higher than entering water temp. <BR>> <BR>> <BR>> <BR>
> ***ERROR*********************************************************************** <BR>> <BR>> <BR>> <BR>> <BR>> <BR>> <BR>> <BR>> <BR>> </BODY>