G2.1.2.14 Fan Power (Systems 6 and 8). Fans in parallel VAV fan-powered boxes shall be sized for 50% of the beak design flor rate and shall be modeled with 0.35 W/cfm fan power.<div><br></div><div>Hope this helps.<br><br><div class="gmail_quote">
On Wed, Nov 30, 2011 at 7:53 AM, <span dir="ltr"><<a href="mailto:omoltay@mimtarch.com">omoltay@mimtarch.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
Dear All,<br>
<br>
What is the correct fan power for VAV PFP systems? My printing of Appendix<br>
G has 03.35 W/CFM, which is definitely a misprint.<br>
<br>
Thank you,<br>
<br>
Omer Moltay<br>
Mimta<br>
<br>