Omar,<div><br></div><div>When looking at a problem like this, you should really look at how the individual energy uses change, not just the total building energy use.</div><div><br></div><div>For example, if it's Space Cooling energy increased, then it's likely that your worse U-factor glazing was acting as a way for heat to escape the building from high internal loads.</div>
<div><br></div><div>This question becomes much simpler if you know where the energy is going in your building.</div><div><br></div><div>-Robby<br><br><div class="gmail_quote">2011/10/13 Omar Osama <span dir="ltr"><<a href="mailto:o_osama@live.com">o_osama@live.com</a>></span><br>
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex;">
<div><div dir="ltr">
<font face="Arial"><div><font face="Arial">Thanks so much,</font></div>I do appreciate your reply ,, I shall re-check internal loads, guess I have excessive lighting loads. <br></font><br><br><blockquote style="border:none;padding:0px">
<span style="background-color:rgb(255, 255, 255);font-size:10pt"><b><font face="Tahoma">Omar AlRawi</font></b></span></blockquote><blockquote style="border:none;padding:0px"><span style="background-color:rgb(255, 255, 255);font-size:10pt"><b><font face="Tahoma">Project Engineer,</font></b></span></blockquote>
<blockquote style="border:none;padding:0px"><span style="background-color:rgb(255, 255, 255);font-size:10pt"><b><font face="Tahoma">EA Sustainable B
 uilding Consultants<br></font></b></span><span style="background-color:rgb(255, 255, 255);font-size:10pt"><b><font face="Tahoma"><a href="http://www.ea-buildingconsultants.com/" target="_blank">www.ea-buildingconsultants.com</a></font></b></span></blockquote>
<hr><br><br><div><hr>From: <a href="mailto:akrickx@seriousenergy.com" target="_blank">akrickx@seriousenergy.com</a><br>To: <a href="mailto:chris@greenengineer.com" target="_blank">chris@greenengineer.com</a>; <a href="mailto:o_osama@live.com" target="_blank">o_osama@live.com</a>; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
Date: Thu, 13 Oct 2011 10:39:02 -0700<br>Subject: RE: [Equest-users] U-Value unexpected impact<div><div></div><div class="h5"><br><br>
<div style="font-family:Tahoma;direction:ltr;color:#000000;font-size:13px">
<div>Hi Omar,</div>
<div><font size="2" face="tahoma"></font> </div>
<div>Another thing to check is that you are modeling a glass with a low-Solar Heat Gain Coefficient (SHGC<a></a>). Low SHGC<a></a> glasses and glass-units are best for situations where there is no need for passive heating (hot climates and internal load-dominated
 buildings).</div>
<div><font size="2" face="tahoma"></font> </div>
<div><font size="2" face="tahoma">You can still maintain high VT (>0.5) with low SHGC<a></a> (<0.3), so it doesn't need to sacrifice aesthetics and daylighting<a></a> options.</font></div>
<div> </div>
<div>Great point on the internal loads Chris.</div>
<div><font size="2" face="tahoma"></font> </div>
<div><font size="2" face="tahoma">Cheers,</font></div>
<div><font size="2" face="tahoma">Alex</font></div>
<div><font size="2" face="tahoma"></font> </div>
<div>
<p><span style="color:#262f13">Alex Krickx<a></a>, LEED<a></a> AP</span></p>
<p><span style="color:gray;font-size:11pt">Building Energy Specialist</span></p>
<p><span style="color:black;font-size:10pt">Serious Energy, Inc.</span></p>
<p><span style="color:black;font-size:10pt">1250 Elko Dr, Sunnyvale, CA 94089</span></p>
<p><span style="color:black;font-size:10pt">(t) <a href="tel:408.541.8124" value="+14085418124" target="_blank">408.541.8124</a></span></p>
<p><span style="color:black;font-size:10pt"><a><span style="color:black;font-size:10pt">akrickx@seriousenergy.com</span></a></span></p>
<p><span style="color:black;font-size:9pt"></span> </p>
<p><i><span style="color:black;font-size:8pt">The information contained in this e-mail and any attachments may be confidential, proprietary and/or privileged. If you are not the intended recipient then
 you have received it in error and any review, distribution or copying of this message and any attachments is prohibited and you are to notify the sender immediately by reply e-mail and delete immediately this message and any attachments.</span></i><span style="color:black;font-size:8pt"></span></p>
</div>
<div><font size="2" face="tahoma"></font> </div>
<div dir="ltr"><font color="#000000" size="2" face="Tahoma"></font> </div>
<div style="direction:ltr">
<hr>
<font color="#000000" size="2" face="Tahoma"><b>From:</b> <a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a> [<a href="mailto:equest-users-bounces@lists.onebuilding.org" target="_blank">equest-users-bounces@lists.onebuilding.org</a>] On Behalf Of Christopher Schaffner [<a href="mailto:chris@greenengineer.com" target="_blank">chris@greenengineer.com</a>]<br>
<b>Sent:</b> Thursday, October 13, 2011 10:04 AM<br>
<b>To:</b> Omar Osama; <a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a><br>
<b>Subject:</b> Re: [Equest-users] U-Value unexpected impact<br>
</font><br>
</div>
<div></div>
<div>
<div>In mild weather, with high internal heat gains, the losses through the glazing reduce the cooling load. In this situation, increasing the performance of the glass will cause increased energy consumption. </div>
<div><br>
</div>
<div>This counterintuitive result is often the result of an overestimation of internal heat gains.   You should perform a reality check on your internal heat gains, before you determine if this result is correct. </div>
<div><br>
</div>
<div>
<div>--</div>
<div><br>
</div>
<div>Chris Schaffner, PE</div>
<div>LEED Fellow</div>
<div>Founder and Principal</div>
<div><br>
</div>
<div>The Green Engineer, LLP</div>
<div>Sustainable Design Consulting</div>
<div>50 Beharrell Street</div>
<div>Concord, MA 01742</div>
<div>T: <a href="tel:978.369.8978" value="+19783698978" target="_blank">978.369.8978</a></div>
<div>M:<a href="tel:978.844.1464" value="+19788441464" target="_blank">978.844.1464</a></div>
<div><a href="mailto:chris@greenengineer.com" target="_blank">chris@greenengineer.com</a></div>
<div><a href="http://www.greenengineer.com" target="_blank">www.greenengineer.com</a></div>
<div><br>
</div>
<div>The Green Engineer, LLP is a Certified B Corporation</div>
</div>
<div><br>
</div>
<span>
<div style="border-bottom:medium none;text-align:left;border-left:medium none;padding-bottom:0in;padding-left:0in;padding-right:0in;font-family:Verdana;color:black;font-size:11pt;border-top:#b5c4df 1pt solid;border-right:medium none;padding-top:3pt">
<span style="font-weight:bold">From: </span>Omar Osama <<a href="mailto:o_osama@live.com" target="_blank">o_osama@live.com</a>><br>
<span style="font-weight:bold">Date: </span>Thu, 13 Oct 2011 16:07:13 +0200<br>
<span style="font-weight:bold">To: </span><<a href="mailto:equest-users@lists.onebuilding.org" target="_blank">equest-users@lists.onebuilding.org</a>><br>
<span style="font-weight:bold">Subject: </span>[Equest-users] U-Value unexpected impact<br>
</div>
<div><br>
</div>
<div>
<div>
<div dir="ltr"><font size="2" face="Tahoma">All,</font>
<div><font size="2" face="Tahoma">    I'am modelling a mid-rise, curtain wall, office building in Egypt (hot humid climate 2a). while I do decrease the glazing's U-value, below 0.5, the energy consumption tends to increase. does this
 issue have a reality related explanation, is it a problem in my file, or is it a software bug issue? </font></div>
<div><font size="2"><br>
</font></div>
<div><font size="2" face="Arial"><br>
</font></div>
<div><font size="2" face="Arial">Thanks for consideration,</font></div>
<div><font size="2" face="Arial"><br>
</font></div>
<div><font size="2" face="Arial"><span style="background-color:rgb(255,255,255);font-family:Verdana,Arial,Helvetica,sans-serif">Omar AlRawi</span><span style="background-color:rgb(255,255,255);font-family:Verdana,Arial,Helvetica,sans-serif"><br>
</span><span style="background-color:rgb(255,255,255);font-family:Verdana,Arial,Helvetica,sans-serif">Project Engineer ,  EA Sustainable Building Consultants</span><span style="background-color:rgb(255,255,255);font-family:Verdana,Arial,Helvetica,sans-serif"><br>
</span><span style="background-color:rgb(255,255,255);font-family:Verdana,Arial,Helvetica,sans-serif"><a href="http://www.ea-buildingconsultants.com/" target="_blank">www.ea-buildingconsultants.com</a></span></font></div>
</div>
</div>
</div>
_______________________________________________ Equest-users mailing list <a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a> To unsubscribe from this mailing list send a blank message to
<a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG" target="_blank">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</span></div>
</div></div></div></div>                                          </div></div>
<br>_______________________________________________<br>
Equest-users mailing list<br>
<a href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
To unsubscribe from this mailing list send  a blank message to <a href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
<br></blockquote></div><br></div>