    <font size="+1"><tt>750 cfm/ton is too high, you should be about
        half that.  I would initially let eQuest size the system, it
        gives you a double check on the design.  The eQuest default is a
        1.15 factor for cooling and is a good starting point.  You can
        dial it down but that depends on the circumstances.<br>
        On the practical side you might be able to get a system to run
        that hard but it wouldn't be very efficient.  You would probably
        need a 14 row coil or more and have a significant pressure drop
        across the coil taking the fan energy way up.  The other thing
        is you don't want the face velocity of your cooling coil to high
        because the condensate will get entrained in the air stream and
        you are going to have water all through your duct system. 
        Typically this can start to happen over 500/550 FPM.  You can
        use moisture eliminators but they are only effective up to a
        certain point and you pay an energy price for them as well.  The
        cooling side of the system normally sets you airflow as this
        side has the smaller delta T.  This may be messing up your
        heating side.<br>
        Bruce Easterbrook P.Eng.<br>
        Abode Engineering<br>
      </tt></font><br>
    On 11/10/2011 11:27 AM, R B wrote:
    <blockquote
cite="mid:CA+f4ixD43Vqk90RfHUv7rWR0f0Lt93hdWyGHeR5zF_yxFnEgQg@mail.gmail.com"
      type="cite">
      <div>For reducing heating unmet hours I have found that reducing
        the min flow helps, or sometimes increasing the reheat supply
        temp if that is an option. </div>
      <div>-Rohini<br>
        <br>
      </div>
      <div class="gmail_quote">On Tue, Oct 11, 2011 at 10:03 AM, nic <span
          dir="ltr"><<a moz-do-not-send="true"
            href="mailto:ffonics@gmail.com">ffonics@gmail.com</a>></span>
        wrote:<br>
        <blockquote style="margin: 0px 0px 0px 0.8ex; padding-left: 1ex;
          border-left-color: rgb(204, 204, 204); border-left-width: 1px;
          border-left-style: solid;" class="gmail_quote">
          <div>Hello,</div>
          <div> </div>
          <div>I am having some issues on a EPAct project with HVAC
            Equipment.  The Quality Check Details states that My CFM/ton
            of Cooling is high at around 750cfm/ton.  I have entered the
            exact design flows/ sizes of the heat pumps as indicated in
            the mechanical schedules, but something seems to be short
            circuiting the heating/ cooling relationship.  Should I
            discard the actual supply flow rate?  I guess the real
            question stems from the fact that when I increase the sizing
            of the system above 1.0 to ~1.25, the heating actually gets
            worse.  Same thing with specifying airflow zone by zone.  At
            this point, it seems that there is something obvious I am
            overlooking.</div>
          <div> </div>
          <div>thanks,</div>
          <div>nic</div>
          <br>
          _______________________________________________<br>
          Equest-users mailing list<br>
          <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org"
            target="_blank">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a><br>
          To unsubscribe from this mailing list send  a blank message to
          <a moz-do-not-send="true"
            href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Equest-users mailing list
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org</a>
To unsubscribe from this mailing list send  a blank message to <a class="moz-txt-link-abbreviated" href="mailto:EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG">EQUEST-USERS-UNSUBSCRIBE@ONEBUILDING.ORG</a>
</pre>
    </blockquote>
  </body>
</html>