<div>Hello All,</div>
<div>             Here is a "sim" output from the hospital bldg I am modelling. The secondary CHW pump has a VFD on it and I would think that the flow would be proportional to speed and the pump would spent some time in the lower load ranges rather being in > 80% load range. </div>

<div> </div>
<div>(<em>Although I do not know as to how eQUEST comes up with the speed to match with flows - my presumption being that the flows are being derived from the loads and delta-T. The constant speed pumps cycles on and off to get deliver the load and VFD equipped pump varies the speed of the pump to regulate the flow to satisfy the load</em>)</div>

<div> </div>
<div>Why is the speed hours not consistent with the flow hours? I am also not limiting the speed of the pump in any way to below 80% range.</div>
<div> </div>
<div>Please advise.</div>
<div> </div>
<div>Thanks in Advance,</div>
<div>Kazim Mirza</div>
<div>Energy Engineer</div>
<div>EMCOR Energy Services</div>