<div>I have a few questions about my baseline model (using Ashrae 90.1 2004) that I'd like to understand, and it would be great if someone could help me:</div>
<div> </div>
<div>- My building have diferent spaces with diferent rated loads, such as galleries, offices and conference rooms. All of them have their own schedules that do not differ for more than 40 hours per week. The selected baseline system is number 7.  <strong>Do I have to model only one VAV system, or can I use one for each space category (one for galleries, one for offices and another for classrooms)?</strong> If not, I would have many spaces that differ more than 31,2W/m2 from the average space load served by the only system, and consequently, I would have many systems number 3 (according to the G3.1.1 exceptions). In addition I think that modelling 3 diferents VAVs would help me in my unmet load hours. (my proposed model have independent units for each type of spaces)</div>

<div> </div>
<div> </div>
<div>- The second question is regarding to those spaces like corridors or halls that do not have thermostats but have some diffusers that supply some outside air just for temper the zone. This air comes from an AHU that serves outside air to fan-coils, or even from a VAV system that serves a conference room or an office. How do I have to model this situation into baseline building. May I link these zones, with its fixed supply air and outdoor air, to the baseline system? Should I introduce them into other system?</div>

<div> </div>
<div> </div>
<div>Thanks very much to all,</div>